  • mattmia2
    mattmia2 Posts: 18,399

    The quick summary would be:

    Vents:

    Balancing with vents would mean the vent speed can delay how long the radiator will take to fill with steam, likely in lower heat loss times of they year to the point the steam never reaches the vent before the thermostat is satisfied so a varying amount of the radiator will get hot depending on cycle length but a sufficiently long cycle will fill the radiator with steam and close the vent so at the end of a long cycle the entire radiator will be heating(depending on the heat loss of the building vs the radiator sizes cycles may never actually be this long in reality or only during recovery from setback.)

    in summary in a long cycle the balance of the system is ultimately set by what size radiators were selected.

    Orifice plates/throttling valves:

    A more or less fixed amount of steam is emitted in to the radiator once the system reaches steady state if the pressure at the boiler is limited with a vaporstat, the orifice plate should be sized so that amount of steam is less than the amount of steam that the radiator can condense so it never reaches the outlet of the radiator. no matter how long the cycle is, only the amount of the radiator set to heat by the orifice plate will heat.

    in summary in a long cycle the balance set by the orifice plates continues indefinitely.

    The radiators are likely oversized on the coldest day and definitely are oversized on mild days so heating the entire radiator probably isn't desirable.

    in reality setting the basic balance with the radiator vents then using the radiator valves to throttle areas that overheat is probably a good strategy to use here.

  • pacoit
    pacoit Posts: 127
    edited July 2025

    [Edit: @mattmia2, I didn't see your post above; thanks; I understand, but below still valid]

    Perhaps I failed to understand something. But I don't think the two responses above answered my question as intended. So, I'll try asking again.

    Is it fair to say that, due to the restriction (steam stands more time before orifice), the orifice plates can cause somewhat more condensate to flow back down the supply pipe due to increased condensation before the orifice plate?

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Short answer. No.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • pacoit
    pacoit Posts: 127

    OK. So taking a limit case, if the orifice were infinitely small (no hole), would the steam just stay hot for the duration of the heating cycle? Or would it condense, at least small amount, in the valve/piping, creating some additional condensate in the supply piping as compared to condensing in the radiator?

  • mattmia2
    mattmia2 Posts: 18,399

    only as much steam gets in as air can get out. if the orifice is infinitely small only an infinitely small amount of steam could get in to that runout before the cycle ended unless the cycle was infinitely long.

  • pacoit
    pacoit Posts: 127

    Ah, good point! Bad example on my part. Didn't look back far enough; and it makes me think perhaps I'm looking for something that's not there. Thanks.

  • Jamie Hall
    Jamie Hall Posts: 27,975
    edited July 2025

    Steam will condense any time it is in a situation to lose enthalpy to something else. Next to a cool surface? It will condense to heat the surface. Sp if some steam could get to the infinitely small orifice location, yes some would condense on the pipe walls near the orifice. Exactly enough, in fact, to compensate for the heat loss of the pipe into the surrounding space.

    But… this has nothing to do with whether the orifice is blocking steam or not. Exactly the same amount of steam would condense in that location and pipe if there were no orifice at all.

    Or let's look at it in a more direct answer to your question as stated, which was "if the orifice were infinitely small (no hole), would the steam just stay hot for the duration of the heating cycle? Or would it condense, at least small amount, in the valve/piping," If the steam were present, and the supply piping were cooler than the steam, heat would transfer from the steam to the supply piping and the steam would condense.

    Or take a third whack. Saturated steam is, by definition, water vapour in equilibrium with liquid water at the stated temperature and pressure. If any energy is extracted from the water vapour, that energy will come from condensation of some of the vapour in the form of liquid water.

    I suggested it earlier, I will again: look up the definition of enthalpy, and then find a good thermodynamics textbook and study it to understand it, and then you will be on the way to understanding how the physics of heat transfer using combined vapour/liquid phase systems (of which steam heat is one — and so are heat pumps and refrigerators) works.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    this is actually the answer to your question about orifices vs vents (which contain orifices but also a valve).

    The vent orifice slows how fast air can get out of the radiator and how fast steam can enter while there is still air in the radiator. Once the radiator is filled with steam and closes the thermostatic valve in the vent, the steam that condenses as a result of heating the radiator will pull as much steam as is needed to replace it in to the radiator. the whole radiator will heat.(assuming the boiler can produce enough steam for the demand of all the radiators).

    The orifice plate at the valve slows both air and steam so it controls the rate at which air can vent from the radiator and continuously controls how much steam can get in to the radiator.

  • pacoit
    pacoit Posts: 127
    edited July 2025

    Yes, it's clear now. Thanks. A nice statement is that a vent "contains an orifice but also a valve".

    So, a noteworthy point comes to mind: when using an (inlet) orifice, its CFM must be limited to radiator condensing power, and that also sets the venting limit (i.e., speed of venting at startup); but, instead, a thermostatic vent with a much higher vent rate could be installed if needed, o provide more system balancing flexibility.

    I think that difference is what I was trying to get to in my initial question, but was going down the wrong path.

    Of course in a vacuum system, these venting and system balancing issues would be basically moot. Right?

  • mattmia2
    mattmia2 Posts: 18,399

    It depends. In a Paul type vacuum system where the vacuum pump is connected to the vents the orifice in the vent would act similar to a regular radiator vent.

    In the more common 2 pipe vacuum systems with the vacuum pump on the returns you would have to balance the system with orifice plates or the radiator valves.

    The radiators are almost neve perfectly proportional to the loads and the loads vary with number of people in the structure, the sun, cooking, the wind, and other things so you rarely want all of the emitters to heat fully all at the same time, you want to speed some up and slow some down to balance the system.

  • pacoit
    pacoit Posts: 127

    "…you rarely want all of the emitters to heat fully all at the same time"

    Yes, but is it fair to say that in the design stage of a system one attempts to create a balanced system (get steam to each radiator at the same time), say on condition that all radiator valves are fully open? Then users can adjust radiator valves according to preferences and varying environmental conditions?

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Hmm… at some risk of appearing contrary, what is it really we are trying to achieve here? It would seem that perhaps the thread title isn't really what's at issue?

    Can we — hopefully @pacoit , our OP, restate and perhaps narrow the objective down some?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Posts: 18,399

    i think we covered the practical parts of this 3 pages ago

  • pacoit
    pacoit Posts: 127

    Thanks everyone for all of your very helpful comments. I originally asked about vent placement. But, actually, I was pursuing a process of general venting theory—-let's call it. The reason is that I wanted to determine if my system was operating correctly, as efficiently as designed, and then in theory what might make it even more efficient. For this, I needed to educate myself quite a boatload. I ended up asking a lot of different questions, ones that, in hindsight, I should have started different threads for. I've little experience in posting online. I take the last comments as a nudge that it's time to end this thread. I have other questions which I'll start different threads for and try to stay more focused on the topic.

    If you like, I can try to summarize in a last post what I've come to understand specifically focused on topic that is the thread title.

  • mattmia2
    mattmia2 Posts: 18,399

    We don't mind answering your questions on this thread, you just are way in to the weeds on trying to calculate it, you just need to try something and see what happens and adjust from there. you are making precise calculations based on imprecise information.

  • pacoit
    pacoit Posts: 127

    You were right when you said, way way back, that my original question had already been answered, namely, my system was under-vented and I should start by putting a Gorton #2 at the end of the longest main tee, and see what happens. It sounded good to me then, and it's obvious to me now. Thanks.

    But, I'm in no rush and wanted to study steam heating much further, pondering how a theoretically ideal system would function. That's the way I am about certain subjects that grab me. So I started with creating a limited model of venting; then I modeled steam production and flow/condensation into the venting model (add a vent somewhere and see its effect on all other parts of system; see what areas each vent contributes to depending on where the steam has reached in the piping; etc.). It's pretty cool and increasingly more accurate. But, the real value is the exercise of doing it, which has helped me flesh out a lot of concepts—-along with your help—-and obtain a more intuitive understanding.

    I have a main tee that is very long (compared to the others) and, sure enough, the last 2 radiators don't heat much unless it's quite cold out. I see that adding a Gorton #2 at the tee end will help a lot; but it will speedup the whole system (much needed) to varying degrees. Those last 2 radiators will still be comparatively slow (a little better). Good to know. I see that putting the Gorton on the last rad return (in my system), should actually work a bit better.

    I see that balancing the system is not possible unless I generously vent the last rad while slowing venting of most other rads. Balancing at the expense of slowing the system seems a poor solution.

    I see that the real solution to quick heatup and balancing is to convert to a vacuum system.

    I see that steady-state heating is the most efficient operating mode. Can't always get what you want. But a newfangled modulating boiler coupled to a variable vacuum system that adjusts boiling temp gets one a bit closer to steady-state operation (i.e., extended periods thereof).

    I see that I can upgrade my system in a variety of ways, the more ambitious ones a stage at a time. I know how to program microcontrollers to operate sensors, switches, and other instrumentation (heh, but I don't see myself designing that "newfangled" boiler anytime soon).

    I write this so you know better where I'm coming from with my questions.

    As to any technical comments in this post, how am I doing?

  • mattmia2
    mattmia2 Posts: 18,399
    edited July 2025

    I see that balancing the system is not possible unless I generously vent the last rad while slowing venting of most other rads. Balancing at the expense of slowing the system seems a poor solution.

    you are slowing those radiators, you aren't slowing the system. the steam can take multiple paths, you are encouraging it to take the path where it heats the main first then heats the radiators at the same time instead of the path where it heats the main and the radiators progressively from the boiler. You aren't changing the output of the boiler, you're just directing it more evenly.

    Vacuum won't solve this problem, it will just make it happen at a lower temp. the steam isn't going to progress until the material at the steam front is steam hot, whatever temp that is at the pressure of the system.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    I'm not going to go all the way back in all this, but I seem to recall a spread sheet or other computer simulation in there somewhere… and I am still a little concerned that in going the calculating direction rather than the empirical direction you may, honestly, be a bit over your head — unless I am misreading your background and experience in thermodynamics, which I may be.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • pacoit
    pacoit Posts: 127

    @mattmia2, by "slowing the system", I did not mean the boiler; I meant the system heatup time.

    I'm with you. But, there is an underlying principle here that I'll try to make explicit. Imagine a main tee section 50' long with 10 runouts equally spaced 5' feet apart; runouts length, radiator and vent are identical. In the heatup (venting) cycle, there is a time diff between steam reaching the first and last radiator.

    Now, a large vent is added to end of main. What happens? The main vents more quickly; steam passes each runout more quickly, and so the runouts begin venting sooner (but not faster). As steam passes a runout, it separates air in main from air in runout; that runout related vent no-longer contributes to main venting but starts runout/rad venting. So, it appears that,

    1. Main venting does not cause mains to literally vent first; it causes them to vent faster relative to the runouts; runouts will begin venting as steam in the main passes them.
    2. The only way the first and last rad can vent at same time due to mains venting is if main length is zero (or runouts are at same location in main).
    3. The reduction in time diff between first and last rad getting heat due to added main vent is a function of the change in time to vent the main. As main venting time is not zero, balance between the two rads cannot be reached, just improved.
    4. Adding generous venting to the last rad may not bring it to balance; the issue is the time diff between the steam to reaching the first and last runout; if, e.g., the diff is 5 min, and the runout venting time is less than 5 min, then even reducing last runout venting time to a hypothetical zero would not balance the system.

    Another point, "slowing the system". Adding a main vent will shorten heatup time (decrease boiler-on time); but to get an outlying rad significantly into balance, even after generous main venting, one may have to slow the other vents. This will increase the boiler-on time, possibly to more than original time, depending on specific case.

    Third point, a vacuum can be employed to eliminate venting time on heatup cycle. It allows steam to travel everywhere very fast (still limited a bit if cold pipes); thus providing balance;

    I thought we were generally agreed on these points—-except perhaps for questioning the "mains venting clears main before runouts begin venting", which wasn't questioned before.

    mattmia2
  • Jamie Hall
    Jamie Hall Posts: 27,975

    "Third point, a vacuum can be employed to eliminate venting time on heatup cycle. It allows steam to travel everywhere very fast (still limited a bit if cold pipes); thus providing balance;"

    This is only partly true. It is convenient to consider that the steam front velocity (what you are looking at as "travel everywhere very fast") can be increased by using a vacuum to "eliminate venting time on a heatup cycle". However, that is not the case. You are still thinking in terms of "limited a bit if cold pipes". It's more than a little bit. In fact purely experimentally — never mind theoretically here — provided adequate venting is in place, additional venting — or applying a vacuum — will make no difference at all. Steam moves (like any well-behaved gas, which it isn't) in response to pressure differences. However, the pressure at the point in a main or runout where the steam is condensing is governed by the vapourization temperature of the steam at that point. And that latter is governed by the temperature of the pipe at that point.

    The actual dynamics at and near that point are interesting. If we make the assumption that there is at least enough steam being produced by the boiler, the pressure at the point on the pipe where the temperature has reached the local boiling point — we assume 212 F, but it's actually variable — the pressure at that point — and, by extension, in the air beyond that point — will be atmospheric. If there is enough steam being produced, enough condensation will take place at that location to heat the pipe and the location on the pipe where condensation is taking place will move along. If that steam front is to move, of necessity the air must also move, and thus the pressure at that point will be, of necessity, slightly higher — but only enough to cause the air to move slowly out of the way.

    This can be demonstrated on a vapour system with crossovers, which has only one vent located at the boiler (if indeed the dry return is not simply open to the atmosphere at that point, which many old systems were). There is virtually no flow out of that vent until all the radiation and all the pipes are up to the condensation temperature at whatever the system pressure is. I emphasize: virtually NO FLOW. How can this be? Simply because all of the steam being produced by the boiler is being condensed somewhere in the system.

    Now if we take another extreme case, consider a sealed system. In such a system the dynamics are a little trickier to visualise, but if we suppose that the initial case is the system is at a high vacuum — most of the non-condensable gas pulled out in some way — as heat is applied to the boiler water will vapourise at that low temperature and warm up some of the piping. Depending on the balance between heat input at the boiler and heat loss in the now warmer parts of the system, the pressure may rise and more of the piping will become warm. At some point — which may or may not, probably not, be around atmospheric pressure — the heat input to the boiler and the heat output from the warmer parts of the system will equalize, and the system will run indefinitely at that pressure.

    This assumes that there are no non-condensables trapped in the system. If there are, they must be removed, or the areas where they are trapped will not heat.

    Now it is quite true that in an inadequately vented two pipe system adding vent capacity will speed things up — up the point where the boiler heating capacity limits. In a one pipe system with radiator vents, it is also true that slowing certain radiators at the expense of others will reduce the average heat output of those radiators. It should be evident from the above, however, that speeding up already fast radiators will not increase their average heat output. Where this can get confusing is in the case of long, unvented runouts where adding venting on the runout (NOT on the radiator) and allow air — non-condensables — to escape at a lower pressure, and thus allow steam into those runouts more rapidly than others (but at the expense of speed in the others…).

    One other thought: it should also be evident from this that if one wants to reduce the time from steam generation at the boiler to steam appearing at the radiator, reduce the amount of heat it takes to warm the pipes and the amount of heat they lose to the environment. Insulate the pipes!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • pacoit
    pacoit Posts: 127

    Thanks for the detailed comments.

    I agree that in a vacuum system, especially in a cold start, steam progression through the system will be slowed by the amount of condensation occurs to heat the pipes. Perhaps for the edge case it may not be much faster than an abundantly vented non-vacuum system. But, wouldn't it be much faster in the general case?

    Additionally, I agree that in the case that boiler power is insufficient, "---provided adequate venting is in place, additional venting — or applying a vacuum — will make no difference at all"

    Any comments on "Main venting does not cause mains to literally vent first;" or on the limits to balancing by venting the main?

    .....Separately, to be clear, when I say vacuum system, I mean a system that remains under vacuum between heating cycles; I understand that during heating the vacuum pressure will reduce and possibly go positive (depending on various initial variables).

    You lost me in your theory example about single dry return vent. You say: "There is virtually no flow out of that vent until all the radiation and all the pipes are up to the condensation temperature at whatever the system pressure is. I emphasize: virtually NO FLOW." Well, if the steam has reached all the piping and radiation, wouldn't the flow add up to the total volume of the pipes and radiation in the system? And wouldn't the flow necessarily have to have progressed concurrently with the steam progressing through the pipes?

  • Jamie Hall
    Jamie Hall Posts: 27,975

    On your last paragraph. Yes and no. The air flow is not exactly zero, of course. Indeed, by the time the system is completely heated — which may take an hour or more in a decently sized system — all the air in it will have been forced out of that one main vent.

