Warren Webster 02H thermostatic radiator traps
Comments
-
I'll have to find my yellow pad that I did all of my radiator math on.
0 -
0
-
It appears that my boiler is sized properly. However with the sunroom and attic radiators shut off it is slightly oversized.
0 -
From my 1935 Webster catalog :
0 -
so the check valves mean it can equalize the return to the boiler without equalizing the return main.
0 -
Do you have any of this equipment ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Yes, it's still all in place and connected to the system.
0 -
-
Well, if it was my system, I'd definitely get a gauge or a home brew water Manometer on that system so you can see what is actually going on. Depending on that vent valve this system may normally fall into a vacuum at times, assuming the rest of the system is still air tight.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I'm very aware of using it sparingly. As a professional mechanic I know that it gets everywhere.
0 -
I used some Dow Corning 111 silicone grease on the threads and "O" ring of my B & J Bigmouth vent, the jury is still out.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
One home brew water manometer as an example.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I also have Blue Monster pipe dope on hand
0 -
I believe the system is pretty tight as well. I did fix a couple of minor leaks at the radiators over the winter which were just loose nuts to one of the valves and one return trap and then the packing nut on the valve in the upstairs guest bathroom was loose.
0 -
Traps can fail open or closed. Usually open.
0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 71 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 392 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 46 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements