New Gorton Stuck Vent, Investigative Surgery

ethicalpaul
ethicalpaul Member Posts: 6,653
About a year ago I received a Gorton #4 from Supplyhouse.com that arrived stuck closed. I'm finally posting the video about what I found:

https://www.youtube.com/watch?v=SiNiu5EXMm0

Then in this much shorter video, I find out if Gorton vents really would block water from leaving the vent, as we have heard people mention so many times:

https://youtu.be/XXevhGi02q4

NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el

Mad Dog_2PeteAmgambuzza
«1

Comments

  • Ironman
    Ironman Member Posts: 7,546
    edited December 2023
    I just put two Gorton #2’s on a job and both are stuck shut. They came from SupplyHouse.

    I wonder what’s going on?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Mad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    Were yours recently purchased? About a year ago a few people saw this but I haven't seen anything about it in some months. Mine seemed like it was thrown or dropped. Supplyhouse sent another one that was fine.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Waher
    Waher Member Posts: 286
    I had a vertical No.4 shipped to me in the past month which works, but was covered in the same weird green oxidation and when I washed it out with tap water a lot of green particulates came out of it. No idea what it was.
    ethicalpaul
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    Good work Paul...Bad outta the box go right back from whence they came or the mongo pail..mad Dog 🐕 
    ethicalpauljesmed1Long Beach EdSgtMaj
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    Waher said:

    I had a vertical No.4 shipped to me in the past month which works, but was covered in the same weird green oxidation and when I washed it out with tap water a lot of green particulates came out of it. No idea what it was.

    Was the oxidation on the outside on the chrome, or was it on the inside on the copper?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Waher
    Waher Member Posts: 286
    edited December 2023
    Dust on the exterior finish, some in the sealed bag, and when I washed the vent it came out in chunks like the green pumice type paste dentists use to clean your teeth.
    ethicalpaul
  • JUGHNE
    JUGHNE Member Posts: 11,274
    FWIW:

    I have put B&J Big Mouth and G-2's on the same venting tree.

    The BJBM will drip occasionally as they have no float inside.

    The G-2's next to it would not drip.

    I did get a few G-2's some years ago that did not rattle, float was stuck.
    Returned for replacement.

    A good G2 will rattle and when held up you can blow thru, turn upside down and the float closes the opening tight.
  • ChrisJ
    ChrisJ Member Posts: 16,309
    edited December 2023
    JUGHNE said:

    FWIW:

    I have put B&J Big Mouth and G-2's on the same venting tree.

    The BJBM will drip occasionally as they have no float inside.

    The G-2's next to it would not drip.

    I did get a few G-2's some years ago that did not rattle, float was stuck.
    Returned for replacement.

    A good G2 will rattle and when held up you can blow thru, turn upside down and the float closes the opening tight.

    The float doesn't stop a vent from dripping, it's allegedly for if the system fills with water. If it's just dripping it's from condensate in it and a B&J by design is more likely to drip. I don't recall if you can, but if you mount it with the outlet upwards I'm betting it won't drip. I had mine mounted vertically with the "vent" sideways and the inlet at the bottom.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ChrisJ
    ChrisJ Member Posts: 16,309
    I decided to do some digging out of curiosity.

    I see no mention of a float, or device to shut the valve in case of flooding mentioned in the patents.

    https://patents.google.com/patent/US2494293A/en

    https://patents.google.com/patent/US2709550A/en?oq=US2709550

    I don't think that was ever intended as a float at all.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Ironman
    Ironman Member Posts: 7,546
    Were yours recently purchased? About a year ago a few people saw this but I haven't seen anything about it in some months. Mine seemed like it was thrown or dropped. Supplyhouse sent another one that was fine.
    Yes recently, about 2-3 weeks ago.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    ethicalpaul
  • Ironman
    Ironman Member Posts: 7,546

    Can someone get Gorton to confirm where the vents are being made?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • dko
    dko Member Posts: 668
    edited December 2023
    If you call them and ask, they say it's made right there at Cranford, NJ.

    I'm sure they can be manufactured in mass with very few people with the process down pat and custom tailored machinery. I find it hard to believe they would outright lie about it so I give them the benefit of the doubt.

    I just find it odd a manufacturer with such a long history has zero photos of anyone ever making the valve. No photos of any manufacturing facility, no tours. No addresses stating it is the manufacturing facility. Maybe it's nothing fancy.. but there's literally nothing remotely close. Even on their website, all the photos are just of the old building and inside an office.

    Usually American manufacturers are proud and proudly display it and mark it. They have no qualms showing their processes. I highly doubt air valves would have a secret process that can't be released to the public. I understand it's not required by law to label "Made in USA," but I don't understand why you wouldn't and then make it so you have to go out of your way to find out. All I can think is that while they are made here in USA, they aren't proud of the way they make it. But that's all conjecture and shouldn't go beyond that without evidence.

    American made products need not be stamped "Made in USA." Marking country of origin is only required for anything coming in through customs.

    I also have tested the gorton valve float with water before. It's not written anywhere the float design was to rise with incoming water (it does not), but I did hear many say so.

    ethicalpaulGGross
  • Steamhead
    Steamhead Member Posts: 17,375
    edited December 2023
    dko said:

    If you call them and ask, they say it's made right there at Cranford, NJ.

    I'm sure they can be manufactured in mass with very few people with the process down pat and custom tailored machinery. I find it hard to believe they would outright lie about it so I give them the benefit of the doubt.

    I just find it odd a manufacturer with such a long history has zero photos of anyone ever making the valve. No photos of any manufacturing facility, no tours. No addresses stating it is the manufacturing facility. Maybe it's nothing fancy.. But there's literally nothing remotely close. Even on their website, all the photos are just of the old building and inside an office.

    Usually American manufacturers are proud and proudly display it and mark it. They have no qualms showing their processes. I highly doubt air valves would have a secret process that can't be released to the public. I understand it's not required by law to label "Made in USA," but I don't understand why you wouldn't and then make it so you have to go out of your way to find out. All I can think is that while they are made here in USA, they aren't proud of the way they make it. But that's all conjecture and shouldn't go beyond that without evidence.

    American made products need not be stamped "Made in USA." Marking country of origin is only required for anything coming in through customs.

    I also have tested the gorton valve float with water before. It's not written anywhere the float design was to rise with incoming water, but I did hear many say so.


    That's correct, they are made in Cranford. I visited their headquarters some years ago.

    We've had a couple #2 vents that were stuck like that. From what I understand they were damaged in shipment. Gorton will replace them when asked.

    The green stuff is probably flux from soldering that wasn't cleaned out. Does it interfere with the vents' operation?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Long Beach Ed
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    edited December 2023
    So the "bell" (we can no longer call it a "float") is designed to prevent the displacement of the part from a drop or shock. It doesn't :joy:







    How Gorton ever got a patent when the Jacobus (Maid O Mist) one was clearly the same design first, is beyond me. Patents are flawed for sure.

    https://patents.google.com/patent/US1547652A/en

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Waher
    Waher Member Posts: 286
    edited December 2023

    The green stuff is probably flux from soldering that wasn't cleaned out. Does it interfere with the vents' operation?
    Wouldn't flux like that eventually make its way out of the vent either into the air (bad if toxic or if it clogged the outlet) or drain out with condensate (also not great into the boiler)?

    When I first noticed the green stuff I was fortunate enough to be wearing rubber gloves and washed out the vent thoroughly before using it.
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    I don’t think it’s that toxic…it’s in every copper water pipe

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    JUGHNE
  • ChrisJ
    ChrisJ Member Posts: 16,309
    So the "bell" (we can no longer call it a "float") is designed to prevent the displacement of the part from a drop or shock. It doesn't :joy: How Gorton ever got a patent when the Jacobus (Maid O Mist) one was clearly the same design first, is beyond me. Patents are flawed for sure. https://patents.google.com/patent/US1547652A/en
    Maybe it helps protect it better than if it wasn't there.

    They're made to be installed on radiators in houses not bolted to the fender of a 6x6 going into war.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    SgtMaj
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    They're made to be installed on radiators in houses not bolted to the fender of a 6x6 going into war.


    Oh I know, and this is why I remain confused as to just what kind of punishment they are getting that is making so many of them get jarred out of position!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Member Posts: 17,375
    edited December 2023

    They're made to be installed on radiators in houses not bolted to the fender of a 6x6 going into war.


    Oh I know, and this is why I remain confused as to just what kind of punishment they are getting that is making so many of them get jarred out of position!
    Have you ever watched package handlers? Here's a particularly bad example:

    https://www.youtube.com/watch?v=5YGc4zOqozo
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    ethicalpaulCLamb
  • 109A_5
    109A_5 Member Posts: 1,658

    How Gorton ever got a patent when the Jacobus (Maid O Mist) one was clearly the same design first, is beyond me. Patents are flawed for sure.

    https://patents.google.com/patent/US1547652A/en

    Patents often only last 20 years...

    Jacobus Edward 1923-11-08
    Joseph A Gorton 1946-09-17

    A 'Bell' full of air may lift if the surrounding chamber fills with water, if it can overcome gravity (its own weight) and other mechanical resistance, if any.

    In general I would think a 'Float' would float in any position.


    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Long Beach Ed
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    edited December 2023
    They last 17 years, but just because a patent expires doesn't mean you can make another one for an identical invention (which this is)

    MoM's "float" is solid plastic and doesn't float.

    Gorton's "bell" is copper and weighs more than the water it displaces (watch my shorter video above)

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • BobC
    BobC Member Posts: 5,501
    In 2011 I installed Hoffman 1A's on my system and found some of them worked initially but then stopped venting. When I took the vent odd the offending radiator I found a large drop of water on the vents tongue, the vent seemed fine otherwise with a free floating float. I suspected that drop was blocking the vent which never sees more than 10-12 oz of pressure
    My local neighborhood hardware store, which is still there, stocked MOM so I picked up a couple of #5's and those worked fine. I later found one of Heating Helps membersd had seen the same problem with the Hoffman's. The common thread between our systems were the 10-12 ft horizontal runouts from the short boiler header running arounf the central chmney to yje vertical pipes going up the walls. I suspect 2" pipe was more expensive than 1-1/4 steel pipe so they kept the main just as short as they could, all my horizontal runouts are 12 ft long and don't don't have a lot of slope on them.
    The net net out of all this is I replaced all my Hoffman's with MOM vents in 2012 and have not looked back. They are all still in place and work just fine. I am surprised Gorton never adopted the interchangeable orifice, they obviously copied the vent from Jacobus in the first place.
    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    ethicalpaul
  • Steamhead
    Steamhead Member Posts: 17,375
    The main difference between the Gorton patent and the original Jacobus patent, also the vents we see here, is the way the free end of the bimetal strip is terminated.

    Look closely at the diagram on the Gorton patent. The end of the strip rests against the casing of the vent, thereby keeping the strip from bouncing downward and allowing the float pin to disengage. But the end of the strip in the vents shown is just hanging there.

    This is a production problem. I'll call Gorton next week and make them aware of it.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Long Beach Ed
  • dko
    dko Member Posts: 668
    edited December 2023
    Steamhead said:


    Look closely at the diagram on the Gorton patent. The end of the strip rests against the casing of the vent, thereby keeping the strip from bouncing downward and allowing the float pin to disengage. But the end of the strip in the vents shown is just hanging there.

    They had one filed in 1946 and then another in 1951 linked above
    https://patents.google.com/patent/US2709550A/en?oq=US2709550

    In their later filing, the end of the strip doesn't rest on anything and the excerpt about protection against shock/blows removed.
  • 109A_5
    109A_5 Member Posts: 1,658
    So change the bimetal strip a bit back and forth over the years and get a new patent.

    Nice job @ethicalpaul, the Diving Bell sinks, who would have thought. Mythbusters would be proud.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    Thanks @109A_5, but to be fair to Gorton, it does seem like they never claim it is a float--but people seem to call it that and do their work for them :smiley:

    oops I take it back, they do call it a float:




    They also call their strip "non-corrosive" even though the new one I opened up was already corroded :sweat_smile:

    I still think they make a good product, no disrespect, Mr. Gorton!


    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Member Posts: 17,375

    Thanks @109A_5, but to be fair to Gorton, it does seem like they never claim it is a float--but people seem to call it that and do their work for them :smiley:

    oops I take it back, they do call it a float:




    They also call their strip "non-corrosive" even though the new one I opened up was already corroded :sweat_smile:

    I still think they make a good product, no disrespect, Mr. Gorton!


    This illustration shows a tab on the end of the bimetal strip that bottoms on the housing. Same basic thing.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    edited December 2023
    That's not how they ship them today though. No tab. Corrosion included free :joy:


    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dko
    dko Member Posts: 668
    I think i've only seen the bent tab at the end of the strip on the gorton #2.
    ethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 16,309
    edited December 2023
    I really don't like being told something that will corrode, won't.   And that it has a float to do a job it can't.


    I also don't like vacuum cleaner companies telling me a fractional hp motor is 6 hp. 


    Do I really care that it doesn't really have a usable float?  No, not even a little bit. But that's not the point.

    To be fair though, I wouldn't be entirely surprised if no one at MOM or Gorton know the floats don't work.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaulCanuckerGGross
  • Waher
    Waher Member Posts: 286
    edited December 2023
    BobC said:

    I am surprised Gorton never adopted the interchangeable orifice, they obviously copied the vent from Jacobus in the first place.
    Bob

    https://www.maidmist.com/spec-sheets/jacobus-adjustable.pdf
    Maid O'Mist recently came out with a knob adjustable orifice (similar idea to the Vent-Rite #11 or Hoffman 1A, but with a much wider adjustment range) as an alternative to their existing line of interchangeable orifices.


  • 109A_5
    109A_5 Member Posts: 1,658
    edited December 2023
    Hello @ethicalpaul,
    Looking at the 'Bell' in yours and then the one in the advertisement picture and imagining the possible size of it in a Gorton #2 maybe some would float and over time the 'Bell' got smaller (production costs or a young engineer that did not perform the due diligence) and it lost the float feature in some cases.

    I wonder if the other brands that have the sealed chamber that expands with alcohol inside float or if they are also too heavy. I know the all metal float in my M&M 67 floats enough to do that job, but it is much bigger than a radiator vent valve.

    "They also call their strip "non-corrosive" even though the new one I opened up was already corroded"
    I wonder if that means the strip won't corrode other parts of the system. Not that it is not subject to corrosion its self.

    If the corrosion issue seen is from flux residue they should have a production method to flush it out, but maybe that went by the wayside for production cost reasons.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    109A_5 said:

    I wonder if that means the strip won't corrode other parts of the system. Not that it is not subject to corrosion its self.

    So the bimetallic strip is a sacrificial anode for the rest of the system? :sweat_smile:

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    JoeKansas
  • 109A_5
    109A_5 Member Posts: 1,658

    109A_5 said:

    I wonder if that means the strip won't corrode other parts of the system. Not that it is not subject to corrosion its self.

    So the bimetallic strip is a sacrificial anode for the rest of the system? :sweat_smile:
    That would be interesting.
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • reggi
    reggi Member Posts: 523
    Here's some cutaways from bulletins from '33 to '47 +/- ... 
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
    Waher
  • Steamhead
    Steamhead Member Posts: 17,375
    Steamhead said:

    The main difference between the Gorton patent and the original Jacobus patent, also the vents we see here, is the way the free end of the bimetal strip is terminated.

    Look closely at the diagram on the Gorton patent. The end of the strip rests against the casing of the vent, thereby keeping the strip from bouncing downward and allowing the float pin to disengage. But the end of the strip in the vents shown is just hanging there.

    This is a production problem. I'll call Gorton next week and make them aware of it.

    Message delivered. They're on it.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    CLambJoeKansas
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    Well this was a year ago (in my case), and since they produce them, reportedly, in Cranford NJ, surely they already knew what was inside them

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,466
    edited January 6
    Why in some pictures do they have the extra clip inside and some do not?

    Probably made in Cranford, China.
    JoeKansas
  • ethicalpaul
    ethicalpaul Member Posts: 6,653
    These are technical drawings/photos from brochures that are now decades old, who knows what production changes might have occurred over all these years

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,466
    "What's this for? Oh, we don't need that part anymore!
    ethicalpaulWaherJoeKansas