Burnham Oil Burner creating tons of soot
Comments
-
Give the tech some credit. He tried different pump pressures and talked with Beckett or Burnham (maybe both)
and the last line says it all "with either pump pressure burner not operating properly"
He might have spent more time on this I probably would have tried some different things.
Factory settings ain.t the bible. They have been proven wrong many times. But you have to start someplace.
This is what makes combustion difficult and with oil more so than gas, Combustion air temp, fuel temp & pressure, draft and boiler water temp and oil quality all change combustion.
Staring at an analyzer screen doesn't do a dam thing. If it isn't working, you need to change something.
So many techs are locked into the analyzer screen and the mfg. settings that they give up when it doesn't work. In their mind it's supposed to work and does not work so they quit on it.1 -
-
From the Beckett OEM Spec Guide:
Model Burner Nozzle Alt. Nozzle Pressure Air settings Head
MPO115 AFG 0.65 X 45°B 0.65 X 45°B* (H) 150 S-6 / B-0 L2
MPO115 AFG 0.60 X 45°W 0.60 X 45°B 180 S-5 / B-0 L2
Note that they use a smaller nozzle with the higher pressure.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
And a W pattern rather than a BBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Why? Mine runs perfect with a B. I run the factory spec in mine and I actually add more air than true zero smoke + because it was reading 90% and my analyzer was freaking out...lolJamie Hall said:And a W pattern rather than a B
There was an error rendering this rich post.
0 -
I'm curious, Has anyone been able to get this running properly while they are standing there? In other words does it run for a period of time only to act up shortly after the crew has left? Or has it never run properly at any time? This sounds so much like a loose or cracked nozzle adaptor.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
1 -
@Grallert "I'm curious, Has anyone been able to get this running properly while they are standing there? In other words does it run for a period of time only to act up shortly after the crew has left? Or has it never run properly at any time? This sounds so much like a loose or cracked nozzle adaptor.
Yes each time it seems to be running fine and then it starts sooting up. Twice after the crew left and the system shutdown and then this last time while the tech was still here.0 -
I worked with a guy years ago who insisted on really wrenching down on the nozzle when servicing the burner. He would back one wrench and really lean on the other stretching's the threads in the adapter and causing a leak through the threads especially at an elevated pressure. It would show up only after enough oil has dripped into the burner tube and out into the chamber. If the burner tube was cleaned with every attempt to solve the issue it would take a day or so to declare it's self. This is something I've seen a number of time since. What you are describing rings that bell for me. An indicator for me was a nozzle that turned out normally for a few threads and then started to bind or gaul the rest of the way.
Just a thought and something I'd look at.
Good luck.Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
2 -
You can still make soot with the right amount of fuel and air if the burner is not doing it's job which is to mix fuel and air.
No one is going to know until MR Beckett gets their0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 67 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements