In need of suggestions replacing an Weil McLain EG 65 steam boiler
also taken a few pics of my current boiler. I am starting from ground zero since I don't really know anything about boilers but I want to get the right boiler at a fair price.
Comments
-
-
-
Actually I would have said the current piping isn't bad at all, except that the steam main should come off after the right hand riser rather than before it, so the sequence from left to right would be riser, riser, steam main, equalizer.
I especially like the location of the pressure gauge and the pressuretrol. I wish more boilers were piped that way.
I too wonder what is the matter with the current boiler that you feel a need to replace it. In any case, if there really is a need to replace it, find someone who will size it properly. Steam boilers are sized on the basis of the number and size of the radiators they power, not on the size of the house.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Just move the boiler over about a foot and put the steam riser here
If you believe a new boiler will lower your operating cost. stop thinking that. Steam is different than Hot Water boilers that are inefficient. Your new boiler will cost about the same to operate as the one in this picture.
So if your boiler is not leaking or has other major problems, all you really need is a good steam boiler man to adjust and maintain it properly. A new boiler will not solve problems with the rest of the system. if your radiators are having problems, then you need to address those problems.
Why do you think you need a new boiler?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
3 -
Sorry I cant help it
In need of suggestions replacing an Weil McLain EG 65 steam boiler
You can look at this model from a company out of Michigan City Indiana.
https://www.weil-mclain.com/products/eg-series-6-gas-boiler
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Changing the boiler will save you pennies if done properly.0
-
@RCooper , I agree you would need a good reason to replace it. But if you want a real good set of eyes on it, look no further:
https://heatinghelp.com/find-a-contractor/detail/g-w-gill-plumbing-and-heatingAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
-
I agree, it is a good looking pipe up except for the indiscretion of main takeoff between the boiler risers.0
-
I had a carbon monoxide leak soot was blocking carbon monoxide that was supposed to go through my chimney and it ended up in my basement causing my detector to alarm. I had 2 contractors out and was told the following " Heat exchanger on both sides on top has cracks and is leaking steam causing heat exchange to rust and soot right side in back is bad not repairable unit needs to be replaced" Sorry for the grammar I am typing exactly whats on invoice.delcrossv said:What's wrong with the current one that you want to replace it?
0 -
How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I was told by 2 contractors boiler was leaking via cracks on both sides causing rust and soot which caused carbon monoxide to leak in my basement. I will call the contractor you recommended first thin tomorrow. thanks!Steamhead said:@RCooper , I agree you would need a good reason to replace it. But if you want a real good set of eyes on it, look no further:
https://heatinghelp.com/find-a-contractor/detail/g-w-gill-plumbing-and-heating0 -
RCooper said:
What's wrong with the current one that you want to replace it?
I had a carbon monoxide leak soot was blocking carbon monoxide that was supposed to go through my chimney and it ended up in my basement causing my detector to alarm. I had 2 contractors out and was told the following " Heat exchanger on both sides on top has cracks and is leaking steam causing heat exchange to rust and soot right side in back is bad not repairable unit needs to be replaced" Sorry for the grammar I am typing exactly whats on invoice.
UL Approved CO detectors DO NOT alarm until 70 PPM of CO has been detected for UP TO 4 hours.They are virtually worthless.Every home should have at least 2 NON UL approved Low Level CO detectors.0 -
I didnt know i was suppossed to add water to the boiler. Yes there is heavy sooting I was told it was due to 2 cracks on both sides of the heat exchanger leaking steamm causing heat exchanger to rust and soot...Jamie Hall said:How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.
0 -
1 st:pecmsg said:
I had a carbon monoxide leak soot was blocking carbon monoxide that was supposed to go through my chimney and it ended up in my basement causing my detector to alarm. I had 2 contractors out and was told the following " Heat exchanger on both sides on top has cracks and is leaking steam causing heat exchange to rust and soot right side in back is bad not repairable unit needs to be replaced" Sorry for the grammar I am typing exactly whats on invoice.RCooper said:What's wrong with the current one that you want to replace it?
UL Approved CO detectors DO NOT alarm until 70 PPM of CO has been detected for UP TO 4 hours.They are virtually worthless.Every home should have at least 2 NON UL approved Low Level CO detectors.
Thanks for the info0 -
I think you need a different opinion. Unless your boiler has an autofeeder on it -- which it might (pictures are always helpful) -- and you aren't adding water you don't have a steam leak. Period.RCooper said:
I didnt know i was suppossed to add water to the boiler. Yes there is heavy sooting I was told it was due to 2 cracks on both sides of the heat exchanger leaking steamm causing heat exchanger to rust and soot...Jamie Hall said:How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Jamie Hall said:
I think you need a different opinion. Unless your boiler has an autofeeder on it -- which it might (pictures are always helpful) -- and you aren't adding water you don't have a steam leak. Period.How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.
I didnt know i was suppossed to add water to the boiler. Yes there is heavy sooting I was told it was due to 2 cracks on both sides of the heat exchanger leaking steamm causing heat exchanger to rust and soot...Jamie Hall said:
I think you need a different opinion. Unless your boiler has an autofeeder on it -- which it might (pictures are always helpful) -- and you aren't adding water you don't have a steam leak. Period.How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.
I didnt know i was suppossed to add water to the boiler. Yes there is heavy sooting I was told it was due to 2 cracks on both sides of the heat exchanger leaking steamm causing heat exchanger to rust and soot...0 -
Jamie Hall said:
I think you need a different opinion. Unless your boiler has an autofeeder on it -- which it might (pictures are always helpful) -- and you aren't adding water you don't have a steam leak. Period.RCooper said:
I didnt know i was suppossed to add water to the boiler. Yes there is heavy sooting I was told it was due to 2 cracks on both sides of the heat exchanger leaking steamm causing heat exchanger to rust and soot...Jamie Hall said:How much water are you adding to the boiler, and how often? I can see heavy sooting causing problems -- such as poor draughting and back draughts into the basement, but... that may also be caused by inadequate maintenance.
This boiler has the old McDonald Miller #47-2 LWCO with water feeder built in to the LWCO linkage. So he has a automatic feeder. The next thing the OP needs to know is that the #47-2 LWCO needs to be flushed once a week. If no one was doing that, then there is a good chance there is a crack in the boiler if it ever fired when the water was too low and the LWCO was full of mud.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
Hiring Mr Gill is a good first step. You should also read this book:
https://heatinghelp.com/store/detail/we-got-steam-heat-a-homeowners-guide-to-peaceful-coexistenceTrying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
delcrossv said:Hiring Mr Gill is a good first step. You should also read this book: https://heatinghelp.com/store/detail/we-got-steam-heat-a-homeowners-guide-to-peaceful-coexistence0
-
If the boiler has leaked enough that the flue passages have filled with rust, and that's causing the sooting, it's toast. We just had two of these situations, and replaced both of them.RCooper said:
I was told by 2 contractors boiler was leaking via cracks on both sides causing rust and soot which caused carbon monoxide to leak in my basement. I will call the contractor you recommended first thin tomorrow. thanks!Steamhead said:@RCooper , I agree you would need a good reason to replace it. But if you want a real good set of eyes on it, look no further:
https://heatinghelp.com/find-a-contractor/detail/g-w-gill-plumbing-and-heatingAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
delcrossv said:Hiring Mr Gill is a good first step. You should also read this book: https://heatinghelp.com/store/detail/we-got-steam-heat-a-homeowners-guide-to-peaceful-coexistence0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements