Amana Heat Pump “01” Fault Code
Amana (Goodman) Model #: ASZC180361CA
Outdoor Heat pump unit is throwing a 01 Fault Code (Low pressure CO trip).
Have tried replacing capacitor, and numerous full system restarts. The unit will come on for 1.5 minutes and then shut off. It also shuts off the air handler when this happens. Thermostat and air handler are both calling for cooling, (AC2 displayed on air handler). Attempted holding down “test” button on outdoor unit. No change.
Any thoughts would be helpful.
Thank you.
Comments
-
Low pressure comes from loss of load on the evaporator (usually an air flow issue) or loss of refrigerant feeding evaporator (usually low on refrigerant).
A capacitor has nothing to do with low pressure.
Start with the basics: is your filter clean?
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
yes, everything is clean. Replaced capacitor before noticing the error code.
system is 3 years old.
0 -
Again, if your air flow is good, then most likely the system is low on refrigerant. In which case, the leak should be located and repaired and the system properly recharged.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Did the system ever work correctly?
Was the indoor airflow ever checked?
0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements