Can you help identify my B&G boiler pump? Possible replacement? Repair parts?

TomAuciello
TomAuciello Member Posts: 4

My home in Seattle is 95 years old with the original hydronic heating system.  Built in 1931 as a gravity fed system, it was modified in the early 50’s (estimated) to add a circulation pump when a second floor living space was added.  That pump has been working for approximately 75 years and I am concerned about how much longer it will function.  

I was wondering if anyone could help me identify what model of pump it is and if it is still possible to get repair parts for it.

If it is too old to continue to maintain, would you have an idea of what kind of modern pump could replace it?

The system has been operating well, heating the house for the 45 years that I have been living here.  There are no issues with water circulation.  A couple of years ago it threw a spring on the coupler and I was able to find a “common” replacement (Bell & Gossett 118705), but still haven’t identified the pump’s actual model number. 

I really like this web site. Any help would be greatly appreciated.  Thanks much! —Tom

Attached are some Photos:

IMG_3331.jpeg IMG_3336.jpeg IMG_3339.jpeg IMG_3345.jpeg IMG_3340.jpeg Boiler Pump Replacement.jpg IMG_3334.jpeg IMG_6962.jpeg
diego

Comments

  • SlamDunk
    SlamDunk Member Posts: 1,761

    That should be easy to replace. Personally, if I was worried, I would buy a replacement from a hydronics guy. I might keep it on a shelf, just in case , or I might replace it for improved efficiency and an oil free motor. Not so sure I would worry about it dying, but that is just me.

    9326ysshClaucia
  • neilc
    neilc Member Posts: 3,033

    can I have that gage ?

    known to beat dead horses
  • mattmia2
    mattmia2 Member Posts: 13,756

    Looks like a 100 series. If the rubber bushings the motor is mounted in rot out it will misalign the shaft and start breaking couplings. Replace them when they get soft.

    Is the system still set up as a gravity system, did anyone change any of the piping or the emitters? If it is not changed almost any circulator will work since it is designed to be gravity.

    delcrossvClaucia1
  • mattmia2
    mattmia2 Member Posts: 13,756

    what's with the "install with this arrow pointing to a wall" thing?

  • delcrossv
    delcrossv Member Posts: 2,185
    edited July 24

    Several drops of oil in the pump oil port, a couple of drops in each of the motor oil ports each year and that pump will run indefinitely.

    Note @mattmia2 's comment about the mounts.

    It's a B&G 100. Still available today.

    https://www.supplyhouse.com/Bell-Gossett-102214-1-6-HP-2-NFI-Circulator-Pump

    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
    Intplm.
  • Jamie Hall
    Jamie Hall Member Posts: 26,236

    As @delcrossv and @mattmia2 say, with a little oil (don't overdo it) and some attention to the motor mounts, that thing will run another century or so without problems. The coupler springs are the weakest part, and paying attention to the mounts will keep hem happy.

    And the same pump is still made. Don't mess with success…

    Oh and one more thing: it's within a percentage point or two of any "modern" pump in terms of efficiency.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    delcrossv
  • 9326yssh
    9326yssh Member Posts: 46

    AMAZING!!

    what machine are we building now that will less for 75 years!? 🥺

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,327

    NOTHING made now will last 10 years never mind 75. Even if it is the same "identical " pump it is likely made in China or some of the parts are.

    There is probably twice the copper in that old motor as a new motor. Take care of it. The volute and housing are probably fine. The motor can be rebuilt at a motor shop and new bearing assemblies are available, I think unless they changed th thing so a new one will not fit.

    But you will need a truck to haul the money from your bank to Bell & Gosset. They give nothing away.

    Alan (California Radiant) ForbesIntplm.
  • mattmia2
    mattmia2 Member Posts: 13,756

    which is why @DanHolohan said the part number for a seal for that is 007

  • Steamhead
    Steamhead Member Posts: 17,920
    edited July 25

    Not a 100- this is that pump's predecessor. My 1940 Bell & Gossett Handbook says it's the model H2, since the pipe connections are 2-inch.

    Given the size of that boiler, I'm thinking that circ might be oversized for that system. This can cause the water to short-circuit through the radiators, reducing efficiency. Here's an extreme case I found years ago:

    https://www.heatinghelp.com/systems-help-center/adjusting-the-flow-rate-for-an-old-gravity-hot-water-system/

    Do you know how many square feet of radiation is on your system?

    Also, an old round boiler like that one is inherently inefficient. A combustion test would probably reveal an extremely high stack temperature.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2HVACNUTPC7060TomAuciello
  • HVACNUT
    HVACNUT Member Posts: 6,927

    That's not a 100. Note the 4 bolt flanges, and flange to flange height difference.

    Alan (California Radiant) Forbes
  • JUGHNE
    JUGHNE Member Posts: 11,480
    edited July 25

    "Point arrow towards wall" means do not point to floor or ceiling. IMO

    Horizontal shaft position only. Some may have been confused by "Horizontal" and "Vertical" wording.

    I have a 1961 school with 2 pumps similar to this. Both original motors still working.

    mattmia2ethicalpaulGGross
  • TomAuciello
    TomAuciello Member Posts: 4

    Good catch, @Steamhead Do you know if replacement parts are available for the model H2? Would they be the same as on a model 100? Thanks for your help.

  • TomAuciello
    TomAuciello Member Posts: 4

    Thanks for the advice, @mattmia2 Can you tel from the attached photos if the motor mounts need replacing? They don't appear soft and look firm and symmetrical.

    Thanks for your help.

    EndMount.jpeg

    End Mount

    NextToCoupler.jpeg

    Coupler Side

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,327

    They look ok but oily. You could take them off and twist them if they crack they are dried out and you will have to replace them. Probably better leaving them alone. If you can find replacements buy them for spares.

  • hot_rod
    hot_rod Member Posts: 25,443

    You might contact the B&G rep in Seattle, CHC, see if they have the motor mounts and spring coupling. They would probably have a motor that fits also, if you want to buy a spare. Replacing that entire pump with another 4 bolt type may be expensive. Or changing flanges and piping with that insulation may be a lot to get into.

    Screenshot 2025-07-25 at 5.06.15 PM.png

    .

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2Alan (California Radiant) Forbes
  • Steamhead
    Steamhead Member Posts: 17,920
    edited August 4

    Bearing assembly might be this one:

    https://www.supplyhouse.com/Bell-Gossett-189163LF-Bearing-Assembly-Lead-Free-Obs-1-1-2-Obs-2-Obs-HV

    But if that were mine, and I wasn't going to replace the boiler, I'd change to a standard 2-bolt flange set and use a standard circ.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • B & G made it very difficult to identify their pumps. It’s like some big secret that only a few have access to. Like the new trendy restaurants or bakeries around town here that don’t have a sign outside with their name on it that crowds flock to.
    Ive called California Hydronics Corp. (CHC) in the past and even they scratch their heads.
    Maybe @DanHolohan can give us some history?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,647

    I worked for the B&G rep from 1970 until 1989. During that time, I don’t believe we had parts for that particular pump. In fact, this is the first time I’m seeing one.

    Retired and loving it.
  • hot_rod
    hot_rod Member Posts: 25,443

    The rep I worked with in Kansas City, Blackmore Glunt always had old pumps like that on their repair bench when I visited. I think all the old timers that might recognize that model have retired however:)

    E mail a pic to the rep in your area, what do you have to lose? I think Armstrong Pump has replacement motors for old B&G stuff also. A spare motor, new seal and coupling could get you another 40 years.

    If you do replace look into an electronic ECM type that you can better dial in to your system needs and save some electricity.

    Replacing it will involve some piping work, no doubt.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,327

    B&G did make it difficult to match things up. At the price of the one above re-piping is probably the way to go.

    B&G replacement parts are outrageous. Not worth fixing a LWCO the parts cost so much it is usually better to replace. They used to be the leader now its like they are putting themselves out of business.

  • mattmia2
    mattmia2 Member Posts: 13,756

    maybe you could get a set of 4 bolt flanges, a set of 2 bolt flanges, some nipples, and an ecm circulator in that space.

  • delcrossv
    delcrossv Member Posts: 2,185
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • TomAuciello
    TomAuciello Member Posts: 4

    Does anyone know if any maintenance is required for the "rope" in the oil reservoir? Mine looks like it might have been disintegrated over the years. Should it be replaced after a period of time?

    OilReservourRope.jpeg
  • tim smith
    tim smith Member Posts: 2,877
    edited August 14

    I am pretty sure the 1/6 hp 2" pump took the 189100 bearing assembly. Which now the # is I am pretty sure 189162. But it does not sound like the bearing assembly is leaking so maybe just a little tlc. Replace coupler and motor mounts, we always did both when needed. The mounts are sagging and probably hardened. You could pick out the old probably varnished oil wicking with something like a dental pick . Order new wicking. Here is pic of wicking p/n

    B&G wicking.JPG

    Here is part sheet I think is correct one. Would need to verify diameter of motor mounts from supplier to what your od & id dimension are of your existing motor mounts. PS, very often when moving motor around to do mounts, you can accidentally short the leads that go from the elect box on motor into motor housing due to insulation being worn out. Then you may just burn up leads. No promises, we fixed many over the last 40 plus years. Once in a long while they had to be put down. Good luck. Here is the part sheet I think is right for that pump. I circled the 2" at top of page. Hope others chime in if they think maybe it would be different.

    B&G 2 pump.pdf
  • mattmia2
    mattmia2 Member Posts: 13,756

    you can sleeve shrink tube over the motor wires if they are crispy, you can warm them up with a heat gun to straighten them without cracking the insulation to get the shrink tube over them if you have to.