The new oil tank should not change the combustion. Best thing you can do is find a competent technician who is familiar with combustion analysis. I wouldn't let anyone who you mentioned in your post anywhere near your boiler. They are clearly incompetent.
Unless the next technician arrives at your door with a digital combustion analyzer don't bother letting him in. The boiler needs to be cleaned and repaired, the draft set to the manufacturers over fire specifications and the burner tuned to a true zero smoke. They should also double check anything the previous idiots touched. This would be fairly simple to resolve for a technician with the correct tools and knowledge.
Where are you located? Which Burnham boiler? It sounds like an MPO3 -
Two comments -- no pricing, please. It's one of our few rules.
The other is that the reason replacement baffles aren't a stock item is that they rarely need replacement -- unless someone has really messed up the combustion. Which seems to be possible in your description, and wouldn't be a warranty item for the boiler manufacturer.
I wonder if you even have the right nozzle in there... or the right pressure setting on the pump.... or .... or. It may take some extensive trouble shooting to get things right again.
One thing, though -- at least you can rest assured that the new oil tank has nothing to do with it, assuming that it was filled with the correct oil for your system (#2 fuel oil).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
Call the owner of the installing contractor and speak with him directly (don't talk with the service manager or anyone else). Tell him you want the boiler cleaned adjusted and fixed to run properly. If it's not fixed promptly tell him you are calling Burnham, the supply house where the boiler was sold and your lawyer.
And no a contractor that installs the tank would not do a combustion test. That is just a lie to get them out of trouble.
Then post the city and state you are located in someone may have a recommendation..2 -
Thank you everyone for posting. I am in Westminster Massachusetts if anyone has recommendations for a tech who can actually fix my boiler. I am still without heat!!
The Boiler is an MPO-115B0 -
MPO can run without baffles, albeit at a slightly reduced efficiency. No need to freezeTo learn more about this professional, click here to visit their ad in Find A Contractor.1
-
Try Charles Garrity -- @Charlie from wmass or Ryan @New England SteamWorks .Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I figured it was an MPO, yes it can run without the baffles. Sometimes I have to remove them to get the over fire draft in the correct range. You can't go wrong with either of the companies recommended above, if they can't accommodate you just make sure whoever does know how to properly use combustion analysis equipment.1
-
Update. Its now Jan 2nd and still no working boiler. US Boiler took 4 weeks to ship the Baffle Kit. Brought in a new company to fix it and they had a hard time removing the old baffles since they had welded in place from the high heat. Was able to exchange two of the four, cleaned the entire unit and smoke stack and reset everything to according to manufacturers specs. Tech called both Burnham and Beckett to double verify the settings were good. Unit is still creating soot. 8 hours of working on it and the tech doesn't know why its still burning incorrectly and creating soot.
My questions:
1. Does anyone know who the residential Burnham Rep and Beckett Rep is for Central Massachusetts?
2. Is it possible this is just a problem child model and has issues
3. Have others run into this problem before?
We are expecting colder weather now so its getting critical. I want the manufacturers to look at the unit before I scrap it and get a new set up.0 -
1-22 until 1-24 is 2 years. Please say it’s been serviced 2 times since install.Combustion analysis #’s will tell a lot.0
-
July 2023 tech was called in but failed to tell me it was full of soot and it hasn't been working this heating season Oct 2023 - Jan 2024
0 -
Point of clarification. You say they set it to spec, but did they use a combustion analyzer to measure the actual combustion numbers, or just set things by a manual?Soot is poor combustion that can be measured with an analyzer then the tech is supposed to make adjustments until the combustion numbers are in line with what is right. It sounds like that isn’t being done.
If they don’t have an analyzer and don’t know how to diagnose they shouldn’t even start working on the equipment.0 -
-
EBEBRATT-ed Thank you so much for this information!! I will contact them tomorrow.
Just checked and Rick Yahoub is with Becket Pumps not Burners......
0 -
KC Jones "You say they set it to spec, but did they use a combustion analyzer to measure the actual combustion numbers, or just set things by a manual?" He first set them to spec and then he used the analyzer and he spoke to Burnham and Beckett and still the soot continued. Thanks for posting. Hopefully we can get the Reps out to look at it.
0 -
Did they do a smoke test in addition to tuning with the analyzer?irishrosepotter said:KC Jones "You say they set it to spec, but did they use a combustion analyzer to measure the actual combustion numbers, or just set things by a manual?" He first set them to spec and then he used the analyzer and he spoke to Burnham and Beckett and still the soot continued. Thanks for posting. Hopefully we can get the Reps out to look at it.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I just went here https://www.usboiler.net/contact.html and posted this
I wonder if enough of the regulars here did the same, If US Boiler might be interested is helping sooner than later.
Or do they even read this stuff
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
3 -
Your problem is neither the burner nor the boiler. It is in setting the draught and the air correctly -- assuming that the oil pressure and the nozzle and burner cone are correct. So -- start off by finding a tech. with the right test equipment and the knowledge to use it. Then have him or her go through the whole show -- correct nozzle, correct setting in the burner, correct oil pressure, set the air and draught to get low smoke. May take some time...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I’d really start over with all the settings and parameters, especially insertion depth, z dimension, and overfire draft. 1/4” on the z is the difference between clean and soot city.
I have a first gen MPO. Set up perfectly it hasn’t been cleaned in 4 years, and doesn’t need it.There was an error rendering this rich post.
3 -
We know some of the good manufacturers monitor this site. Others may not care.
@irishrosepotter
Did the original installer take out a permit for the oil installation as required with the local fire dept.???
There are several reasons for asking one of them is because they have to submit a written copy of the Combustion test to the Fire dept and that the job has been tested and is complete to run.
RW Beckett phone # is 866-232-5388 says for contractors and technicians only. Homeowners are supposed to call there local heating professional.
Certainly, possible that the original installer did not do something right either in the installation or the set up and either did not do a combustion test or faked one.
It is also possible (but not likely) that the mfg. stuck the wrong burner on the boiler or that some burner part is wrong or missing.
Either way a decent installer would have caught that.
0 -
EdTheHeaterMan - Wow thank you so much for posting that to them! I appreciate the support.
0 -
"MikeAmann">Did you check the chimney for blockage? Yes I had the chimney professionally cleaned back in November when this all started. The flue to the chimney has also been cleaned. No blockage...
0 -
EBEBRATT-Ed
"Did the original installer take out a permit for the oil installation as required with the local fire dept.??? " yes they did pull a permit and the fire department came out and did a visual inspection. Great idea to get a copy of the original Combustion test. I know the first night it ran tons of black smoke started coming out and I had to shut it down. The installer came out the next say and had to clean all the soot out. Not sure what happened after that but the system ran.0 -
EBEBRATT-Ed
"It is also possible (but not likely) that the mfg. stuck the wrong burner on the boiler or that some burner part is wrong or missing."
Interesting you said this because when the tech was on the phone with the Burnham tech, the Burnham tech said he wouldn't have speced the burner I have with that boiler but then back peddled a bit and said I guess its ok. I am amazed at how much the consumer is at the mercy of these HVAC companies. I unfortunately relied on their recommendation of burners. I did get several quotes from different companies but what did I know about which boilers and burners are better. I am kicking myself for not learning more about them before having this work done. But damn I am retired, single woman who unfortunately didn't get my HVAC license before ordering a new heating system. I am hoping the manufacturers will step in and help cause my head is spinning at this point and New England is supposed to get hit with a major snow storm this weekend.
Thank you all for your input.1 -
An industry educator I respect greatly would say that even if something comes wrong from the factory, supply house or similar place, he would still fault the installer.
Why? Because they didn't check it! (Thanks, @Firedragon !)
@irishrosepotter , you need to get someone in there who can give you much more than excuses.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting5 -
Jamie Hall
"It is in setting the draught and the air correctly -- assuming that the oil pressure and the nozzle and burner cone are correct. So -- start off by finding a tech. with the right test equipment and the knowledge to use it. Then have him or her go through the whole show -- correct nozzle, correct setting in the burner, correct oil pressure, set the air and draught to get low smoke"
The tech today did all this. he cleaned it all, verified and changed the nozzle, corrected the settings, oil pressure was good, new oil tank and oil no gunk in the line, the whole deal several times....just couldn't get it to stop sooting...
0 -
"Steamhead">An industry educator I respect greatly would say that even if something comes wrong from the factory, supply house or similar place, he would still fault the installer.
Why? Because they didn't check it! (Thanks, @Firedragon !)
@irishrosepotter , you need to get someone in there who can give you much more than excuses.
I agree but who is that person???? Thats why I am trying to get the manufacturers involved. This whole thing is making me crazy......lol and yes definitely the installer sucked and should be doing the right thing but isn't so had to move on.
0 -
the Burnham tech said he wouldn't have speced the burner I have with that boiler but then back peddled a bit and said I guess its ok
Sometimes you can catch someone speaking truth before they snap out of it and go back to covering for their possibly-not-so-competent industry brethren. Good luck getting it on paper though.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
On getting the manufacturer involved. May I humbly point out that they build the machines -- but they do not install or maintain them unless they are Tesla cars. They -- and you -- are dependent on competent, careful installers and maintainers. This is true for everything from coffeepots to 787 airplanes.
Even if you were to get a manufacturer really involved -- even the best of them (and there are some really good companies out there), they will still be dependent ultimately on the guy or gal spinning wrenches in your basement.
It is possible that the particular burner/boiler/chimney combination which you have simply won't work. It does happen, but it's rare. In which case, someone should be willing to tell you that, and tell you what you need to do. It won't be free.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
"Jamie Hall">On getting the manufacturer involved. May I humbly point out that they build the machines -- but they do not install or maintain them unless they are Tesla cars. They -- and you -- are dependent on competent, careful installers and maintainers. This is true for everything from coffeepots to 787 airplanes.
Even if you were to get a manufacturer really involved -- even the best of them (and there are some really good companies out there), they will still be dependent ultimately on the guy or gal spinning wrenches in your basement.
It is possible that the particular burner/boiler/chimney combination which you have simply won't work. It does happen, but it's rare. In which case, someone should be willing to tell you that, and tell you what you need to do. It won't be free."
If the coffeepot has a manufacturer's defect no matter who is making the coffee its going to leak all over the counter.
I am not looking to save money I am looking to get heat and answers to why this unit is not working properly. Three HVAC companies have been unable to troubleshoot this. They can't all be incompetent. I have Beckett coming on Monday (I am trying to expedite and have him come in sooner and I am waiting on a date from the Burnham Rep I just spoke to.)
0 -
@irishrosepotter maybe you can get the Beckett rep and Burnham rep to colaborate. You probably only need one of them.
When boiler and burner mfgs pick a burner or several burners to use with a particular boiler usually one of them is responsible for testing. At this point we don't know who that was.
The burner manufacturers want the boiler MGF to pick their burner so they are usually anxious to do the testing.
Burnham and other boiler MFGs may offer a particular boiler with a Beckett, Carlin or Reillo Burners. (they are the most common)
They are all good burners but some installer specialize in using the burners they like.
In my case I wouldn't use a Riello................too many specialized parts but that is JMHO
Whomever shows up from Beckett or Burnham they need to be technicians not salesmen.
It would not be the first time a manufactured package did not work. I have run into this several times.0 -
@EBEBRATT-Ed "@irishrosepotter maybe you can get the Beckett rep and Burnham rep to collaborate. You probably only need one of them."
Yes you are correct. Only the Beckett Rep will be coming over on Monday morning rather than both of them coming over. So I am SOL till Monday at the minimum.
0 -
I think all I am really suggesting is... try "we have a problem, let's see what we can do to fix it" rather than "you screwed up. Fix it".Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
The only thing I can say is that I work on several MPO boilers with AFGs and I don't ever have this problem. It's gotta be something related to poor combustion setup. It shouldn't be too difficult to figure out if you have the right tech on site, but without being there in person I can't do much to assist you from here.0
-
I have had sever instances with 'factory Packages" Both of these were several years ago.
One was an HB Smith series 19 with the exact Power Flame oil burner specified for the boiler. This burner made soot on 1/2 the boiler. So if you split the boiler in half lengthwise the left side was soot and the right side was clean.
The burner was removed from the boiler. The refractory was inspected for impingement. Every part of the burner was checked against the factory specs, blower wheel, choke ring, diffuser, nozzles (different ones tried, pump pressure etc. Everything that could possibly be checked was checked.
I don't remember which nozzle was originally specified it was a bypass nozzle and was either a 60 or 80 degree. We were the installing contractor. At this time we were not the Power Flame rep but had been for the previous 10 years.
Finally in desperation we substituted a 45 degree bypass nozzle and that fixed the problem.
We had 0 help from Power Flame or Smith on this "we have never seen this problem before Yada, Yada"
We spent and ate a tremendous amount of labor on this job.
The second job was an air force base with a Weil McLain/Carlin factory package. We did not install this and were hired to do the start up. We check the burner against the factory specs and everything matched.
No amount of work would make this burn right. Everything was checked and was at factory spec. We called in Carlin who made some changes to the burner that fixed it. It was so long ago I don't recall the problem.
The 3rd job were Power Flame burners installed in Buderus boilers (factory package) in some schools in the Boston area. These were combination gas/oil boilers.
Again, we did not install these we were hired to do the start up. On gas they were fine. On oil high fire was ok but low fire was disgusting. Oil fire was so awful that I disconnected the oil solenoid valves so they could not run oil. I talked with the burner mfg and asked "who did the testing" on this package and got some evasive answers.
We decided to leave oil disconnected and to just let the problem smolder to smoke out whose problem it was as it sure was not ours.
After 6 months we were told it was decided to remove the baffles in the boiler 'too much back pressure" and to reconnect the oil and try it. Apparently that was the fix. I never saw the job.
Ok so the point is I don't trust the MFGs to do the proper testing before they send the equipment into the field. If you do blindly accept what they tell you they will lead you astray.
The above are commercial jobs. Maybe they are more diligent with residential equipment.
Take even a residential boiler that is made in say 3,4,5 and 6 sections
Now test that boiler with a Beckett, Carlin and Riello burners. 4 different boilers with 3 different burners is 12 different boilers to test.
Do you think the MFGs are really doing this?
Do you really think they are doing this on commercial jobs when they have more than 4 sections and more than 3 different burners plus testing with gas burners, natural gas and propane with straight gas burner and combination gas/oil burners.
They combinations are almost endless and I know this testing does not always get done. Most who have done residential work will probably not believe this and that is fine. But my experience has proven otherwise.
The point is the installer may have done a bad job; he may not have set the burner up properly. There may be a job site condition like a chimney problem or an oil issue or a combustion air problem.
But factory problems (though rare) are not nonexistent and do exist.6 -
-
@captainco Do you ever notice that when people say the combustion numbers look good they never list them. Draft. smoke, CO(lightoff, Run, Shutdown), O2, Flue Temp
These are the numbers off the workorder.....
replaced spinon oil filter and . 65/45W nozzle
-adjusted pump pressure from 180psi to 150psi according to Beckett technical support but Burnham technical support has the pump pressure at 180psi
-adjusted air settings to Beckett OEM specifications
-draft in stack -.05
-with either pump pressure, burner is not operating properly
0 -
And none of that is the numbers from the combustion analyzer. The analyzer would show the improper combustion to the tech, and then they make burner adjustments based on what the combustion analyzer is showing. The factory settings are just a starting point, and unless the world is perfect, many times won't result in proper combustion.irishrosepotter said:@captainco Do you ever notice that when people say the combustion numbers look good they never list them. Draft. smoke, CO(lightoff, Run, Shutdown), O2, Flue Temp
These are the numbers off the workorder.....
replaced spinon oil filter and . 65/45W nozzle
-adjusted pump pressure from 180psi to 150psi according to Beckett technical support but Burnham technical support has the pump pressure at 180psi
-adjusted air settings to Beckett OEM specifications
-draft in stack -.05
-with either pump pressure, burner is not operating properly
Do you have the printout from the combustion analyzer? I'm guessing no. If not, all that work order says to me is they did not do their job correctly.
2 -
The key to that list of settings is "adjust air settings to Beckett OEM specifications". That will -- with either pump pressure -- allow the burner to fire. But -- there is no guarantee from Burnham or anyone else -- that that will be the correct setting. Odds are it's way rich. You need the instruments...
On the nozzle and pressure. The nozzle will flow different oil volumes at different pressures (again, you need the instruments to set the air differently for each one). Perhaps more important, you will get slightly different flame patterns. Someone needs to take a good close look (one of the few times when the Mark 1 eyeball is really useful) to make sure that the pattern doesn't have any flame impingement anywhere in the firebox. If it does, you need a different pattern or different pressure -- more likely the former.
And I'm not even an experienced tech. Far from it. Get someone in there who is!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Someone needs to put a combustion analyzer on that equipment and make the adjustment indicated by the results of the smoke test. The Smoke Test should be the first test.@KC_Jones said: The factory settings are just a starting point, and unless the world is perfect, many times won't result in proper combustion.@Jamie Hall said: The key to that list of settings is "adjust air settings to Beckett OEM specifications". That will -- with either pump pressure -- allow the burner to fire. But -- there is no guarantee from Burnham or anyone else -- that that will be the correct setting.
Both are basically saying the same thing. The factory settings are not the final word.
On page 42 of the US Boiler I/O manual that the installer must follow is a Section 8 paragraph E that reads as follows:
E. ADJUST OIL BURNER WHILE OPERATING. (flame present)
1. ADJUST DRAFT REGULATOR for a draft of zero inches (water gauge) in the canopy (see Figure 5-3) after chimney has reached operating temperature and while burner is running. (At least five minutes) See Tables 14-1 thru 14-4 at rear of manual for details.
2. READJUST THE AIR SETTING on burner for a light orange colored flame while the draft in the canopy is zero inches water column ("w.c.). Use a smoke tester and adjust air for minimum smoke (not to exceed #1) with a minimum of excess air. Make final check using suitable instrumentation to obtain a CO2 of 11.5 to 13.0% with draft of zero inches water column ("w.c.) (water gauge) in canopy. These settings will assure a safe and efficient operating condition. If the flame appears stringy instead of a solid fire, try another nozzle of the same type. Flame should be solid and compact. After all adjustments are made recheck for a draft of zero inches water column ("w.c.) in the canopy. Replace plug at completion. See Tables 14-1 thru 14-4 (at rear of this manual) for details regarding the overfire pressure when baffles are both installed and removed.
3. READJUST THE HEAD SETTING. It might be necessary to move the head forward or back one position at a time to optimize the smoke and CO2 readings. Refer to Burner Manufacturer's Manual for details.
4. TURN “OFF” BURNER and remove pressure gauge. Install gauge port/bleeder plug and tighten. Start burner again. WARNING Do not loosen or remove any oil line fittings while burner is operating.
5. FLAME FAILURE The Boiler Control operates the burner automatically. If for unknown reasons the burner ceases to fire and the reset button on the primary control has tripped, the burner has experienced ignition failure. Refer to Oil Primary Control Features, Paragraph J, Step 2 of this Section and Section 13, Trouble Shooting, Paragraph B.
You want to see the report from the testing instruments like the Smoke tester, the CO2 readings and the draft numbers that are mentioned in this part of the instructions manual. Especially the #2 and #3 where it says "READJUST". If no one has completed that, then there is your problem. Get that part done by someone who knows what they are doing, and you may find the answers you need.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements