Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!

Copper to Pex in hydronic heating for DIY

Options
inspectordad
inspectordad Member Posts: 3
edited June 2025 in THE MAIN WALL

Hi, I'm doing a remodel and need to move a couple of pipes connecting my baseboard heating to the boiler.

It's copper. I don't know how to sweat copper so I was thinking of using PEX and shark bite connections.

So for those of you who know; is this a bad plan?

I need to do this as inexpensively as possible but also, and just as importantly, safely.

Does anyone have a different suggestion? Know of a plumber who could do the job on the cheap? (Woburn, MA 01801 area)

I NEED to move one line (3/4” copper), which means 2 new connections. But I'd LIKE to move a total of 2 lines (the 2nd being 1" copper) which would be a total of 5 new connections.

1000007414.jpg 1000007413.jpg 1000007407.jpg 1000007406.jpg 1000007412.jpg 1000007405.jpg

Thanks for the input!

Comments

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,642

    Moving heating pipes, without knowing what you're doing, can make your life miserable

  • Jamie Hall
    Jamie Hall Member Posts: 27,698

    Sharkbites are OK — for a temporary or intermittent use (and yes, I have used them!). They really shouldn't be used for a permanent installation… and I think you have more than two connections there…

    PEX is OK. But use proper crimp type fittings everywhere you can.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,834

    Nothing will be cheap in Woburn.

  • hot_rod
    hot_rod Member Posts: 28,078

    SharkBite is listed for that use, temperature and pressure. Large size reducing fittings are not always available.

    Copper press to pex would be another good option. You can rent or borrow the press and crimp tool.

    Screenshot 2025-06-29 at 11.08.18 AM.png

    Compression fittings are also available. Use a pex fitting adapter to fit inside a coupling.Compression fittings are common in Euro hydronic systems.

    Screenshot 2025-06-29 at 11.08.47 AM.png Screenshot 2025-06-29 at 11.12.49 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    inspectordadIntplm.
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Hi, I'll just throw out there that learning to "sweat" copper really is not that difficult. Here's a video from the CDA showing how: https://copper.org/applications/doityourself/#podcast68854 I'll add that much of what they give applies more to bigger pipe and fittings. Smaller sizes are quicker and easier. Every plumber has their preferences, but I like C flux as it turns dark when it's time to apply the solder. I only use mapp gas also. You can back the torch away from the pipe to quickly control the amount of heating. It's important to thoroughly clean flux off the joint when finished. I keep a spray bottle with water in it to both wet nearby surfaces and to help with rinsing off the flux. Practice on a few joints first, and you might be surprised by how easy the process is.

    Yours, Larry

  • inspectordad
    inspectordad Member Posts: 3

    Thank you everyone, I appreciate all the input! I'm leaning towards giving a go at sweating the fittings myself.

    My newest concern is wondering how to know if my practice joints are up to snuff or not.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,834

    after you solder them and they cool down heat them back up and take them apart you will see where the solder flowed .

    1. clean the fittings good with sand cloth, scotchbrite and or cleaning brushes. For the fittings I buy a cleaning brush and cut the handle off. Chuck the brush in a drill. It makes very quick work of cleaning the fittings
    2. Controlling the heat is the key. Its better to start with to little heat you don't want to overheat the fittings.
    3. clean the tubing with sand cloth or scotchbrite
    4. apply flux to the end of the tube. just a thin film

    Practice makes perfect. Most say for 1/2" tubing use 1/2" of solder, 1" tubing 1" of solder etc. a little more is ok. You want the solder to flow so pull the heat away when the solder starts to flow, you can reheat if needed.

    The solder follows the heat and you want the solder to pull in so with a coupling you would aplpy the heat to the center of the coupling with an elbow you apply the heat to where the end of the tube is inside the fitting.

    Doing the bottom of a fitting on a vertical pipe is a little more difficult. Kepp the heat higher on the fitting to pull the solder up. Use minimal heat. Don't heat the pipe below the fitting or the solder will fall out of the joint and flow down.

    After soldering have a dry rag to wipe the excess solder off. Do this gently to not disturb the joint.

    It sound more difficult than it is. With a little practice you will be fine. Water in the pipe is your enemy.

    Larry Weingarteninspectordad
  • rick in Alaska
    rick in Alaska Member Posts: 1,529

    My first concern is if you have the room above the pipes to move them there. I wonder why if there are two pipes going up into the ceiling that are close together, why they didn't run both of them up together and then split off. You might want to cut open the ceiling first and make sure there is not any structural issues in the way, and the pipes can go up in that space.

    Also, if you do decide to move them yourself, keep a spray bottle of water and a fire extinguisher handy. You will probably be soldering next to some very dry wood, and you don't want to start a fire.

    Rick

    inspectordad
  • mattmia2
    mattmia2 Member Posts: 17,905

    @EBEBRATT-Ed you can buy fitting brushes with a hex shaft that fits in an impact driver or drill now, don't have to cut apart one with a handle.

    inspectordad
  • inspectordad
    inspectordad Member Posts: 3

    Thank you everyone, you've been great. To answer the question of ceiling space, there is plenty. You can't see it in these photos but most of the ceiling is actually already down. I left the parts that have the pipes sunk through for the time being. The ceiling was basically the only part of our basement that wasn't destroyed by the flood but it was a poorly done job in the first place so replacing it all is a bit of a relief anyway.

  • ethicalpaul
    ethicalpaul Member Posts: 8,978
    edited July 2025

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    rick in Alaskapecmsg
  • mattmia2
    mattmia2 Member Posts: 17,905

    so is orangeburg and galvanized potable water piping…

    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 8,978

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 17,905

    that is ai. it is allowed in the code.

  • ChrisJ
    ChrisJ Member Posts: 17,622
    edited July 2025

    I didn't check other areas, but in New Jersey galvanized pipe is allowed within the home, but not for a water service. I'm not sure why anyone would use it, but, you can. Even in a brand new house. At least in NJ.

    I tried to look for Orangeburg for soil pipe, but I don't know it's real name. Best I can tell, there's absolutely no mention of Orangeburg, fiber tube, or anything remotely similar in NJ's code. Probably because the stuff disappeared 50 years ago because of how wonderful it was.

    Screenshot 2025-07-02 114521.png

    Screenshot 2025-07-02 114553.png

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,905

    From the 2015 michigan residential code

    image.png image.png

    It looks like they removed orangeburg. it was in the 2002 code.

  • ChrisJ
    ChrisJ Member Posts: 17,622

    Orangeburg for water distribution or service? Under pressure?

    Wasn't that strictly for drains etc?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,905

    waste. i believe outside of the building only but i'd have to dig out the 2002 code and look. the 2002 code book is about 1/4 the thickness of the 2015 code book.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,834

    Isn't orangeburg just clay tile used for drainage?

  • mattmia2
    mattmia2 Member Posts: 17,905
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,834

    Ok I have seen that as well tough to cut

  • mattmia2
    mattmia2 Member Posts: 17,905

    i have a couple very gooey sawzall blades with no teeth on them.

  • ChrisJ
    ChrisJ Member Posts: 17,622
    edited July 2025

    You posted charts for water distribution and water service, not waste.

    Or, did you check the waste / soil pipe section for that and just not share it because it wasn't there anyway?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,905

    only posted the part for galvanized in supply piping. the orangeburg looks like it isn't in the current version but I'm pretty sure it was there 20 years ago. still never really got a clear answer about if the galvanizing sometimes had some lead in it. it would need to be lead free for potable water.

  • hot_rod
    hot_rod Member Posts: 28,078
    edited July 2025

    I worked with Orangeburg pipe when I was young, cut it with a hatchet! Basically cardboard and tar.

    Started in Orangeburg, NY!

    I don't recall it being used form potable water use? Or any pressure? It didn't have much of a coupling feature.

    Screenshot 2025-07-02 at 2.22.16 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ethicalpaul
    ethicalpaul Member Posts: 8,978

    I don't have access or ability to understand the codes, I admit.

    So galvanized pipe is allowed for new homes in 2025?

    And if so, how many years does it last? I imagine quite a few. Just like sharkbite. Even Orangeburg reportedly lasted 50 years. Anyway all this is distraction. Sharkbite is accepted by the standards bodies for permanent installations, today.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • hot_rod
    hot_rod Member Posts: 28,078

    All piping materials have a weakness. With galvanized, softened water, for one, can be too aggressive., attack starts at the threads, fittings and pipe, where the galvanizing has been removed.

    Water + bare steel= rust and corrosion.

    Both press fittings and grip fittings depend on an o-ring for the permanent seal. If that frightens anyone then sweat, braze, thread, copper glue :), compression, flare are other options.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 17,905

    the galvanizing is still at the joint on the water side but the wall is thinner where it is threaded. they frequently leak at the valley of the threads

  • lowercanada
    lowercanada Member Posts: 17

    MAPP Pro is not the original MAPP gas….and doesn't burn as hot….