    In an hour or so. That is such a small rate of flow — a few cfm at most — as to be almost (but, granted, not quite!) negligible (to put a number on it — suppose that we have the equivalent of 400 feet of 3 inch pipe to deal with — that will be about 0.3 cfm to vent, which a single Gorton #1 can handle at 1 ounce pressure differential. Indeed, this is why the "go to" vacuum tight vent for vapour systems was (and is) the Hoffman #76 (if you can afford one…). It would handle a system of that size quite happily at a two ounce steady state differential pressure. Even if we consider only the pipes, and suppose that the condensation/steam front moves at 15 feet per minute (a pretty good clip), that's still only about 0.8 cfm and a single Gorton #2 will handle that at 1 ounce.

    It's also important to note that once the power demand from the installed radiation rises — as the radiators fill — to approach the power output of the boiler, the venting rate will fall, and the pressure registered at the boiler is only that which is required to overcome friction loss in the pipes — again, a few ounces.

    This is also why true two pipe, and particularly vapour, systems, which use crossovers, can and do function brilliantly with remarkably little venting (by conventional thinking) and startlingly low pressures.

    In principle, what will be observed as steam rises in the boiler is an initial rise to perhaps one or two ounces; at first this will indeed be the resistance of the main vent, but as time progresses the demand on the main vent will drop, and thus its pressure drop, while the distance that steam must travel will increase — and hence a pressure rise due to friction. In practice this results in that initial small pressure rise — and then a very constant pressure for the remainder of the run.

    If the boiler is oversized, then when all the radiators are full the pressure will start to rise again — which is when the boiler should cycle off long enough for the system to catch up, but that's another story.

    I'm not at all sure that a system starting under a deep vacuum will result in a shorter travel time to the radiators. Indeed, it might be longer — since the system will start at a much lower temperature, and thus take longer for the pipes to warm up. I'll have to work on that one.

    I might add, however, that supposing that one can indeed maintain a deep vacuum at will, then the power output of the radiators can be modulated as required by allowing the pressure to change which, in turn, can be done by adjusting — modulating — the power output of the boiler. This is not novel technology, however: a coal fired boiler, the power of which can be modulated by the dampers, coupled with a vapour system with a vacuum vent can accomplish just this trick — and did. Even more remarkable was that the modulation was accomplished by a thermostat, but all with no electricity involved! The efficiency was horrendous, but it worked. A century ago…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • pacoit
    pacoit Posts: 127

    "I'm not at all sure that a system starting under a deep vacuum will result in a shorter travel time to the radiators. Indeed, it might be longer — since the system will start at a much lower temperature, and thus take longer for the pipes to warm up. I'll have to work on that one."

    Under a deep vacuum the pipes would not have to warm up as much since the boiling point will also be lower. So, I would think the heatup time—-and so travel time—-would actually be shorter given the lower differential temperature of the cycle.

  • mattmia2
    mattmia2 Posts: 18,399

    Slightly, but the specific heat involved in a transition of a delta t of say 110 f degrees vs 130 f degrees isn't much. The main reason vacuum systems were used was to increase the time the boiler would steam as the coal fire died out or some mechanical vacuum systems would use the vacuum to lift condensate from emitters below the water line.

  • pacoit
    pacoit Posts: 127

    So, a vacuum system would be useful if combined with a modulating boiler to vary the heating rate and boiling point in order to achieve longer periods of steady-state operation (imitating somewhat vacuum systems with coal-fired boilers)? Sounds good.

    What benefits does a vacuum system provide the Empire State Building?

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Yes to the first paragraph. None — so far as I know the Emprise State Building is a pretty plain vanilla two pipe system. Not even vapour…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Posts: 18,399

    Mainly that you can use smaller main and return piping I think.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Didn't realiuse that.

    However… may I humbly point out that steam systems don't know anything about the gauge pressure? Or vacuum? All they know is the pressure differential. So, to take the above comments on the Empire State Building as an example, lets' suppose that they have a steam feed pressure of 2 psi GAUGE and are operating at 10 inches vacuum. Now 10 inches vacuum is almost exactly - 5 psi GAIGE so that the building is operating on a pressure differential of 7 psi. It will in fact — except for temperature of the radiation — operate in exactly the same way with a boiler pressure of 7 psi GAUGE and open vents or, for that matter if you could get there, - 5 psi GAUGE at the boiler (10 inches of vacuum at the boiler) and 20 inches of vacuum on the returns…

    Bottom line. If you really want to understand what is going on in a steam system, always work in absolute pressure and differential pressure. Gauge pressure and inches vacuum with trip you every time.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • pacoit
    pacoit Posts: 127

    So, for my system (2-pipe; separate drips to wet return; currently Hoffman 1a vents in basement on the drips near ceiling), what would be a good way to convert to a 'natural' vacuum system ( assuming fairly air-tight piping), i.e., without using a vacuum pump (which could optionally be added later)?

    1. Orifice plate at each radiator; replace Hoffmans with simple air check valves?
    2. Orifice plate at each radiator; replace Hoffmans with flex tube to common hub with one higher-end check valve?
      1. Would make ready for optional vacuum pump.

    Other ideas?

  • mattmia2
    mattmia2 Posts: 18,399

    I think @ethicalpaul went on this quest a couple years ago, but you're going to have trouble finding a valve with low enough cracking pressure.

    plus you need to save up to deal with that asbestos first.

    ethicalpaul
  • ethicalpaul
    ethicalpaul Posts: 9,076

    yes I tried some stuff. In the end I believe the whole vacuum idea is a fine marketing gimmick that surely made Hoffman and others some nice money but I don’t think you could measure or observe any economic or comfort benefit from it.

    Make sure you operate at a low pressure always with good vents or traps and you’ll be in fine shape

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • 109A_5
    109A_5 Posts: 4,761
    edited July 2025

    Natural Vacuum with a true 2 pipe system, read his postings and/or talk with @PMJ he is doing it and would not go back.

    You may find this interesting too.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Jamie Hall
    Jamie Hall Posts: 27,975

    Natural vacuum on a two pipe system? Can it be done? Sure — as @109A_5 mentioned, @PMJ has worked with it. Is there an advantage? I expect so, but I'm not at all convinced that its large enough to be worth the effort — @PMJ likes to experiment with things, as does it well (and knows what he's doing), but… cost benefit? Hmm…

    Old coal fired systems sometimes — by no means always — did have vents which held a vacuum. One of these — the Hoffman #76 — is still available, I believe. However, those systems did not have the firing characteristics of oil fired systems, and I've not run into any examples of modulating burner gas systems. Why is this significant? Because the coal fired systems took advantage of the vacuum to use the large amount of residual heat available in a coal fire which has been banked, or allowed to run low on coal. Modern burners are either on or off, and the only residual heat available is in the mass of iron and water in the boiler — and even a brief experiment will show that there isn't much.

    So long story short — I'm with @ethicalpaul on this one. Nice idea, but… not worth the cost and effort to implement.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Posts: 18,399

    Coal boilers also had about 10x the mass of iron and water compared to a modern boiler.

    ethicalpaul
  • PMJ
    PMJ Posts: 1,325

    @pacoit, I see the vacuum thing is up again. Probably because there actually is something to it.

    I have been running my two pipe system closed up with natural vacuum between cycles close to 20 years now. The impact it has had on comfort by evening out the heat is dramatic. I have learned that with intermittent fire what happens in the system when the boiler is off is more important than when it is firing. And what happens during that off time is very different closed up vs open vented.

    You will find that there is minimal interest in this here and as far as I know I am the only one actually doing it.

    As always, I'm happy to discuss with anyone at any time.

    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
  • Jamie Hall
    Jamie Hall Posts: 27,975

    To be clear, @PMJ , if I had the money I would replace the Hoffman #75 and Gorton #2 which Cedric has with a three Hoffman #76s (to get the same venting capacity).

    I don't.

    So I won't.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • PMJ
    PMJ Posts: 1,325

    @Jamie Hall , if the system will hold vacuum at all you never need that venting capacity anyway. As you know, cold starts are slow and air leaves so slowly 1 small vent would easily do. On hot starts after that there is no (or very little) air to vent anyway and only at the very end of the burn. I keep saying it - the only opening to the atmosphere I have in a 1000EDR system is a single 1/2" pipe way far from the boiler in the garage. Venting beccame a total non-issue with this at least in my Mouat system.

    For reference, as a backup should my solenoid valve fail to open I have plumbed next to a cheap check valve as a safety valve( link below). The system runs just fine with just that. I prefer not to ever even get the system as high as the cracking pressure required but it really wouldn't be a big deal.

    For some reason I'm never able to communicate what a game changer this all was.

    https://www.mcmaster.com/46835K52/