Mitsubishi heat pump not keeping up
I have a 3 zone 30,000 Btu Mitsubishi mxz3c30nahz4. Heads are msz gs18na, msz gs12na and msz gs 06na. Most of the time I just run the 18,000btu unit which heats the entire first floor (about 800sq ft) and keeps the upstairs pretty warm as well from the heat rising up. Lately I’ve been putting the 12,000 Btu unit on at night to make the bedroom upstairs a little warmer but when I do so the 18,000 Btu unit downstairs starts struggling. By the morning the downstairs can be as cold as 64 degrees when unit set to 70 with both lights on indicating thermostat not satisfied and is blowing air like crazy with fan on auto trying to catch up. As soon as I turn the 12,000 Btu unit off the 18,000 Btu unit catches up pretty quick and settles down. If I don’t put the 12,000 Btu unit on in the bedroom, the downstairs will be 72 degrees in the morning when set to 70 and the 18,000 Btu unit will be cruising like it’s no problem. I never really put the 6,000 Btu unit on because it is a guest room. Is it normal for one unit to struggle this much when putting another unit on at the same time?
How old is the install? Did it ever work right?
I think I'd start by checking the charge. Tech Support can tell you it's not right by taking some pressures & temperatures, but the only way to know it's right is by sucking it all out and weighing it back in.
It is a little over a year old. It is hard to say if it was ever working right because the first heating season I had a firmware issue causing defrosts every 20 minutes. When I finally got the new circuit board the heating season was mostly over and I never really ran multiple units at the same time. Only the 18,000 Btu which worked great on its own. Then cooling season didn’t seem to be any issues running all units at the same time.
Your home most likely needs a larger outdoor unit. Your indoor units add up to 36,000 BTU and your outdoor unit is only 30,000 BTU. and that is rated at an outdoor temperature is at about 40°F. The heat pump will deliver much less the colder the outdoor temperature gets.
I think it is time to ask the original installer what criteria was used to select the 30,000 BTU outdoor unit? Since the system is clearly not large enough to heat the home, what are they going to do about it?
@EdTheHeaterMan That unit is a cold climate unit, this specific one delivers 2.5 tons of heat at 5F. They can be paired with up to 130% capacity indoor heads, but you won't get more than what the outdoor unit is capable out of it.
https://ashp.neep.org/#!/product/152220/7/25000/95/7500/0///0
@ksm Crank the thermostats on all 3 indoor heads. max heat, max fan. After about 15min measure the air temperature coming out of it with something semi accurate (digital meat thermometer works). You should see about 105F out asssuming 70F room. If it is significantly less than that, the unit is down on refrigerant which means you have a small leak.
it’s possible you’ve lost some juice. it’s possible you have a leak.
Long lines? After 98 feet the installer needs to add juice
Can you get a basic temp rise? 30 degrees is good. 40 degrees is nails.
Once you pas your 28000 btu, you can’t expect all the heads to provide full bore power.
Mitsubishi allows for 130% connected load. You can connect 130%, but you sure won’t get 130% blowing into the home
1 -
@Kaos Said: @EdTheHeaterMan That unit is a cold climate unit, this specific one delivers 2.5 tons of heat at 5F. They can be paired with up to 130% capacity indoor heads, but you won't get more than what the outdoor unit is capable out of it.
I tend to disagree with the 2.5 ton (30,000 BTUh) at 5°F statement. It is just the way that Heat Pumps operate. you see the colder the outside temperature is, the less heat there is to take from the air and compress it to make the inside warmer. Now a Heat pump that is rated for 2.5 ton at 45°F outside temperature can not possibly generate 30,000 BTU heating capacity at 5F. It is a physical impossibility. Here is the specification sheet from the MXZ-3C30… it clearly states that the heating capacity at 17° outdoor temperature is less then 2 ton.
When it gets to 5° outside temperature, does some magic low temperature fairy come down from the sky and make it produce more heat? I think not. I still stand by my statement that the 30 is too small for the space and that the 36 may have been a better choice.
If you need to understand more about how heat pumps operate, I will be happy to learn ya some basics… Just send me a PM
1 -
Ed, this unit is NAHZ4 not NA3 as you show on the product data sheet. Different unit specs. Here is correct one. Not quite full capacity but much closer than other spec. Again max capacity does have some limitation but can reach it.
Original poster, what’s the od temp at times you’re having problems. Also of course would be necessary to have load calcs of your house. You probably don’t have that.
3 -
You are looking at a different model Ed, many heat pumps have their rated heating capacity near 0f these days, typically we would call them "cold climate" I think mitsubishi calls them "hyper heat" models. I believe @Kaos linked to the data sheets which show 28,600 btu/hr at 5f COP1.91, which is a fairly standard output for a 2.5 ton cold climate modern inverter heat pump (mini split ODU)
just double checking the brand I am more familiar with, LG, their cold climate (RED) multi ODU 36k model, is 36k btu/hr output at -13f, obviously more heat output as the outdoor temp rises I can link the spec sheet if needed but don't want to confuse the conversation by throwing in a different model link here
I have had this issue when the outdoor temp is as high as 35f. If I only run the 18,000 Btu by itself it has kept the downstairs at 70-72 when set at 70 when outdoor temps are into the low teens to single digits. This is why I’m so confused. I understand the machine has limitations but to completely lose it at 35f outside and only running 2 inside units seems ridiculous for a hyper heat condenser. I have measured discharge air temp with a meat thermometer at up to 110 f when only running the 18. When I turn the 12 on simultaneously the highest I’ve measured is in the 90s
I would not be surprised if low on charge from start or a leak. Someone will need to weigh out charge and then calculated what’s needed and weigh back in. Talk to installer and see what he charged with? Maybe just used pre charge weight? Knowing what it started with will help determine if leak after current charge weighed out. Takes competent refer tech.
1 -
This really sounds like a design issue to me. You probably don't have any of the heat loss data for the rooms or the outdoor design temp they were calculated at. Get the charge checked and weighed to see if it is correct. If it is, you were swindled from your installer from the start. if it is low, you had a sub-par installer.
This has nothing to do with Man J or heat loss. The unit is simply not running properly.
Mitsubishi publishes a correction factor for defrost. It is actually not that much once you get bellow freezing:
@ksm If you can't get hot air out of all heads when cranked, the unit is down on juice. 99% of the time a multi split operating strange is a charge issue.
3 -
Its definitely not functioning as designed. Hopefully just a charge and not a valve problem.
My house has the non hyper heat version with 3 indoor units. It has no problems like that (keeping all heads roasty toasty) when outdoor temps in teens. Efficiency is another issue though.
Did you have anyone come service them? Or is it because the outside temperatures came back up to what the system is designed for?
Without pulling and weighing the charge we can only guess
"All units put out air between 110 and 115"
You didn't type the indoor air temp, but those numbers seem really good
I have not had them serviced. I find it odd that when cranked all the way they are capable of producing such warm air but when it’s in the 20s out and I have two heads running at 70-72 degrees the downstairs unit cannot keep up and is indicating the thermostat is not satisfied. When not keeping up the air coming out is usually in the 90s. Why can’t it produce that 110 degree air when it only needs to reach a setpoint of 70 and is struggling to do so. I have also noticed that when it’s colder outside, it does defrosts when there is absolutely no frost on the coil whatsoever. It used to do this every 15 minutes but after having the circuit board replaced it is only every hour at worst. Is it normal to defrost when no frost on coil?
I would start with is the charge correct.
There were some 'firmware' issues. Not sure if that's what may be happening to your unit. We had a unit (might be the same model) that had to be re-written (it was doing funky things, more defrosting than it should have)
But if it's defrosting for no apparent reason, that could be it. The other popular reason is, you lost some juice (leak)
You will never know where to begin until you get the charge verified. Once you know if it has the right charge, then it can be figured out what may be wrong.
Late to the party but just want to add 2 cents.....I deal with tons of minis in all forms it's a big part of my business. Can't tell you how many times I see this and it's the user causing it. Not saying this is you but......the fan speed limits the output. In any mode the fan needs to be in auto. Anything less limits heat/cool ouput. People put them in low or slower speeds and call with problems all the time
The fact you cranked them up and set to high and they put out led me to post that info
2 -
I quite agree that the most likely culprit, if there is one at all, is the refrigerant charge.
But, having said that, may I also wonder if you are running up against the maximum capacity of the system? I wonder this because you note that when it's 32 out it produces 110 degree air, but when it's 20 out it drops below 100… what is the inlet air temperature to the heads in those cases?
yes I always have the fan in auto. When I say I cranked it was just during experimenting. I did this a while ago but Inlet air was probably 70 when 110 outlet air and around 67 with outlet air below 100. Upstairs head also still buzzes even when off. Nobody can tell me why.
the buzzing is possibly from the unit allowing extra refrigerant to bleed thru that head.