Landlord states the building heats very well
The landlord states that he has owned this unit for 5 years and has never had any issues with heating. One pipe steam system - air vents on each radiator. Each radiator has a thermostatic trap on the supply line - the bellows are all still in place in all of the traps. No steam vent at the end of the main. No signs that this was ever a 2-pipe system. Unless all of the traps are failed in the open position, how would the steam ever enter the radiators? By the looks of it, the piping has been this way for a very long time. How has it worked like this for so long?
Near boiler piping is also incredibly incorrect but thats another story.
FYI - boiler is being replaced this week, removing all thermostatic traps and replacing with rad valves, replacing all rad steam vents, and adding steam vent towards end of steam main.
Located in the suburbs of Philadelphia.
Comments
-
Philadelphia has more than its share of steam boilers piped by "good hot water men", which is NOT a compliment; but I have never seen anything like that. I don't see how it worked at all.
—
Bburd0 -
I hope they don't have the same installer LMAO. As soon as you find out what make and model and size they are installing I'd download the installation manual and ride them like a hawk. Print out the near boiler piping and gas valve instructions and hang it in the basement lol.
0 -
Haha, I am the new installer. Existing boiler is 275 sqft steam, oversized - current EDR is 105 sqft between all of the rads (small twin home - only 5 radiators). When my service tech was on site, I had him facetime me to confirm what he was telling me was accurate. I immediately called the landlord to ask if he has had any issues with the heating system to which he replied, "none".
1 -
Me either. There has to be a second connection to the rad for it to work. That Trane B1 trap is way too small to do the job. Are all the rads like this?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Not wanting to speak out of turn here;
I hope that they eliminate all the copper, install a skim port, install a double drop header, install a proper Hartford Loop with the shut off valve and dual immersed low water cut offs unless they use one autofill valve with the blowdown valve and a separate low water cut off.
I think It would be ideal if they made a Tee and union off the new pig tail so the pressuretrol and pressure gauge were at both ends of the Tee to allow easier cleaning of the pigtail.
0 -
maybe if you crank the pressure up enough it forces the steam trap open. the riser is too small even if it weren't choked down by the seat in the steam trap and plugged by the element closing on the steam. the radiators must be filling up with condensate until the cycle ends too
0 -
-
-
-
Seems like an @ethicalpaul experiment to me. Although different traps may close and be capable of holding back different pressures.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Too specific of an experiment for me, and I only own a single trap 😅
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Would someone please explain in layman's terms what the main problems are here?
I'm just curious.
Thanks!
0 -
Let me preface this by saying I know zero about steam heat - am I'm not exaggerating that (although I'm fascinated by steam heat and read every thread about it).
But I remember a published story from a very old golf pro who commented on a golfer whose grip was wrong, his backswing was wrong, his downswing was wrong, his follow through was wrong, and yet he somehow managed to get the ball in the middle of the fairway almost every time. So I wonder if by some weird combination of mistakes if all these things so wrong somehow managed to provide a fairly decent working heating system? 😅
1 -
The issue is that thermostatic traps allow air and condensate pass through, but not steam. When the steam hits the bellows, the alcohol content will expand and close the passageway. In this case, not allowing any steam to enter the radiator. So theoretically, none of the radiators should be heating (assuming that the traps are functional).
On a 2-pipe system, the trap is typically located on the outlet of the radiator. On start up, the air will vent through the radiator and expel out of the main vent which should be located on the end of the return main. When the steam enters the radiator and hits the thermostatic trap, the trap will close and lock the steam in the radiator until it gives off enough heat to condense back to a liquid. The condensed liquid will cool the trap off enough to open it and allow the condensate to return to the boiler.
0 -
Ive seen countless systems that are piped incorrectly and still manage to heat. Whether they are working "efficiently" is a different story.
In this case, the only way that steam could possibly enter the radiators would be if all of the traps failed in the open position.
0 -
I'd love to see this job………………..
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
Thank you so much! Now I see why this the general reaction to this is alarm and amazement.
I have no experience with thermostatitic traps, so now I know — thanks.
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 121 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.8K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements