Sure. The problem I'm running into is how do you model it?
Let's say a heat pump has a minimum modulation of 6,000 BTU/hr but your heating load is 4,000 BTU/hr. So that heat pump is going to run for 40 minutes per hour. But is that going to be four ten minute cycles, ten four minute cycles, forty minutes on and 20 minutes off? I don't see any way of predicting that in advance, and it's a pretty big difference which one it is.
0 -
"There is a fundamental asymmetry between heating and cooling with a heat pump."
Note that there is an asymmetry in hot weather vs cold weather too. Above I posted the hours-by-degree chart for Washington, DC. On the heating side it goes to zero hours at 5F, 17F below the 99th percentile temperature. On the cooling side it goes to zero hours at 101F, 9F above the 99th percentile. The all-time low is -15, which is 37F below the 99th percentile and 20F below the zero-hours temperature. The all-time high is 106F, which is 14F above the 99th percentile and 5F above the zero-hours.
So the cooling end of the curve is a lot steeper than the heating end of the curve.
You see this regionally as well, that the cold in the coldest parts of the country is a lot more severe than the heat in the hottest parts of the country.
0 -
Oh absolutely, @hot_rod . And, just for the sake of curiosity, what do you as a manufacturer look for as a mean time between failures? I've never known for that type of equipment. 10,000 cycles? 1,000? 100,000?
And of course that is the major downside of on/off cycling — it does impose a definite life-limiting burden on any mechanical component. One would think that all solid state circuitry wouldn't be quite so subject to that — but it does have a mtbf rating as well.
No, I was thinking more along the lines of the optimum characteristics of cycling as an approach to modulation, and the efficiency hit (if any) of various strategies…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
OK, this is what I'm thinking for modeling short cycling. Stipulate that:
- At the start of each cycle there is 2 minutes of "wasted" power use while the compressor gets up to speed.
- The compressor has short-cycle protection that limits the minimum on time or off time to any cycle to no less than ten minutes.
So if the duty cycle is less than 50%, the on time for each cycle will be ten minutes, the off time will be whatever is needed to achieve the duty cycle. With two minutes wasted from each ten minute cycle, the efficiency hit is 20%.
If the duty cycle is more than 50%, the off time for each cycle will be ten minutes, the on time will be longer, again whatever is needed to achieve the duty cycle. So if the duty cycle were 66% you'd have 20 minutes on, ten minutes off. With two minutes wasted out of 20, that's a 10% hit. If your represent the duty cycle with DC, the on time would be:
OT=DC*10/(1-DC)
The efficiency hit is 2/OT, which simplifies to 2/(DC*10)/(1-DC) or 2*(1-DC)/(DC*10) or 2/10*(1/DC-1), which goes to 20% as DC approaches 0.5 and to zero as DC approaches one.
How does that sound?
0 -
Pretty much all these units are inverter based for both compressor and fan. They are pretty gentle on ramp-up, I doubt cycling does much wear. Unlike a boiler with a gas valve and ignitor, there is nothing really turning on/off here.
I did find something for an air to water heat pump. Look the trace about 5.58, there are no big drops in COP when the unit cycles.
Similar argument about a cycling unit needing to deliver higher temp air VS running continuously, thus lower COP, can be made for air to air as well. I think as long as the cycling is only happening on the warm end of the shoulder season, this COP loss is big enough to worry about.
Where you have to watch sizing and cycling is with multi splits (many indoor units on a single outdoor unit). Since those bypass refrigerant through any indoor unit even when not heating, oversizing and cycling pretty much kills the COP. Those units oversized, COP can drop to around 1 in a hurry.
0 -
I think on my unit the circulator never shuts off. It modulates from 3- 6.4 gom the outdoor fan runs unless the call for heat ends. So its mainly the compressor modulating. My control display shows fan rpm and compressor Hz
So in my case I only see on/ off of the fan and compressor when the buffer tank is satisfied
So I would say they are engineered well as to cycle efficiency.
I know that was a complaint with early A2whp, with fixed speed compressors and probably a sizable amp draw when they kick on? Fan and compressor
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Actually I was going back to contemplating cycling on hot water or steam fuel fired systems. I had no idea that there was that much wasted time or power in heat pumps. I like them even less than I did before now.
Something is stone age about that…
Especially considering that I can bring a gas turbine engine from off to full power in exactly the time it takes to spin up from zero rpm to 100% N1 — perhaps 20 seconds on a 76,000 pound thrust turbofan. The old Solar gas turbine genset I had at a waste treatment plant, about 40 years ago, could pick up the full plant load in 15 seconds, cold start.
Humph.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
The old Solar gas turbine genset I had at a waste treatment plant, about 40 years ago, could pick up the full plant load in 15 seconds, cold start.
That's hard to do today. The clearances in both the compressor and turbine are so tight that they need a certain time at idle power to warm the cases. If you tried to use a modern commercial aircraft turbine engine to takeoff in 20 seconds……………..it would most likely seize on the case ID.
Check out the flight of Pinnacle 3701. These jokers nearly stalled the aircraft at 41000 ft. and both engines shutdown due to poor airflow at a very high angle of attack. They could NOT restart them!! They didn't live to tell about it.
0 -
@Jamie Hall i think the cycling efficiency hit for a non-modulating forced water boiler is minor if you have a thermal purge. If the boiler is sized 1.25ish x load, then I think it’s not worth worrying much about. If we’re talking about installing a new boiler, why go bigger than that?
I think we’ve all discussed this point before? Is anything new being added?
0 -
nope! but it's fun… I remember that Pinnacle airlines crash. The engine installation on that aircraft has a minimum airspeed for a windmill start, partly from turbine rub but as much to friction in the auxiliaries. The folks in the cockpit not only took the aircraft above its absolute ceiling in a zoom climb — and the engines flamed out, to no one's surprise — but never got the airspeed high enough for a windmill start on the way back down.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
@Jamie Hall "I had no idea that there was that much wasted time or power in heat pumps"
Where do you see wasted power? Anything air to air will have ECM indoor fans, those on low speed might use 20W-50W.
The air to water units also use ECM pumps, since they are generally connected to larger pipes, running at a couple GPM is around 10W-20W.
There is also a crankcase heater ~50W-80W, that usually doesn't run if the unit is operating even if cycling.
A standing pilot and a draft hood would loose orders of magnitude more energy.
0 -
OK, new chart. This is the same format as before, but I added in a correction for short-cycling:
The Y-axis is efficiency, expressed as a percentage of the most efficient size. The x-axis is sizing, expressed as the rated capacity of the heat pump divided by the design heat load. Left is undersized, right is oversized.
This is more the shape I would expect, although I will admit that's a contrived finding because I'm just guessing at the effect of short-cycling, so of course I'm going to see what I expected to see.
Anyway, the most efficient size is slightly oversized, there's not much difference between 100% and 200% sizing, get outside of that window and efficiency starts to fall off.
0 -
@Jamie Hall "I had no idea that there was that much wasted time or power in heat pumps"
In this context, what does "wasted time" even mean?
0 -
All Systems need 10 - 15 minutes run time yo reach peek performance. Anything less is not good.
do you step on the gas hard until you hit the speed limit or control the speed.0 -
-
sounds like a interesting read!
0 -
-
and @Jamie Hall Surely, spoiled is the wrong word, "fortunate" (and in some cases ungrateful) is proper. As you mention, we shouldn't 'try to live the hard way' simply because people before us did. Great correction.
My (failed) point to make was that maybe we lose on the efficiency end of things because we're more concerned about the convenience of things. While the hospital or a business certainly isn't interested in 'being chilly' at the benefit of saving a few pennies, maybe some homeowners would be?
"An important part of this calculation is, what is the penalty for oversizing and what is the penalty for undersizing? " @DCContrarianGreat question, would love to learn more!
1 -
@RascalOrnery I actually agree with you — fortunate is a much better word. And you bring up a very important point (if it was your initial thought, I apologise for missing it!): There is a very definite and often rather dismaying set of tradeoffs between comfort, convenience, cost, reliability, and efficiency (and often simplicity). It's a fascinating area to comtemplate… at length! — and every situation will be different.
One of the things to be grateful for is that — so far at least — we live in a society where individuals can evaluate the various tradeoffs and make choices.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Every load calculation software I have ever used has been capable of taking into account all of those things. I can input number of people in each room, individual devices that populate as an estimate, or if I know the devices that are in the room I can manually enter an internal load number. I can do this as a block for the whole building, or room by room. Including solar gain etc, even whether or not there are blinds on the windows and what type of coverage those blinds will have
1 -
How does zoning divide up heating load? Surely a house requiring 100,000 BTU with two zones is going to be paired with a different device than the same house with five zones, or am I wrong? Are they treated the same and if so, why?
0 -
When you're sizing for cooling you add all those things, assuming the house is fully occupied and the occupants will be bathing and cooking. When sizing for heating you assume it's night and there's no solar, no equipment is running and the occupants aren't doing anything but sleeping.
The Manual J process is about comfort.
1 -
If you have a device that can provide 100,000 BTU/hr to either two or five zones, and provide each zone with the amount it needs, then that same device could be used in either configuration. With hydronics that's normally the case. With furnaces or heat pumps you run into issues with minimum sizing, you run into minimum output constraints when running only one of five zones. As you go to more zones sometimes you have to have more, smaller pieces of equipment.
But in either case the total load is the total load.
1 -
An apples to oranges comparison? Failures of bridges, airplanes, fire suppression systems, and sewage systems cost lives, as can the failure of a heating system. Unless significantly undersized, a heating system that can't keep up on the coldest days causes discomfort.
0 -
Manual J has fudge factors. I have heard it oversizes the load by 30% or more. Then when the appliance is chosen and the load is say 61K and the closest appliance is 66K when the 58K would be adequate. Not likely to have a problem unless the insulation or air tightness was a lot worse than what was entered into the load calc.
0 -
I've skimmed through some of the thread……..
Regarding having a system that is more efficient most of the time and loses some temp on a rare occasion….
It makes sense, but, what's the operating cost difference between having one that is slightly oversized vs one that's slightly undersized? "More efficient" doesn't really say anything useful.
If you're talking about living with a system that falls behind during extreme cold, and makes it so you can't even hold a door open to bring groceries in etc, to save $10 a season……… that's not practical.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
In my area design day is 0f, most everyone I know sizes for -10f. Generally I check the numbers between both temperatures, there is rarely a different piece of equipment needed whether I size for 0 or -10f, maybe one time it put me to the next size boiler but honestly I never remember that happening. On top of everyone I know sizing to a lower temp than what is "code" the manual J software also has a bit of a fudge factor in it. We have some times when you might see -30f, I've never had a situation where the boiler is undersized (on jobs i sized anyway). To add to that when we are talking extreme temps, outside the "design day" parameter it generally is something that is not sustained, maybe one whole day, usually just a few hours though. I would recommend that anyone, no matter the size of their heating equipment, not leave the door open when the outdoor weather is beyond design day conditions, it's going to give you a blast of cold no matter what at that point, pick up the groceries the following day, maybe the temp drops for 10 minutes or so? I don't think we should be designing residential heating systems for keeping the door open below design day conditions either way.
2 -
I guess you're not familiar with Stoßlüften?
Few will be unless you're German, but do a quick search on it.
Do they practice Stoßlüften during extreme cold? I have no idea, but I'd love to know.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thats interesting I'm curious what some German folks have to say about this in the current age since their companies pushed outdoor reset so heavily and obviously outdoor reset doesn't play super nice with Stoßlüften
(leaving windows open in cold weather to provide fresh air for the curious)
Maybe they just all switch to ERV/HRV?
I'm thinking maybe they just expect it to be cold briefly while they ventilate? probably don't do it when its extreme cold temps though? I imagine this is mostly in apartments like we have in NYC old practice of opening the window for ventilation? at that point the boilers are definitely sized for it I'd think, a new house in the US needs ventilation accounted for whether through infiltration or dedicated mechanical means, and is taken into account by all manual J software
1 -
Being a "bear of very little brain", I am at a loss for words. Unable to follow much of the logic of this thread very far I've come to the conclusion that it has devolved into a discussion about how many angels can sit on the tip of a pin.
At 80 years old I have known privation. Hunkering down in dank muddy fox holes, clattering down the tracks in the far corners of empty box cars wrapped in a thin blanket, spending an unscheduled night in a snow cave next to a dead snowmobile at 11,500 feet, feeding the tiny firebox of a small woodstove in a drafty Montgomery Ward "kit house" - I have known privation.
Is there no tolerance left? No willingness to undergo a little temporary inconvenience? Is there no sweater in the closet to don when the design day calculation turns out to be off for a few hours. Not all of us here in these United States expect to spend the winter indoors at 70 degrees Fahrenheit - actually, probably less than 50% of us do. (That would be about 2% of the population of the planet.
Please don't misconstrue. I like comfort. I never became accustomed to want and strove to overcome it. But having experienced and survived it gives me an appreciation of comfort, not an expectation of it. Some automobiles can go 170 mph yet the speed limit is 75. The prudent drive slower yet.
Remember "Cold 70"? I wonder if we could become accustomed to "Cold 60". Talk about energy savings!
2 -
Air doesn't hold all that much heat. Say a 2000sqft house 10' ceilings, has an internal volume of 20k ft^3. Raising the temp of say 20% of that air from 0F to 70F takes ~5000BTU, so pretty much squat. As long as you don't keep opening the door to let that fresh air in many times an hour, doesn't increase the load all that much.
2 -
I was just reading about California, which uses a different energy code from the rest of the country, what they call Title 24. For heating equipment, they have an anti-oversizing provision:
"Heating design temperatures shall be no lower than the Heating Winter Median of Extremes values." I assume that's the same as (or similar to) the average annual low reported by NWS. For perspective, where I am 99th percentile temperature is 22F, average annual low is 6F.
They're talking about changing this, the new proposed language is: "Heating design temperatures shall be no lower than the 99.0 percent Heating Dry Bulb or the Heating Winter Median of Extremes values." Which makes no sense, because 99th percentile is always going to be warmer than median extreme. I suspect what they're trying to say is it has to be between those two value.
0 -
Every state adopts their own energy code though right? It's different here in Michigan, and further different parts of the energy code are only in effect depending on your climate zone. We also have a written rule in the code about what temp we can size to, it must be sized "in accordance with manual J" and manual J has strict rules on those temperatures you choose. It rarely if ever really matters though unless your entered value is massively off from the "correct" value. My county is known to have the most strict building department in the state and they are OK with how I calculate the load, I told them I would change the paperwork if they want but we are still sizing emitters etc down to a bit lower temp. Modulating equipment essentially negates the equipment sizing requirements (which I believe are no greater than 30% over the load here) because it modulates so the max input is less important. Also there are stipulations that don't make the equipment sizing all that strict for single stage equipment as well, If your brand only has an option that is either less than required load, or next step up is 40% too large, they have to let you install the larger one (in Michigan anyway)
0 -
I was going to write something about the above two posts… but I guess I'd better not.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
"Every state adopts their own energy code though right?" Other than California every other state (and DC) is based on the IECC, with whatever modifications the state legislature puts in when enacting it and then subject to whatever interpretations the local AHJ's come up with. So they all come from the same place. California is the only place that starts fresh.
1 -
In addition the localAHJ can add addendums. We had multiple pages of addendums to the UPC and UMC where I had my business.
We had the combustion air requirement cut to 1/4" per thousand due to snow banks in, and freezing boiler rooms.
So glad to see mod cons and sealed combustion equipment for the cold snowy climates.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes, one I installed on the beach, which I too-conservatively sized steam with a 15% pick-up factor and a baseboard hot water loop in the basement. When the wind blew off the ocean on a 10-degree day, it just wouldn't do the job. I wound up over-firing the burner 5% to compensate.
0 -
@GGross : "
"whether I size for 0 or -10f"
design day temp usually comes before the heat loss calc???
how do you do this—from the heat loss somehow? with straight line calculation from the heat loss per degree??? so many K btu's per degree?? or do you redo the heat loss calculation?
0 -
Not especially relevant to the topic, but perhaps interesting to some.
I set up a 100lb/25gal propane tank as a buffer tank with two HX coil necks for tankless heaters , fed by a coal boiler and a (preexisting) oil boiler. One HX is for DHW, and the other is for the hot tub. (The hot tub circulator flow runs through a UV sterilizer, works nice.)
The coal boiler runs flat out most of the time during the peak heating season, and the oil boiler kicks in and runs as much as needed to satisfy high demand. The buffer tank prevents short-cycling nicely.
There was an error rendering this rich post.
0 -
Wind is the one factor that AFAIK is not typically accounted for in design day sizing but can really suck a lot more heat out of the building.
In our 4-unit condo building in the Boston area, during the Feb 2023 polar vortex, our boiler run times represented a 40% increase in heat loss over the design day zero-degree heat loss in still air. Normally our zero-degree heat loss in still air is about 100,000 BTU/hr, but during the polar vortex event with near-zero temps and persistent winds at 30+ mph, we lost 140,000 BTU/hr on average.
That is in a 100-year old building with masonry first floor, wood frame second floor, double-pane replacement windows on one side, and professionally weatherstripped original wood windows (with spring bronze and silicone bulb weatherstripping) plus old storms on the other side, and 10" blown cellulose in the attic.
Our boilers are 3x oversized for a calm, zero-degree day, and they were still 2x oversized for the polar vortex, so they just loafed along. But if they had been sized at the ASHRAE recommended 1.4x of design day, they would have been perfectly sized for the polar vortex with high winds.
So an extra 33% pickup factor or 40% ASHRAE margin can be the difference between coping with high winds on a design day, or not.
1
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements