At the beginning of last winter i've zeroed out my automatics water feeder. At the end of the season it read 247… Not good!

Opening the boiler covers i saw a sorry state of the boiler's top - with huge rust holes. 

PXL_20250813_133512529.jpg

I though i could seal it with some kind of steam-resistant high-temp epoxy.
I've searched long and identified some pro epoxies uses used in the oil industry. Sales rep has confirmed that it could work (key word: "sales rep"...)

I cleaned up the surface prepping it for the epoxy. I filled the holes with the marine version of JB Weld (btw, very good epoxy!)

PXL_20250826_224841888.jpg PXL_20250829_033427798.jpg

Then covered the top with the "pro" grade reinforced with some carbon mesh.

PXL_20250901_023642791.jpg

Soon i started having doubts.
In my research i didn't consider high temperature of the flue gases. Though metal jacket heats up only to around 250F, the surrounding flue gases can get to 600F (the verge of the epoxy stability).

Even before fire test, i started thinking about plan B.

Test fire has confirmed my doubts.
The surface, despite the prep, showed epoxy delamination due to rust developing between epoxy and the cast iron. Surprisingly, the water resistant JB Weld held quite well.

PXL_20250913_202548707.jpg

The boiler was "dead" again so i removed the epoxy and this time chose not to stop until i found some solid metal. The holes kept on growing...

PXL_20250914_012926746.jpg

I started to think the whole cast iron section turned into a clump of rust held only by wishful thinking. That said, i started to see some hope. Some chunks were still quite thick. If i could manufacture metal plates, drill then tap some holes to hold those plates then maybe - just maybe - i could get another heating season out of this boiler.

I drilled some holes in strategically located places. Surprisingly all had enough metal to tap those with at least a few threads.

PXL_20250916_222311115.jpg

Some extreme heat silicon (rated at 750F) was applied to create gasket between cast iron and metal plates.

PXL_20250918_230138515.jpg

The plates were bolted onto the boiler with stainless screws (ah, why not at this stage?).

PXL_20250918_234201865.jpg

After a few days of firing, so far so good.
Wish me luck this heating season!
(i'll update you as the months go on)

»»» See my steam heat YouTube videos:
https://www.youtube.com/@HeatingBlog

Mad Dog_2109A_5GrallertAlan (California Radiant) ForbesRobert O'Brien

Comments

  • Steamhead
    Steamhead Posts: 19,007

    Never seen that done before- it'll be interesting to see how it works out. That said, start saving for a new one. And make sure there aren't any leaks out in the system- fresh water shortens the life of a boiler.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    Mad Dog_2109A_5
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328
    edited October 2025

    Yeah, I would start saving………….and I would save fast! I don't know if you're going to install the new one yourself or not but if it was me, I would size the new boiler and have it in the basement on standby.

    But I commend your ingenuity you did a neat job. Just doubt it will last.

    Alan (California Radiant) Forbes
  • mattmia2
    mattmia2 Posts: 18,399

    The boiler itself isn't all that expensive, for that amount of work you could have replaced it.

    jim s_2ethicalpaulSlamDunkJohnNY
  • ethicalpaul
    ethicalpaul Posts: 9,075

    It's kind of ironic…the boiler will have to be replaced, there is 100% no doubt of that. The question is when. You have gained a year or maybe 3, and boilers will be more expensive then, so unless you are investing all that money in something that can beat inflation, you just cost yourself money in addition to all your effort.

    When you get a new one, be sure to size it to your radiation, the existing one is almost certainly oversized.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ChrisJ
    ChrisJ Posts: 17,763
    edited October 2025

    I'm not so sure I agree. They're far from free, that's for sure.

    It seems like boiler prices have gone through the roof vs when i bought mine back in 2011. I understand inflation etc, but it just seems like it's far more than that. Off the top of my head, I think my EG series costs double what I paid yet I think inflation is less than 50% since then.

    Maybe I'm just remembering wrong.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Grallert
    Grallert Posts: 1,237

    You know what else you could do? Add some sodium silicate to the boiler, flood it and bring it up to near boiling. That water glass will find any small hole and seal them.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • ethicalpaul
    ethicalpaul Posts: 9,075

     I think my EG series costs double what I paid yet I think inflation is less than 50% since then.

    Inflation of your boiler, according to what you said above is 100%. The inflation of eggs and stuff isn't relevant to this.

    I should have said "…so unless you are investing all that money in something that can beat boiler price inflation…" for clarity

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    ChrisJ
  • mattmia2
    mattmia2 Posts: 18,399

    The price of construction materials has gone up a lot faster than average inflation because of demand in countries that are transitioning from rural to urban environments. The materials to install my 100' of gutter with stainless hardware and 100' of fiber cement fascia cost over $2k.

    GGrossChrisJ
  • ChrisJ
    ChrisJ Posts: 17,763

    They're using a lot of cast iron boilers in these transitions?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Posts: 18,399

    they are using a lot of steel which drives up the cost of cast iron.

    ChrisJ
  • SlamDunk
    SlamDunk Posts: 1,831

    necessity is the mother of invention. That actually looks pretty good.

    The temperature changes and different expansion rates of the two steels may cause looseness in the bolts, so maybe check their torques until you are comfortable they wont loosen.

  • At this moment, the boiler is a "science experiment".

    Will it last? Yes, it will.

    How long? Noone knows.

    Yes, when i see a sign of leakage, i'll clog all my radiator vents with temporary plugs and add some boiler stop-leak (so the vents don't get clogged with that stuff)… after all, with 250 fresh water units in one season, this thing has drank itself to death.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • mattmia2
    mattmia2 Posts: 18,399

    the fresh water will corrode everything below the water line, not just the boiler.

  • ethicalpaul
    ethicalpaul Posts: 9,075

    I disagree with that, but different opinions is what makes the world interesting!

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • patrykrebisz
    patrykrebisz Posts: 168
    edited October 2025

    "The speed of corrosion for a metal is highly dependent on its specific location relative to the waterline. Generally, the most aggressive corrosion occurs not when the metal is fully submerged or completely dry, but in the area that is intermittently wet, known as the splash zone or waterline region."

    Which puts in question how my specific corrosion has occurred.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • ethicalpaul
    ethicalpaul Posts: 9,075
    edited October 2025

    That boiler in particular (if it is, as it appears to be, a Burnham IN series), but lots of other boilers too, maybe all atmospheric boilers, rust out at the top I believe because at the top the temperatures are hottest from the lack of liquid water up there

    There are a few variables that affect rusting rate and temperature is a significant one of them

    There is some discussion out there that the IN boilers' castings may be thin up there as well but I have no personal knowledge of that.

    Keep in mind the entire interior of that style boiler probably isn't very dry ever.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 1 month later and the boiler is going strong. just 1 gallon of fresh water intake so far (and i'm sure it's my radiator vents).

    i'll take the covers at the end of the heating season so we can "learn" something from this experiment.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

    pumpcontrolguy
  • ChrisJ
    ChrisJ Posts: 17,763

    If you lost a gallon of water from vents etc during an extremely mild month, I'd start working on that as it's likely why your boiler rotted out.

    Obviously weather is different all over, but I haven't added water since last March or so.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaul
  • patrykrebisz
    patrykrebisz Posts: 168
    edited November 2025

    Congrats on having tight system!

    1gallon/month (around 6 per heating season) is within the specs of this boiler.

    That said, due to history of extremely high fresh water intake (assuming that the water counter wasn't zeroed out at some point, around 600 gallons), this boiler will fail sooner rather than later. So whether it's 1 gallons or 2 per month isn't of consequences at this point.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

    ethicalpaul
  • ChrisJ
    ChrisJ Posts: 17,763

    There's certainly no need for sarcasm.

    A gallon a month in a mild month is bad.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • 109A_5
    109A_5 Posts: 4,759

    Might as well repair the consumption issue before a new boiler is installed.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ChrisJ
  • Without a little sarcasm, life would be a bit boring.
    My point is: let’s not lose sight of the forest because of the trees.

    The fix works and drastically reduced water intake — and therefore energy consumption as well.

    Moreover, your idea of “mild” might be very different from mine. My neighbor keeps his house at 68F; I keep mine at 74F. I bet his boiler hasn’t fired even once this season, so one gallon for him means something quite different than it does for me.

    When a new boiler is installed in a season or two, if I can average 6 gallons per year in fresh water intake, I’ll be ecstatic. I’ve seen what 600 gallons can do to a 10-year-old boiler — AND that it can still have just enough metal left to survive another season (or two?).

    As i mentioned before, this boiler is now a working "science experiment." I'm not sure if reducing the water intake further will serve us much.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • ChrisJ
    ChrisJ Posts: 17,763

    Understood, the boiler is an experiment.

    The rest of the system isn't and it will greatly effect your next boiler. If you used a gallon in October, it's going to use a whole lot more in January-Febuary.

