  • mattmia2
    mattmia2 Posts: 18,399

    That is not a knife switch, it is an enclosed safety switch, it is more or less the opposite of a knife switch. They still make more or less that same fused disconnect today out of slightly different materials. Square D invented the enclosed safety switch.

    The requirement for type s fuses appears in the code in the 50's but as far as I can tell it wasn't enforced until the 70's or so.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    So I googed "Knife Switch" and looked at images that were all very much like the one on the right.

    @mattmia2, can you explain how the one on the left is not a knife switch? Does the enclosure make this not work the same way as a knife switch? Does the handle need to be that piece of bakelite of rubber or some other insulating material at the end you lift to open the circuit? I thing this Square D enclosed fused disconnect uses two knife switches in the assembly. But I might be mistaken. I want to be accurate when explaining the facts.

    Screenshot 2026-02-13 at 6.00.33 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • ChrisJ
    ChrisJ Posts: 17,763

    I get your point but I also get Matt's

    I think the term knife switch is almost if not always used to describe open switches.

    Here's a current 3 phase disconnect.

    1000023788.jpg

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Posts: 7,634
    edited February 14

    old electrical switch gear

    These are knife switches

    image.jpeg
    mattmia2
  • 109A_5
    109A_5 Posts: 4,761

    I knew what Ed meant. IMO Safety switches commonly use knife switch 'type' switches for the disconnect means. I suppose in the case of this boiler, it is a safety switch with fuses, since the switch is enclosed and close to the appliance.

    In modern times they usually do not open the Neutral, and the Neutral is not fused.

    @ChrisJ three phase disconnect ??? How about Hot, Neutral and Ground wires ? Just Joking.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ChrisJEdTheHeaterMan
  • ChrisJ
    ChrisJ Posts: 17,763

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    The neutral can be switched as long as a two pole switch is used that breaks the hot wire with the same hand movement.

    As far a fuse in the neutral that is a no-no now but in the old days it was common to fuse the neutral and the hot.

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    a knife switch is open, it isn't enclosed. almost any high current switch's contacts are going to be a bar of metal moving in any out of a pair of contacts, usually rotating on a shaft like in that enclosed safety switch, even high voltage transmission line switches have similar contacts. that contact arrangement in itself doesn't make it a knife switch. you could have a knife switch in an enclosure but in a knife switch you are moving the contact bar directly, usually with an insulated handle on the end of the bar, it isn't moved from outside of the enclosure with a remote handle.

  • 109A_5
    109A_5 Posts: 4,761
    edited February 14

    Since it is an exception, knife switches inside an enclosure must exist.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    square d made their business selling that switch as a safe replacement for knife switches.

    a lot of old theater lighting systems were open slate boards with open knife switches to route the crosspoints to/from the dimmers and open dimmers.

  • mattmia2
    mattmia2 Posts: 18,399

    i like how the code rule says exactly the opposite of the ai "answer"

  • 109A_5
    109A_5 Posts: 4,761

    Yes that is amusing.

    To me a knife switch is a basic style of switch. If you enhance the application of it by putting it in an enclosure and that may also include mechanical interlocks, etc. and you call it a safety switch that is fine too.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    So the consensus is that once you take the parts of a knife switch and place it inside of an enclosure, put a bar on it so you can operate the knife portion from outside the enclosure, then it is no longer a knife switch.

    I'm glad to know this now. I will include this in a chapter of my book called “Scheight that don't make sense”.  I would not want to have anything false in my publication. I will certainly be selling copies of my book in the paddle store I plan on opening at  the top of Scheight’s Creek.   I hear there are lots of folks up there without paddles.  I should make a fortune selling paddles there.  Another business opportunity for anyone keeping score.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2TheUpNorthState88Larry WeingartenGGross
  • 109A_5
    109A_5 Posts: 4,761

    To me the knife switch part is often a sub-assembly of a safety switch.

    I have a boiler that actually boils water to make steam. All you hot water folks have something else, I just don't know what to call it. Apparently no one else does either so they call it a boiler. And if water is boiling inside that is BAD.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • ChrisJ
    ChrisJ Posts: 17,763

    Can we get over the knife switch we all knew exactly what he meant. This is like guys arguing motor vs engine.

    Ed of all people doesn't deserve this.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    Deserve… I thrive on this type of stuff.

    Thanks for your support Chris

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2109A_5GGross
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I agree that the term "knife switch" came from the older open switches. But a modern disconnect, safety switch whatever you call it is still a knife switch IMHO.

    Just like all face tissues are Kleenex and all refrigerators are Frigidaire

  • ChrisJ
    ChrisJ Posts: 17,763
    edited February 15

    and all refrigerators are Frigidaire

    How dare you!!! We don't use the F word in my house.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    EdTheHeaterManGGross
  • mattmia2
    mattmia2 Posts: 18,399
    edited February 15

    did the early meter misers use rubber terminal seals?

    i feel we may have drifted off topic.

    EdTheHeaterMan
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @ChrisJ

    My mistake. All refrigerators are😎 GE

    EdTheHeaterManChrisJ
  • PC7060
    PC7060 Posts: 1,980
    edited February 15

    the pilot on my now replaced 1980s vintage New Yorker 140KBTU boiler was ridiculously big ; added $10 month to gas bill in summer. The boiler had a 40 gallon tank and the pilot was large enough to keep the water at 120f with no demand. 😬
    I always shut it off during off season.

  • 109A_5
    109A_5 Posts: 4,761

    The way I see it, if you want you can shut off the pilot in the summer. IMO Thermocouples are inexpensive and maybe more reliable than Intermittent Pilot ignition modules. For me I'd rather have the reliability when it is cold out. And yes you could have a spare of either, but the Intermittent Pilot ignition module will cost a lot more.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Posts: 18,399

    there are plenty of intermittent pilot systems that work for 30 or 40 years without any attention.

  • 109A_5
    109A_5 Posts: 4,761

    And many that don't. I don't want to find out when it is zero outside on a weekend. I like my heating as simple as possible. It is your choice… I my case, have no desire to replace my old boiler or any of its controls just because I can. To me new is not necessarily better.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    TheUpNorthState88Larry Weingarten
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    I had and old Crane boiler at my house with a millivolt system. Sometime in the 80s (energy saving days) I bought the Honeywell kit with a damper and spark ignition conversion kit and installed it. it worked fine for 25 years.

    First the damper quit so I bypassed it and it was fine for 10 more years. Then it would spark and the pilot would light but wouldn't' prove the pilot. I fiddle with it all weekend. Took the burners, pilot apart and cleaned everything, changed the flame sensor. Ran a separate ground from the pilot back to the control. Checked and cleaned everything. NG

    I got so pissed I put the old millivolt back on and ran it with that until I replaced the boiler.

    I had wanted to measure the microamps but couldn't find the information. I found it after I put the millivolt back in and I wasn't going backwards.

  • 109A_5
    109A_5 Posts: 4,761

    In @TheUpNorthState88's case replacing the boiler's control wiring is a reasonable idea. It provides an opportunity for him to learn the system better, improves the quality of the wiring and to remove unused abandoned equipment. Removing the electrical clutter makes it easier should the system ever need service in the cold of the Winter.

    IMO he does need the right person to do the job. I'd hate to hear that an electrician ripped it apart, got confused and then walked away, or an HVAC contractor just wants to sell a new boiler.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    EdTheHeaterManTheUpNorthState88
  • Steve Minnich
    Steve Minnich Posts: 2,964

    Beautiful boiler. Legal or not, I don’t like the idea of switching a neutral. There is no good reason for it.

    Steve Minnich
    EdTheHeaterManLarry Weingarten
  • ChrisJ
    ChrisJ Posts: 17,763

    What's bad about it? Assuming the hot is switched with it I mean.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Steve Minnich
    Steve Minnich Posts: 2,964

    If the fuse for the neutral fails “open” for any reason and there’s a call for heat, that 120 volt supply source is going to start looking for a way to complete its circuit and will usually find one. I’ve seen it happen where a printer or computer somewhere else in the house gets cooked by getting hit with 240 volts.
    It’s the same reason if you’re disconnecting a connection on a receptacle live, you always remove the hot wire first, then the neutral. You may ask why someone would do that? Well, I’ve done it hundreds of times because it speeds up the process and it’s safe if you know what you’re doing.
    I live, unfortunately, in Vegas now. I spent 60 years living in Chicago or it’s close by suburbs. I started in the field in ‘80 and as far back as I can remember, breaking a neutral with a fuse was against code. I was a Tinner and later strictly a boiler guy, I got my electrical license early and had it until 2018. The inspectors in the city would tag and lock that in a heart beat.

    Steve Minnich
    EdTheHeaterMan
  • ChrisJ
    ChrisJ Posts: 17,763

    I'm sorry, you said switching not fusing, so I went off of that.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Steve Minnich
    Steve Minnich Posts: 2,964

    I was referring to that specific box where the fuse would have the same effect as a switch. Just use a wire nut.

    Steve Minnich
    ChrisJ
  • mattmia2
    mattmia2 Posts: 18,399

    the 2 pole switch is ok but unnecessary, the fuses are the problem. maybe try a penny….

    EdTheHeaterMan109A_5
  • @109A_5


    And here’s the thing, after confirming both the vintage aquastat works as intended and the mercury shutoff most likely works (I'm not draining the system down to test low water shutoff), even with the "questionable" wiring scheme discussed here. I'm just going leave well enough alone. With the wiring being BX that's not damage, or frayed, everything is tucked away in metal boxes/conduit. I don't want to chance things. I have a good electrician, but this boiler, and all its components predate us both by many decades. Not mention, it's the simplicity of every component. Not one computer chip insight here. Literally, everything is pure mechanics. Many of the comments here (even when things strayed a bit off topic) have influenced my decision.

    As many say in the trade, all these old systems worked beautifully when first installed. It wasn't until people started "fixing" stuff did they stop working optimal. I can honestly say nothing has really been changed on my system and it shows because everything works so damn well.

    Thank you,

    Lifelong Michigander

    -Willie

    Steve Minnich
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    LOL

    Yeah > like > until someone does you a "favor" > fur sure > and puts a fuse in there for you. Like maybe a 10 amp fuse while the hot has a 20 amp fuse. They heard that putting a penny in those fuse holders was a No No!

    It's the same as the neighbor closing a basement window while he was watching your house, while you went skiing for a week in Aspen. You come home to a sooty mess because of that favor that shut off all the combustion air. That is why you need to follow the code. A permanent combustion air inlet is required, not an open window that can be closed by your friend.

    I could give you hundreds of "Good Enough" fixes, just like those examples, that would not pass a code inspection. Just do it right!

    (NEC 404.2) Only the ungrounded (hot) conductor may be switched.
    A grounded (neutral) conductor shall not be connected to a switch unless the switch is listed and identified for that purpose.

    So why is there any discussion on this topic. I was taught that rule over 50 years ago. Of course there are exceptions to that rule but a gas burner in your basement is not one of those exceptions! Don't do it! Fix it if you find it. or have the customer call an electrician to fix it if you find it. Note it on your work order. That way you are not liable if something comes up about it later.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Steve Minnich
    Steve Minnich Posts: 2,964

    I’d buy that boiler just to display in my shop and like you, I would keep it forever unless the block breaks. The key is finding a heating controls guy who also understands combustion analysis.

    Steve Minnich
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,952

    Sorry I'm retired. and my wheelchair probably can't get down that basement.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Steve Minnich
  • Steve Minnich
    Steve Minnich Posts: 2,964

    I’m in the same predicament. I have a motorized and a manual, but not one that can navigate stairs.

    Steve Minnich
    EdTheHeaterMan
  • mattmia2
    mattmia2 Posts: 18,399
    edited February 17

    The disconnect switch(which can be an ordinary toggle switch) and the transformer are the only parts that need to be protected. The rest could be replaced with modern thermostat wire dressed with zip ties and anchors and bushings.

    If it were mine I would bring a new dedicated circuit(code requirement, the load is tiny) in to a new switch and transformer, remove all the existing wiring keeping the t-stat wire and wire all the controls and safeties in series from that new transformer to the gas valve with new t-stat wire using bushings/grommets in the various controls where the loom/bx/flex connects now and adding anchor points as needed.

    Some of the safeties are switching line voltage I think because it had an oil burner at some point. Those can be moved to the 24vac circuit.

    You should also rebuild the lwco if it hasn't been apart in a while.

    It has already been reworked several times and has remnants of old things that are no longer there hanging around.

  • TheUpNorthState88
    TheUpNorthState88 Posts: 145
    edited February 17

    @Steve Minnich @EdTheHeaterMan

    As I have invited others, if you are ever passing through or visiting Michigan, you are welcome to see it all in person. Attic expansion tank included haha! I will happily give tours, this is a very niche group here so it not like most folks would even care to see any of this.

    Lifelong Michigander

    -Willie

    Steve MinnichEdTheHeaterMan
  • mattmia2
    mattmia2 Posts: 18,399
    edited February 17

    This is what the michigan residential code says about switching neutrals:


    E4001.8 Grounded Conductors