Monoflo tees
what is everyone’s opinion on monoflo tees oriented so that the branch is laying flat up against the floor joist? 3/4”x1/2” “scoop” tee? Should I use two monoflo tees instead of one on the return? Kickspace is above. About 15-20 feet of branch piping. I’ll have the tees about 13” apart, that’s all the room I have.
Thanks guys
    A monoflo tee has a physical partition that divides the flow. that does a lot more to encourage flow in the branch than the pipe between tees. One or 2 depends on the resistance of the emitter and output and if it is above or below the main.
    cm6230
  • would having the tees lay flat matter? Instead of looking up or down?
    cm6230
    It shouldn't make a difference. You will need a bleeder on the emitter because you won't be able to get the kind of flow you need to purge the emitter. That isn't specific to the tee orientation but because it is monoflo.
    cm6230
  • thanks guys, appreciate your feedback!
  • Ironman
    Ironman Posts: 7,975
    15-20 feet of branch piping is a concern with only 13” between the Tees. The basic rule is that you should have as much spacing between the Tees as there is in the branch. Two Monoflo Tees will help, but I’d be concerned about that much branch piping with only 13” between the Tees.
    A small circulator with two closely spaced standard Tees (primary/secondary) would be a sure solution.
    Bob Boan
    cm6230EdTheHeaterMan
    You could put a balancing valve on the main between the tees if you aren't getting enough heat from the emitter. Use long sweep 90's on the branch and use 45's and an offset wherever you can, 90's will be more restriction than the pipe itself.
    cm6230
  • Big Ed_4
    Big Ed_4 Posts: 3,585
    I would use two MF tees for a kicker and add a purge set .. so you don't have the need for a constant rise …
    cm6230