can I identify oil consumption each unit on two unit apartment that share same oil heating system?
Hello, I have two tenants—one prefers high temperatures (around 77°-80°F), while the other doesn’t like that much heat, because his temperature also rises. How can I control the heat for each unit separately? Can I set a specific temperature? Additionally, is it possible to identify oil consumption for each unit? Both units currently share the same oil heating system from the same oil tank.
What type of system are we talking about here? Steam? Hot water? Air?
@Jamie Hall, it's Hot water and brand "Utica boiler".
Separate thermostats? Separate zones?
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
One Utica boiler with two different zones using two different zone valves? or two different circulators?
It will not be as accurate as an electric meter or a gas meter that has to be calibrated by the authority having jurisdiction, but there are BTU meters that can get you close. You will need to measure both systems with the same type of meter (two meters) then do the math to determine what percentage each unit uses. From that percentage you can divide the oil tank usage from each fuel delivery.
The percentage may change from one delivery to the next, so you will need to keep a log at the time of deliver from the previous delivery. Like …take a meter reading on the day the oil truck delivers fuel. Then compare the total meter reading from the last delivery. Once you know the total BTU of both zones and divide that total by one of the meters then you will know the multiplier for the fuel delivery purchase.
I don't know what a BTU meter might cost, but if it is going to stop a constant discussion over who pays for what, then it may be worth it.
1 -
Why that hot? Really 77 - 80°F?
Separate boilers and seperate tanks. Or include it in the rent.
@EBEBRATT-Ed
Comment on BTU billing not being permitted. There are district heating systems in Europe that use BTU meters for billing individual properties. What about steam meters on NY steam supply? You can get heat meters that are calibrated to the same standards as electricity and gas meters. They work my measuring the flow and temperature difference between flow and return.
the OP is talking 2 units not District systems.
Am I reading this correctly? You have one boiler and one thermostat and there's a conflict? One tenant on the first and one on the second? Thermostat on the first? If that's the case and depending where the thermostat is located the only way to do this would be to lower the heat out put in the unit asking for a cooler space. How to do this depends on the type of emitters. Or repipe and zone the floors independently.
Thermostatic valves on each terminal. Separate supply pipe with water meter for each suite.
I bet those who like it warm will turn down those valves.
Certainly not legal in New York.
