Is it possible to extend snow melt loops.
Hi,
I've laid the snow melt loop for a sunken entrance through my basement pad but not set the outside loops in concrete yet. Do you think I could splice the pex to be able to extend the loop into the concrete steps I'll be pouring at the same time? I originally wasn't intended. The loops is very small, only 30sq ft of pad, just worry about separation.
Comments
-
Personally I'd rather not see PEX splices — or anything else splices — embedded in concrete. However, if the splices can be located where you can get at them when they leak, there's no problem.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Sure, what size and type of Pex? Type A? If so, I would expand the Pex and use a brass fitting (coupling) and not a plastic fitting. I would wrap the fitting with black electrical tape afterward to prevent corrosion. I would stay under the recommended loop length depending upon tube size.
0 -
why not run a seperate loop for the stairs?
0 -
It is better form never to splice. That being said, splices happen! Test your splice when you are done and isolate brass splices from the concrete. When it comes to stairs, be sure to run the tubing parallel to the treads and ~2" from the surface and edge of the nose. I am in the process of tearing out a very expensive staircase where the original contractor decided it was easier to run the tubing in the lower portion of the stringer.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
the Pex tube manufacturers have a specific method to follow for in slab splices. Heat shrink tubing is a good option compared to electrician tape.
Whatever you use needs to be compatible with the Pex tube outer coatings, EVOH typically.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
Several PEX manufacturers will allow the use of their couplings in embedded applications, as long as you follow their instructions.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements