Cost to replace boiler sections

Options
josephny
josephny Member Posts: 407

Today I found that out the my EG-95 (400kbtu) gas boiler (small apt building) stopped working because it has a couple of leaking sections and something happened last night where the flame spilled out and burned some wires.

The boiler service company recommends replaceing all the sections, which means tearing it all apart (including the header), and the burner base.

I don't want to violate any rules of the board regarding pricing. Can I ask for a ballpark of what this job should reasonably cost?

Location is Brooklyn, NY.

Thank you.

Mad Dog_2

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,388
    edited January 6

    Yeah you can't ask price .. I can tell you it an't cheap .. I would say your lucky to find someone to do the job in this weather, as a thought .. Better luck for the New Year

    There was an error rendering this rich post.

    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,729

    @josephny

    How bad is it leaking? Can you get by for 3 months?

    How old is it?

    Are they talking a complete new boiler or just sections?

  • mattmia2
    mattmia2 Member Posts: 15,749

    could you pour some sealer in it and get by until spring?

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,437

    There are too many variables to shoot you a ballpark price, even if we could. Unless it is a very large boiler, changing sections will usually not be worth it. You need to do your due diligence and get several quotes from local licensed and insured boiler contractors. Then, you'll see if your in Fenway or Yankee Stadium. Mad Dog

    CLamb
  • josephny
    josephny Member Posts: 407

    @Big _Ed_4: I've had a long standing relationship with the current boiler company, and I have a service contract (which effectively means they will service my boilers at full price vs. without the service contract where they will not service my boilers). This goes directly to your understanding that I am lucky to find someone.

    @EBEBRATT -Ed: Service guys say it is full of crud and no way they can get it working. It's not old -- less than 10 years. They said they recommend just swapping the sections.

    @mattmia2 : Service guys say no. I specifically asked about getting through this season.

    @Mad Dog _2: EG-95, 400K, I don't know how many sections.

    My problem is I have tenants who are rightfully pissed off because they are cold, so no time for due diligence (which I would certainly prefer to do).

    I have the water level on this boiler (and all my boilers) checked and skimmed at least weekly. What I don't have is a full service done annually -- I need to get that in place!

    Thank you all, as always!

  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,437

    Go rent some electric heaters. Takes the pressure off. You have one chance to do this right or suffice consequences $$$$$ the next 25 years..mad Dog

    STEAM DOCTORmattmia2
  • mattmia2
    mattmia2 Member Posts: 15,749

    lots of contractors that will work on Brooklyn, look in find a contractor at the top of this page.

    if it has been properly installed and serviced, why is it leaking after less than 10 years?

  • Big Ed_4
    Big Ed_4 Member Posts: 3,388
    edited January 6

    Sometimes we just have to throw money at it :)

    Working Brooklyn you know ..

    There was an error rendering this rich post.

  • Intplm.
    Intplm. Member Posts: 2,846

    Replacing the sections? All of them?! That sounds like an entirely new boiler. Get it done but first find out why this boiler failed so prematurely, and get that corrected.

    Meanwhile,add some boiler seal to mend the leak, this will buy you some time till the repair, or should I say replacement is done.

  • josephny
    josephny Member Posts: 407

    All sections scheduled to be replaced today.

    The potential problems from tenants calling NYC and filing complaints, or using electric heaters which will still not satisfy tenants and introduce some degree of safety concern, combined with the likely cost of providing heaters for every room in every apt and the likely demand for a rent break is just not worth delaying this any.

    I think monitoring water usage is a great idea. I think the water feeder copper line is 1/2". What would be a light weight, simple water meter to install?

  • Intplm.
    Intplm. Member Posts: 2,846

    Interesting. @josephny How did you come to the conclusion to replace all of the sections and not replace the boiler?

    Here is one type of water meter to consider. This is a Neptune T-10. Some have a remote reader that can be used without having to enter the building.

    shopping.jpeg
  • josephny
    josephny Member Posts: 407

    Replacing the sections is what the boiler service company suggested, and would be substantially less expensive

  • Intplm.
    Intplm. Member Posts: 2,846

    Wow. I would not have thought that. Go figure.

    Please post how things went.

  • mattmich
    mattmich Member Posts: 221
    edited January 7

    » IMHO for an EG properly installed to fail in 10 years probably means one thing. Excessive MU water.

    Yes.
    And we have the explanation right here from the owner.. so long as "skimmed weekly" is really what happened. Checking is good, skimming should not be necessary on a ten-year-old boiler.

    » I have the water level on this boiler (and all my boilers) checked and skimmed at least weekly

    I'm thinking that policy needs some revision to make the new sections last.
    The other mystery that did not get sufficiently addressed is

    » replacing all the sections

    "All the sections" — other than the jacket and the firebox, that's the entirety of the boiler.

    I do understand the idea of getting things up and running post haste, but it'd be good to get an understanding of what's going on for the future. Take a good look at the old boiler pieces to see what caused the trouble.

    Maybe the best thing would be to quietly find someone from this forum to come in for a consultation. That would not ruffle any feathers with your existing provider and be a great investment.

    cheers -matt

  • Big Ed_4
    Big Ed_4 Member Posts: 3,388

    Your boiler uses O-rings construction , if you have the mussel it is not a bad job …

    There was an error rendering this rich post.

  • josephny
    josephny Member Posts: 407
    edited January 7

    I think I misused a term.

    I wrote skimming but I think my understanding is incorrect.

    I just meant opening the drain valve for 10-20 seconds to remove the water that accumulated dirt.

    I was instructed to do this weekly during heating season from the boiler company.

  • josephny
    josephny Member Posts: 407

    Heat is up, but they're putting finishing touches on everything.

    WhatsApp Image 2026-01-07 at 3.46.43 PM (1).jpeg WhatsApp Image 2026-01-07 at 3.46.43 PM (2).jpeg WhatsApp Image 2026-01-07 at 3.46.43 PM (3).jpeg WhatsApp Image 2026-01-07 at 3.46.43 PM (4).jpeg WhatsApp Image 2026-01-07 at 3.46.43 PM.jpeg boiler2.jpeg boiler3.jpeg boiler4.jpeg boiler5.jpeg
  • ChrisJ
    ChrisJ Member Posts: 17,097

    I assume you mean cleaning the LWCO?

    I'd dump it until the water runs clean, 10-20 seconds seems awfully long. I'd expect 5 seconds honestly.

    Also, make sure you do it with the burner running so you can confirm the burner shuts off. If it doesn't, the LWCO isn't working and needs to be addressed immediately.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 17,097

    Curious,

    How are you going to skim that new boiler? They didn't install a way to skim it that I can see?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Big Ed_4
  • mattmia2
    mattmia2 Member Posts: 15,749

    why is the old one sooted?

  • josephny
    josephny Member Posts: 407
    edited January 7

    There was some incident (I don't know exactly what happened, but I assume a big splash of water from a leak occurred) that triggered this whole situation. That's when the soot appeared, burned the wires, and brought down the boiler a couple days ago.

    I'm going to install a water meter on the MU water feed on this boiler (and other boilers I have) because it sure sounds like (from the experts here) that excessive MU water is what cut my boiler's life by more than half.

    It's not surprising, unfortunately, because (and I'm grateful for the opportunit to vent a little here), I have tenants who will go a month or two before letting me know that they are ready to "escalate" the problem of the steam leaking from a radiator and ruining their items and their quality of life — of course, the idea that they would sit quietly on this info for months and then threaten to escalate an issue that I did not know existed is bizarre, but combined with the fact that I have a very healthy relationship with my tenants (they tell me about a problem and I take care of it ASAP) it's just incomprehensible. (This is a true story that just happened yesterday at another building — turns out the radiator valve had a crack.)

  • josephny
    josephny Member Posts: 407
    edited January 7

    I believe I used the incorrect term. I should have said "clean the LWCO."

  • josephny
    josephny Member Posts: 407

    It very well could be less than 10 seconds.

    Excellent tip on doing it with the boiler running to confirm the LWCO is working. Many of my boilers have both a float and a sensor type LWCO. Drain from the float, right?

  • mattmia2
    mattmia2 Member Posts: 15,749

    only float type LWCOs require a weekly or so blowdown.

  • mattmia2
    mattmia2 Member Posts: 15,749

    i understand why they don't tell you, it is a pain to contact someone and describe the problem with them, then deal with someone in your home fixing it.

    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 17,097

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2
  • Big Ed_4
    Big Ed_4 Member Posts: 3,388

    Why did they use the old gauge glass assembly ?

    There was an error rendering this rich post.

  • mattmia2
    mattmia2 Member Posts: 15,749

    you can see some signs of minor leakage in the pictures that would likely have been there if it was inspected at the beginning of the season. it doesn't look like it was a major leak but it is hard to tell from pictures. it however looks very sooted and that didn't just happen last week.

  • Big Ed_4
    Big Ed_4 Member Posts: 3,388

    Bad O-rings

    There was an error rendering this rich post.

  • josephny
    josephny Member Posts: 407

    I would very much like to know why this happened also.

    I assume by soot you mean the black carbon on the surface. I don't know if you mean the soot on the boiler blue case panels or on the sections.

    All I know is what I'm told and the little I've learned. I'm told they did a flood test and the boiler had a substantial leak from multiple sections and was full of crud. Does that report, together with the pictures, fit an explanation of excessive MU water over the a substantial period of time? I have suspected for quite a while that it was using far too much MU water, and did a diligent search throughout for any leaks, finding quite a few vents, radiators, and valves with leaks.

    Only float type needs cleaning? So a boiler with only a sensor type doesn't need to have dirt removed from the water on a regular and frequent (weekly?) basis?

  • mattmia2
    mattmia2 Member Posts: 15,749

    well, both, but it is outside the jacket because it has been inside the boiler block for a while. gas should produce no soot if it is burning properly. I don't know if the steam leaking can cause the sooting, it doesn't seem like it would but i'm not an expert on combustion. you can see that it is burning very yellow in one of the early pictures so it isn't burning right for some reason. the soot caused the rollout. i don't see why it couldn't have been brushed and vacuumed and whatever was wrong with the combustion fixed and the leak wait until spring but i might be missing something.

    A probe type lwco should be disassembled and cleaned once a year but it doesn't need weekly maintenance.

    the blowdown of the float type lwco is to make sure the float isn't stuck and to remove sediment from the float bowl.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,639

    This water feed has a digital counter. It is not accurate to the ounce, but it will give you a ballpark of how much Make Up water you are using. And that is all you are looking for, and you need a water feeder anyway. Hydrolevel water feed with digital counter.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • ChrisJ
    ChrisJ Member Posts: 17,097

    I don't understand why they reused any of the old stuff?

    Does the cost of the boiler jacket, burner assembly etc even register compared to the block and the labor to pull all of that apart and reassemble?

    It seems to be done often tho, so there must be a reason.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Member Posts: 6,818

    Could be a Permit thing!

  • ChrisJ
    ChrisJ Member Posts: 17,097

    Like knocking an entire house down but leaving 1 wall etc…

    Interesting point.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ethicalpaul
    ethicalpaul Member Posts: 8,195

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/