I understand the I-series boiler has a switch relay internally for single zone. I have already set up a switch relay and grundfos pump powered separately from my boiler. I have a tekmar smart thermostat already connected to the switch relay. I need to know how to connect my switch relay to the combi boiler. I am thinking the T/T 1 Connection at the boiler to the C and N/O connection at relay but the t/t conn has the three connections C, R and W. Is there a different place in this panel I should connect for call for heat when pump kicks on?

image.jpg image.jpg
PeteA

Comments

  • Jamie Hall
    Jamie Hall Posts: 28,006

    Use R and W on the boiler. C is provided for a common return from powered thermostats.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ok. So c and w on boiler to the n/o and c on relay?

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030
    edited April 25

    R and W will run the boiler. R and W. = Will Run

    image.png

    In this illustration I have fadded out the unimportant parts of your photo and highlighted the important parts of the diagram. Take 5 (COM) from the Taco SR501 and connect it on R for zone 1 of the Rinnai I-Series. Take 6 NO from the Taco SR501 and connect it to W on the Rannai I-Series as shown above.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Posts: 4,790
    edited April 25

    The common and the N/O on the relay really don't matter which go to the R or W on the control board. The ''C" on the control board is not used.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Posts: 4,790

    It just acts like a switch, closed calls for heat, open no call for heat.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Thanks everyone for the direction.

  • 109A_5
    109A_5 Posts: 4,790
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    PeteA
  • pedmec
    pedmec Posts: 1,488

    You know you could have just wired everything up directly to the boiler?

  • 109A_5
    109A_5 Posts: 4,790
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    tcassano87
  • Kaos
    Kaos Posts: 1,008

    Since you are using the P/S kit, the purge valve is also not really needed here, make sure you keep this valve always closed.

    To purge the primary loop, connect a garden hose to the P/S kit drain valves.

    image.png
    PeteA
  • hot_rod
    hot_rod Posts: 28,789

    let’s see more of your piping, how you are using two sets of close tees.

    There may need to be a boiler pump, loop pump, then zone pumps?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    EdTheHeaterMan
  • tcassano87
    tcassano87 Posts: 164

    being able to connect 4 zones directly To the boiler is such a great design

    EdTheHeaterMan
  • PeteA
    PeteA Posts: 328

    Wow these photos can be used as a Webstone and Bluefin advertisement there has to be at least 20 valve handles in just these 2 photos, I see Yellows, Red, White and Blue. This will be one person who will not have any issues isolating any part of this system.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030

    I think there is a rule about how many valve handles you are allowed in a 5 square foot area. You have certainly gone over the allotted amount here. You may get a call form the valve division of the mattress police if they ever get a look at this photo.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    PeteA
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 13,030

    It is a nice looking job!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?