Hi everybody. I'm deep into an interesting shower drain issue. Tasked with replacing a trap for a shower. Without getting long winded I'll put up some pictures as an illustration of what I'm working with. This building is all masonry and this shower trap cast into about 12' of cement. I need to get from a new shower drain and trap into the existing 3"wye. The problem I'm having is a 3" rubber bushing is too big and a 2" is too small. I'm missing something I guess. Any advice would be greatly appreciated.

Displaying IMG_2846.jpeg Displaying IMG_2842.jpeg Displaying IMG_2845.jpeg Displaying IMG_2844.jpeg Displaying IMG_2843.jpeg

Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

«1

Comments

  • mattmia2
    mattmia2 Posts: 18,437

    your images are missing but i'm thinking lead and oakum?

  • Grallert
    Grallert Posts: 1,246

    weird about the images. I think youre right about the lead and oakum which is something ive not ever done I’ll try the images again

    thenks for the reply

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Grallert
    Grallert Posts: 1,246

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • mattmia2
    mattmia2 Posts: 18,437

    is that a hub you're looking at? could also try calling fernco or mission and see if they have different size doughnuts. different manufacturers and different weights of ci have different hub sizes.

    you'd need a runner to pour lead on a horizontal joint.

    Grallert
  • mattmia2
    mattmia2 Posts: 18,437

    is there a bomb shelter under that bathroom?

    Mad Dog_2
  • Grallert
    Grallert Posts: 1,246

    I will look around for a different size. My first stop was F W Webb. Second stop was you guys.

    That's the living room below. 12' ceilings. Being renovated. There was a steam condensate leak at a tee in the ceiling/floor along with a roof leak running down a vent in the wall saturating the masonry. This destroyed the ceiling. We thought it was the trap. It was not but in order to find that out I had to dig.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,365

    Not a plumber but I looked up the diameter of Ex heavy and service weight CI pipe and hubs and I saw nothing that was 3 1/4".

  • Grallert
    Grallert Posts: 1,246

    Seems odd. My guess is it's actually 3" or was. I have a bushing marked 3" for SV and POG-3-SW but it's far too large to fit into the hub. Or seems to be. I recognize they are a very tight fit but this really seems excessive.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Grallert
    Grallert Posts: 1,246

    Though I am unable to see if it's extra heavy or service my guess is extra heavy judging by how this building was put together.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • pecmsg
    pecmsg Posts: 7,654

    that is one thick floor!!!

    Grallert
  • Intplm.
    Intplm. Posts: 3,164

    You will need to chip away the outer diameter of the pipe and use that as your connection.

    When it's that deep into the floor, I would use a four-band no-hub clamp, or a reducing four-band clamp.

    From the look of it from here, probably a 4 x 2 or a 3 x 2. That is, unless a hub appears when you chip the cement away from the outer diameter of the pipe, then you would need a push gasket.

    th.jpg

    Push gasket

    c400hw-3.jpg

    Four-band no-hub clamp.

    Larry WeingartenGrallert
  • Grallert
    Grallert Posts: 1,246
    edited August 5

    What is pictured there is the hub of the wye. Do you mean clamp directly to the outer diameter of the hub? I hadn't thought of that. That might be the direction I need to go.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Grallert
    Grallert Posts: 1,246

    Ya. Three day of careful chipping away to avoid any buried surprises. I did find a 3/4 brass cold supply. The whole domestic supply is threaded brass wrapped in tar paper buried in cement.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Grallert
    Grallert Posts: 1,246

    The next challenge will be to rebuild the floor, seal it water tight and tile it.I'll cross that bridge when I get to it.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • DCContrarian
    DCContrarian Posts: 1,594

    That looks to be a slightly oversized hub for 2" extra-heavy cast iron soil pipe.

    Cast iron pipe comes in two sizes, "service" and "extra-heavy." You can see a chart of dimensions here: https://www.engineeringtoolbox.com/cast-iron-soil-pipe-dimensions-d_1751.html

    Extra-heavy in 2" has a hub inner diameter of 3.06".

    The fitting you need is a Fernco donut: https://www.supplyhouse.com/Fernco-22UX-205-2-x-2-Compression-Donut

    That will allow you to transition to 2" PVC. Will that work? I don't know. Fernco makes two sizes of the donut, for service and extra-heavy, even though the hub inner diameter only varies by 0.12", or 1/8". Your hub looks to be about 3/16" bigger than extra-heavy.

    The donut is only about $8 so it's worth trying. If it doesn't work, you can do it the old school way, pack the joint with oakum and seal it. You can pour lead on PVC, but there is a modern sealant specifically made to be a cold replacement for lead in these kinds of joints:

    https://www.supplyhouse.com/Hercules-25215-Plastic-Seal-10-3-oz

    If the Fernco donut makes a mechanically sound joint — ie, it stays together — you can also use the sealant with the donut.

  • Grallert
    Grallert Posts: 1,246

    Thank you for this. I'd forgotten all about the engineeringtoolbox.

    Here's the fitting cleared away a bit. I'll head over to the supply house and see what they have.

    Thanks again

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,365

    Lots of good info in this Tyler Pipe booklet attached. Pg. 103 has some dimensions

    There was an error displaying this embed.
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,437

    also, are you sure that is cast iron and not clay?

  • mattmia2
    mattmia2 Posts: 18,437

    your attachment is just a bang graphic that says "unsafe" if you hover over it. not sure if it needs approval or if it never will show up.

    Grallert
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,365

    @mattmia2

    seems to be ok now.

  • mattmia2
    mattmia2 Posts: 18,437
    edited August 6

    it could be 3.5" pipe too

    you might want to measure it with a caliper and call fernco. their catalog doesn't give dimensions and they seem to have hundreds of sizes that aren't in their catalog.

  • DCContrarian
    DCContrarian Posts: 1,594
    edited August 6

    It would be consistent with 2.5" iron pipe. There are two types of iron pipes, cast iron sewer pipe and schedule 40 steel pipe. Cast iron is joined with hubs, schedule 40 is threaded and joined with fittings. In cast iron 2.5" isn't a standard size, but it is in schedule 40. It's not uncommon to see them mixed in a drain system, usually what you see is schedule 40 for 2" and under, which then transitions to a 2" cast iron hub. The sizes don't exactly match but the hub system is very tolerant.

    The spec sheet for schedule 40 is here:

    https://www.engineeringtoolbox.com/ansi-steel-pipes-d_305.html

    Did you save any of the pieces that were there?

  • Intplm.
    Intplm. Posts: 3,164

    If it's a hub, then you would use a push gasket as mentioned in my earlier post. Please note that plumbing is measured in inside diameter, or I.D. HVAC/R is measured in the O.D., or outside diameter. This is plumbing; all you should need to do is measure the inside diameter of the pipe, not the inside of the hub.

  • Grallert
    Grallert Posts: 1,246

    Definitely cast iron. I think it's 2" but really hard to tell. I've tried a 3" push bushing too big and a 2" is too small. Kind of hard to tell but this is a 4" clamp on the OD of the hub to a 4x2ABS adapter. I wont seal this in cement like it was originally but suspend a poured floor over it in some way to allow access from below. Is this completely hair brained?

    IMG_2877.jpeg

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

    Intplm.
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,365

    Looks like to me.

  • Grallert
    Grallert Posts: 1,246

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Alan (California Radiant) Forbes
    edited August 10

    If the old pipe is in as good a condition as the hub, you're golden. The ABS p-trap with bushing is a good solution and if it doesn't leak when you run a water stream down it with a hose, it passes muster. Just make sure it remains undisturbed as you progress.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GrallertIntplm.
  • DCContrarian
    DCContrarian Posts: 1,594

    It's worse than that. Plumbing is measured in "nominal size."

    There are two main nominal size systems, IPS — iron pipe size — and CTS — copper tube size. An IPS fitting has the outside diameter of an iron pipe with an inside diameter of the nominal size — or did, when the standard was created. Since pipes are joined on the outside, the outside diameter has to be kept constant, even if new materials and manufacturing techniques mean the wall thickness has changed.

    Here are the dimensions of different types of 3" nominal IPS pipe. First number is outside diameter, second is inside diameter:

    Sch 40 steel 3.5 3.07

    Sch 80 steel 3.5 2.90

    Sch 40 PVC 3.5 3.068

    Sch 80 PVC 3.5 2.90

    Note that none of them have any dimension that is exactly 3" but all have the same 3.5" outer diameter.

    Similarly, CTS is based on the outside diameter of a copper pipe with the nominal inner diameter. It's used for copper, PEX and CPVC.

    Here are some specs for 3/4" nominal pipes of different materials:

    Type K copper 0.875 0.745

    Type L copper 0.875 0.785

    Type M copper 0.875 0.811

    CPVC 0.875 0.70

    Type B PEX 0.875 0.709

    Note that none of them have an inner diameter of 0.750" exactly but all have the same 0.875 outer diameter.

    PC7060GrallertIntplm.
  • PC7060
    PC7060 Posts: 1,982
  • PC7060
    PC7060 Posts: 1,982
    edited August 6

    @DCContrarian - Good information. I've always found it crazy that CPVC uses a different sizing standard than PVC.

  • Grallert
    Grallert Posts: 1,246
    edited August 6

    That's what I was/am hoping to hear. I got the adaptor from our local F.W.Webb. The no hub connector fit easily over the cast hub and quite tightly over the adaptor. What you see there is just a proof of concept really. It flows water with out any leaking as is sits now. I will roll that clap over so the nuts are assessable from below if there's an issue in the future.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • mattmia2
    mattmia2 Posts: 18,437

    what i would do i pack it with oakum and that lead substitute stuff to more or less seal and support it then slip that contraption over it.

    or call fernco and get the right doughnut.

    Grallert
  • DCContrarian
    DCContrarian Posts: 1,594

    That will probably work and give years of trouble-free service, but it violates a core tenet of plumbing that a drain line should never decrease in size. The end of that hub is probably 2.5", the no-hub is 3". So you're creating a spot where the water flow will slow and debris can drop out, and then a constriction.

    But it may be the best you can do.

  • mattmia2
    mattmia2 Posts: 18,437

    I would also grind the stop out of this reducer so you can slip the pipe through and in to the hub until it more or less meets the run of the pipe.

    image.png
  • Grallert
    Grallert Posts: 1,246

    That is a really good idea!!!!

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • Intplm.
    Intplm. Posts: 3,164

    It's a 4 x 2 ABS bushing.

    Grallert
  • PC7060
    PC7060 Posts: 1,982
    edited August 7

    I thought that line serviced just the shower and feeds into main drain line so meets smaller into larger criteria.

    Grallert
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,365

    Shower drains don't typically plug up do they?

    I could see things getting hung up with a toilet drain or a kitchen sink especially with a disposal. Of course if someone mops the floor and uses the shower to dump the mop bucket I suppose it could plug.

    Not to spoil the party I don't think MA. allows PVC or ABS in commercial buildings. But I am not a plumber and I won't tell.

    Intplm.Grallert
  • Intplm.
    Intplm. Posts: 3,164

    There is no, or shall I say, has been no indication of ABS or PVC not allowed in a commercial setting.

    The party is still on. 😉