    The point is, start fixing the rest of the system while you've got time and that way when it's new boiler time you won't even have to look at it, it'll be done.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Posts: 18,399

    If you look at the indoor temps of 68 and 74 on a mild day, 45 to 68 is 23 f degrees and 45 to 74 is 29 f degrees. That is only about a 20% difference in heat load.

  • patrykrebisz
    patrykrebisz Posts: 168
    edited June 12

    UPDATE:

    Yesterday, since the heating season is over, I opened up my boiler to see how it held up (it has been in service the past 8 months). I knew the fix wasn't permanent because i still had significant water intake - 110 gallons during that time: some due to the boiler leaks, some to a failed vent, some due to a tiny steam leak one on of the pipes.

    A few notes:
    > The boiler rusts from the inside out, so if you see holes, there may be much more rust inside. This also means that other parts of the boiler can rust through, exposing new holes.

    > It's shocking how untreated metal plates (painted on the top but not on the bottom), about 4 mm thick, can rust through completely.

    > Rust is a powerful force—it can deform thick metal plates (see photo 7). This also means that non-mechanical repairs can fail miserably. That said, the epoxy on the right side (near the hinge) did hold up, even though the metal underneath rusted through.

    Here are the results:

    PXL_20260612_020841428.jpg PXL_20260612_020949863.jpg PXL_20260612_020952473.jpg PXL_20260612_020955506.jpg PXL_20260612_020958300.jpg PXL_20260612_021518019.jpg PXL_20260612_021522844.jpg PXL_20260612_021526138.jpg PXL_20260612_021648526.jpg PXL_20260612_021651419.jpg

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

    mattmia2pumpcontrolguy
  • mattmia2
    mattmia2 Posts: 18,399

    the plate rusting through probably in part is because of the huge amount of fresh water it is still taking on. that will happen to the piping too so you probably want to replace the boiler and fix the other leaks asap.

  • pecmsg
    pecmsg Posts: 7,634

    My point is: let’s not lose sight of the forest because of the trees


    that boilers shot!

    mattmia2Steve Minnich
  • 109A_5
    109A_5 Posts: 4,759

    I take it the sheet metal was not stainless ? I would have used stainless steel sheet metal. It would not stop the CI from rusting but it may have stopped (or slowed down) the holes through the sheet metal.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • patrykrebisz
    patrykrebisz Posts: 168
    edited June 13

    If i had to do it again:
    1. Skip epoxy

    2. Drill and tap + high temp silicon (as i did)

    3. Paint the metal plates both on top and bottom.

    4. Understand that you will get 1 season out of this repair, but that's about it. (notice the red bubbling on the sides, indicating that even if the plates didn't rust through, other parts would open up.

    »»» See my steam heat YouTube videos:
    https://www.youtube.com/@HeatingBlog

  • mattmia2
    mattmia2 Posts: 18,399

    you can pack lead wool in the hole too instead of putting a plate over it.

  • 109A_5
    109A_5 Posts: 4,759

    What paint did you use ? It seems to hold up well to the combustion gasses. I wonder how well it would hold up inside the boiler.

    I'd maybe skip the paint on the sheet metal and use stainless steel sheet metal. Then the issues is minimizing the CI rusting where the corrosion was cleaned off for the sealing of the heat exchanger. I'd probably coat all shiny CI with the high temp silicon, not just make beads to seal the heat exchanger. Help mininize the rust jacking.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • mattmia2
    mattmia2 Posts: 18,399

    the top of the casing probably doesn't really get all that hot, probably not a whole lot above 212 f because the mass of the casting takes the heat away so high temp paint would do great there, even ordinary paint would probably be ok.

  • 109A_5
    109A_5 Posts: 4,759

    Hmmm… Why did the center section patch hold up better than others ???

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Intplm.
    Intplm. Posts: 3,160

    Pretty interesting repair. Maybe consider using a boiler seal product after installing those plates.

    Again. A very nice repair, it got you through the winter.

    Grallert
  • pedmec
    pedmec Posts: 1,488

    That's a great experiment. Pretty interesting stuff going on. I will bet if you caught the leaking heat exchanger earlier you might have had better luck with the plates holding up. The holes in the HX were pretty big to try and patch up. Plus the different materials expanding at different rates didn't work in your favor.

  • Robert_H
    Robert_H Posts: 377

    I have to say, I really admire your tenacity and ingenuity. I have nothing to add to all the good advice here but Damn, I am impressed!