Need help with this old snowman boiler
Hello all,
Bought this house in October and it came with a new Burmham Megastem for 1st floor and this ARCO snowman for 2nd and 3rd floor. There are 6 radiators on 2nd floor and 3 on 3rd.
The 3 on 3rd connect to the valves on 3 of 2nd floors radiators.
This thing takes 40 minutes to get to temperature, I’m burning through oil. It was serviced in September.
The guys at the heating company said to keep the PSI at 1psi but from what I’m reading, it should be around 10-12psi ?
I desperately want to get rid of this because it takes so long to heat but is it the PSI?
the circular gauge almost always reads 0 never goes up.
The PSI is controlled by the grey box to the left of the killswitch
thanks
40 min seems pretty long even for a snowman
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
any ideas on the PSI question? I have to imagine 1PSI is super low?
Who the dickens said 10 to 12 psi? That old beast is steam — and 1 to 2 psig max is all you ever want. I think, perhaps, that you were mistaking the recommendation for hot water heat?
Anyway. 1 to 2 psig is what you want.
No, the pressure is not what makes it take a while to heat.
Now — whether you actually have that or not is an open question. I'm not at all surprised that the old round gauge doesn't go up at all. Half of them don't work, and none of them are all that accurate at low pressure.
A couple of quick safety checks, though. Below the low water cutoff there is a ball valve with a green handle which is closed. It should be. However, once in a while — at least once a month — that low water cutoff should be checked, and the way to do that is — with the boiler running — open that blowoff valve all the way. The water level in the sight glass should drop and the boiler should shut off. Now close the valve. The water level in the sight glass should come back up and the boiler should restart.
Does this boiler also do the hot water for those apartments? I have an idea it does. I'm also thinking I see an automatic water feeder on the right, tucked up next to the big white vertical pipe. Does it have a readout on it to five you some idea as to how much water — if any — it is feeding?
Now there are several clever ways to add a low pressure gauge to that thing, which — if you were to keep it — might not be a bad idea.
However…
Much as I love antiques, that boiler is doing you no favours so far as oil usage goes. Plan to replace it. I'm not totally pleased with the installation of the new boiler, but it's not actually horrible, so possibly the same outfit.
you’re right, I was looking at the PSI for how water boilers.
Noted on the green valve
it can do hot water but I closed that off and have electric hot water heaters instead. I will likely disconnect that whole part of the boiler so it stops heating the water.Any ideas why it might be taking so long to heat?
I will try 2psi since it’s 2 floors and 9 radiators.Thanks
PSI should be low. These systems are designed to never need more than 2 PSI at the boiler on the coldest day of the year.
You might start by replacing that tiny main vent where it drops to return to the boiler. How long is that main, and what pipe size?
The MegaSteam is a great boiler, but whoever installed that one couldn't be bothered to read the instructions. Where are you located?
hmm I replaced the main vent with a Gorton 1
and yeah I’ve been told by a few people that the mega was not installed totally correctly. Before my ownership.Any other ideas on why it takes so long to heat up?
Thanks0 -
Where are you located? I have an excellent Asbestos abatement company...also reasonable. Mad Dog
You're heating up a lot of water and a lot of iron. That snowman was intended to operate warm all day long (and most of the night!) on a steady fire — just enough to keep it boiling. Then if you needed a bit more warmth, you went downstairs and poked the fire. Literally. The modern setup with a fuel fired burner which is either on or off with that massive a boiler really doesn't work all that well.
Depending on what thermostat you have, you might try setting it to more cycles per hour — if it's set on 1. Try setting it on 3. It may be quicker and more even. It will also be less efficient, but… that's life.
Make sure it is running off only the thermostat and the pressuretrol and the aquastat for the dhw coil is turned down or disconnected.
It should heat at a couple ounces of pressure. If parts aren't heating either air can't get out or water is trapped somewhere or possibly the boiler is underfired. Setting combustion on a boiler like that isn't the same as for a modern boiler.
1 -
thank you all for this info!
in other words, underscored means that burner is too small? Another comment mentioned that it’s a “slow speed burner” , could be my issue?
It might be underfired — but it's not really that likely that it is underfired or undersized by that much. Not to worry. "Slow speed burner" simply refers to older oil burners — like the one you have — which had lower speed motors, and thus lower speed fans and pumps. For various reasons, they tend to be less efficient inherently than newer burners, but are actually better suited to that old boiler. Which isn't that efficient inherently, either!
so I now am realizing it’s surging. The water in the gauge goes up and down quickly. Seems totally related to its inefficiency. Thoughts?
Well surging can cause added inefficiency if its producing wet steam that could be the reason it doesn't heat well.
Seems odd I don't think I have ever seen one of those old boilers surge.
never had trouble with those old boilers and they were never made with skim tappings.
Think about that!!😊
They have a big steam chest above the water for the water to fall out of the steam before it goes out to the system.
I know exactly why that boiler is taking so long to heat up and make steam. When that boiler was brand spankin' new, the fire was COAL and it was located about 20" higher near the middle door of the boiler. When it was converted to Oil Heat, the fire grates were removed and the oil burner was installed in a combustion chamber that was built inside the ash collection pit at the bottom. That fire is 20" away from the place where the fire was designed to be.
I actually did a job on a commercial boiler in 1979 that had the oil burner in the bottom just like your boiler does. It took about 6 hours for the steam pressure to build enough to get the unit heater fans in the building tio start to heat the space. I removed that oil burner and installed a high efficiency oil burner in the fire door of the boiler. That same boiler made steam in about 15 minutes and the fans in the unit heater started to blow hot air in 20 minutes. That modernization saved my customer over ⅔ of the oil usage with that modernization job. YES his oil usage was ⅓ of what it used to be before the new burner in the door job.
I dont know of anyone that might be willing to take on that job today, but if you could find one, that would be much less expensive compared to a complete new boiler installation.
2 -
I've seen a couple of those fire door installations (inshot gas)and they do work great.
Here is what you need an old-timer to do for you
- Remove the old oil burner and seal up all the openings below the fire door.
- Fill the old ash pit with dirt debris and sand to within 7" of the expected bottom of the flame position.
3. Add 4” of Vermiculate Insulation and pack it down with a fire brick to form a base to hold the fire brick combustion floor. This may be done in a rounded bottom shape to make a nice fire brick reflective surface to send the heat back into the flame for more complete combustion with less excess air
4. Top off the floor with 2000°F fire brick. (K20). They can be cut and shaped easily with a hack saw blade to conform to the round sides of the boiler combustion area.
5. Install the new high efficiency oil burner in the fire door.
6. Be sure to add a secure latch to the fire door so the normal pressure of combustion will not unlatch the door and cause the fire to burn outside the fire box hanging on the opened door.
7. Be sure to include all the necessary safety limits and controls including a pressure switch that breaks on temperature rise, A low Water Cut Off, primary safety control (usually included with the new burner) and a operational barometric draft control, oil filter and perhaps a tiger loop to make the job easy to operate.
The side arm DHW coil can be disconnected or not. As long as the DHW temperature limit is not connected to maintain a minimum temperature, then the additional water and steam in that small amount of piping will have very little affect on the amount of fuel used.
Putting the fire where it belongs will allow you to use a smaller nozzle and still get a hotter flame, in the designed location of that SnowMan. That is where the Dead Men that designed those boilers wanted the flame to be.
4 -
@EdTheHeaterMan you are the MAN. Thanks!
I hear ya' Ed
I found an L model Columbia boiler with the old original Columbia oil burner (1725 RPM) about 3 years before I retired. The thing was well maintained and looked good. The only problem was the gasket between the tankless coil looked like a real mess and that was covered by the front cabinet that also covered the cleanout openings and the burner. I told the customer that the boiler was older than me (because it looked like the boiler in my home when I was 6 years old). I removed the Columbia burner and installed a Riello with new L7224U controls to make it a cold start boiler. The savings was 40% from the old burner and the maintaining temperature control system. I think that the customer still has that in operation today.
I gave no guarantee for the old boiler except this: I would replace the boiler if it started to leak within 2 years and credit ½ the cost of the new modernization job to the price of the new boiler. Full price if it leaked within 1 year. (then I would order a boiler less burner and save a couple hundred on the new boiler cost)
I have a feeling that this old snowman boiler may outlast the both of us if the OP can get someone to help him save $$$ on operating it.Edward Young Retired
1 -
So no MegaSteam there? And repipe the other at the same time?
I didn’t know if the Mega Steam was having a problem. OP did not mention that there was any problem. Do you often recommend fixin’ stuff that aren’t broke?
Second boiler equals more than one person, paying for heat in the building, equals rental income property, equals return on investment, equals, if the building is too expensive you might as well sell it!
sounds like the building owner has a decision on what is the best option to reduce the cost of filling that oil tank? If a burner in the door will cut the oil bill by 20% at about $2,000.00 DIY + a professional combustion analysis upon commissioningV.
Over $20,000 for your suggestion and save 25% on oil, I might choose to modernize over a Mega Steam.
and I believe that savings will be closer to 50% based upon my experienceBut that’s just me
I know what you mean @HVACNUT , and a new Mega-Steam installed properly is going to cost over $12,000 to $19,000 in just about any market, and to repipe the existing one will be about the same amount of labor and pipe fittings, less the removal of the old boiler (‘cause you are using the same boiler) and the cost of the new boiler (‘cause you are using the same boiler), so that is gonna be around $5000.00 to $8,000.00.
A new burner and some sand, fire bricks, draft regulator, and some fuel line might be had for less that $4000.00 retail and if it is a DIY project it will cost less that$1,300. Add in a professional to do the combustion testing on start up of $150 to $250 and leave the existing MegaSteam alone if it is working, That is a really big difference in $$$ for a landlord that is trying to reduce costs.
Lets spend $20,000 to fix your systems because that is the only way I would do it
OR
Let's put the new oil burner in that old beast for about than $4000.00 and you will save almost the same amount of $$$ on your oil bill.
Understand this, that old boiler is OLD and there are no guarantees on how long it will last. But even a brand new boiler can fail within 5 years under warranty and it will cost you $$$ out of pocket to replace a section or the whole block assembly (depending on the manufacturer’s decision). Knowing how well those old ARCO Snowman things are built, and how well the Mega Steam is made today, I would chance it in my own home. Why not give this guy the option to decide?
1 -
Are those prices WITH Asbestos Abaitment?
Building owner has indicated that he is going the encapsulate route. again less expensive that the removal option.
WHEN it has to be removed that’s going to be a big nut!
Yes, When. 10 years from now? 20 years? 50?
Cost now vs. cost in the indefinite future. And in any event, the burner can be re-used on whatever replaces the snowman. Not a lot of downside to @EdTheHeaterMan 's suggestion.
hi all, it’s working much better now that I drained the system and connected the aquastat.
I like Ed’s idea, seems reasonable. I am also now aware that my megastram was piped wrong. This was before my ownership. It does work very well though and does not use much oil
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues