Recessed radiator valve is higher than old radiator.
![gm4533](https://secure.gravatar.com/avatar/77d45c2993d3f631bce0ee3bbb47f74e/?default=https%3A%2F%2Fvanillicon.com%2F8ccea1a49e43bfcbcf85d1530d1d137e_200.png&rating=g&size=200)
Hi, I just replaced my recessed radiator with a bigger one for more BTUs. The issue I'm having is that the new 12 section sunrad radiator has the connection about an inch higher than the 10 section one and this is creating a 1 inch gap to the connection pipe coming through the floor. I have pictures attached to show you what I mean. Is there anyway I could get an extension to mate the two pipe without removing the floor to change the piping?
Comments
-
A union with a close nipple maybe. Is the rad on top of the carpet or the floor beneath?
0 -
The radiator is on top the carpet. I replaced the carpet padding with 7/16" thick wood blocks where the legs sit.
0 -
What's below?
0 -
This. And you may find you actually need to raise the radiator slightly to get it all to fit.
However, before you start to do that, are you sure that the pipe in the floor didn't drop some when you removed the old radiator? Very sure? Any way to find out if you can lift that pipe? Because… if it dropped the part under the floor may have too little pitch or even be reverse pitched, which will cause water hammer…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Well there's at least 7/16 closer you can get. I second what Jamie said just above about the possibly dropped pipe
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Pluck the union nut up from the carpet with a screw driver or putty knife and pull, turn it on to the threads of the valve. Im thinking it should be as easy as that. If you have access from below get some help and push it up.
0 -
-
I put the radiator on blocks because if the radiator sinks too much into the carpet I won't be able to fit the bottom cover.
As for what's under the carpet. The flooring under the radiator is just plywood because the 100 year old hardwood gave out in that area. The area where the heating pipe is there's a 12" x 24" piece of plywood that i can remove to access that pipe if I really need to alter it. It's just that I installed new carpet in that room and I would have to pull it up.
0 -
-
Intplm, I actually have access to the pipe from the basement. The pipe runs through a notch in the joists, I cant push it up any.
0 -
Can I unscrew that union coming from the floor and install a longer union?
0 -
Let's go back to square one here.
Now that I really look at this, that is a union coupling, not a threaded joint.
You cannot add an extension to the piece coming up from the floor. Period. That is half of the union, the other half is on the valve.
The ONLY way to do this is to lift that pipe up to meet the valve and screw the union together. The only other option would be to access the piping from below and add a short extension between the pipe itself and the union.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements