Fine tuning...........

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,972
    Bravo~ Now it's working the way it's supposed to work!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Mad Dog_2mattmia2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    I was actually astounded..it never budged...dont see that often.  Mad Dog 🐕 
    PeteA
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,989
    Amazing.
  • reggi
    reggi Member Posts: 522
    Did you rip open your jacket and expose your Deadman T-shirt on when the H.O. asked you "Do you raise bodies from The Dead too???" ...No folks , but I learn from the Deadmen.. 
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
    Mad Dog_2PC7060
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    That's Good Reggie...I might just do that next time...Mad Dog 🐕 
    reggi
  • dko
    dko Member Posts: 668
    I chuckled at "piggly-Wiggley"
  • mattmia2
    mattmia2 Member Posts: 10,211
    Mad Dog_2 said:

    I was actually astounded..it never budged...dont see that often.  Mad Dog 🐕 

    So they sized it and piped it right, they just ignored the rest of the system.
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    Close...but...look closer...One problem with the header, techinically..Mad Dog 🐕 
  • mattmia2
    mattmia2 Member Posts: 10,211
    Mad Dog_2 said:

    Close...but...look closer...One problem with the header, techinically..Mad Dog 🐕 

    Well you don't actually show the header but i'm guessing it is that 18" piece of pipe instead of a close nipple or street ell connecting the equalizer.
  • mattmia2
    mattmia2 Member Posts: 10,211
    edited November 2023
    And there is no high loop to it.

    EDIT there is a high loop. i was misremembering as i thought about it more. Just the length can hold a horizontal pocket of water to hammer when the steam hits it.
  • mattmia2
    mattmia2 Member Posts: 10,211
    Although i know that is the reason for the close nipple but I don't see how the air can get out of that section if the bottom of both sections are below the water line, I don't see how the air can get out for the steam to get in.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    Oops forgot those...there i go...Mad Dog 🐕 ...
    mattmia2reggioffdutytech
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    It's a really nice beefy, used both 3" Tappings, Header....but...Mad Dog 🐕 
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 10,211
    the risers from the boiler have to both be before the risers to the main
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    edited November 2023

    Voila!!!! Yes, as per manufacturers specs. That being said, with such a generous beefy full 3" Double Header, I don't think its really ever a big issue, because I've seen thousands just like it done by really good

    Old timer Steam Men. They do it like this for the obvious reason: Everything looks nice, neat & Sqaured Away, and you don't have to do monkey shines & acrobatics to line everything up.  


    I know several EXCELLENT heating men

     Charlie A (RIP), Vince, 3 Jimmys, John & Jimmy's, (Retired) Tony B (RIP) who did cookie 🍪 cutter, assembly line boilers. Everyone looks identical.  They Did a boiler a day for 40 -50 yrs...they yell out every nipple...4 1/2" !!!! They know how to knock out a boiler & be done by 430p.m..


    I'm too artistic, eccentric and out-Of-the-box thinker. I have typical things I Always do, but no two Steam boilers look the same. Unless, the houses are all in the same development & done by the same Deadmen, there are too many different factors to contend with. My Hot water boilers are all very similar. Mad Dog 🐕 

  • ethicalpaul
    ethicalpaul Member Posts: 5,938
    The old steam men built thousands of headers that way, purposely against manufacturers’ instructions  and against obvious good practice because it looks neat and that’s OK? 

    That’s a strange position to take.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    I couldn't tell you WHEN that became written in stone by the Manufacturers?  Why Doncha research that for us!  Moreover, people aren't made of money, Eithical Paul. Most clients have limits on what they have or will spend.  I have to focus on what's REALLY going to make a difference & fix the the problem for a minimum of dollars 💵. 

    The boiler is already in 5 years, warranty on the block is water under the bridge 🌉.  If I repiped it, it would make a very miniscule difference...ask me how 🤔 I know these things....I don't recall saying this is "ok", preferred, equivalent, or swell.  I said, its already done, many otherwise-really good Heating men did them this way for years because it saved them time and fittings.  The guy used both 3" Tappings, Swing joints, good height..its DONE NOW. 

    I have never personally piped one like that, even in my Green days, because I always read the instruction because I was afraid of ruining a $3 or $ 4 K hunk of equipment.  I did my first steamer in 1985.  Before then, couldn't tell ya WHAT the manuals said. (You'll get back to us on that, E.P....). When I did point this out to Charlie A, he said he NEVER heard that before.  He checked with a Bookish, Steam 🤓 nerd he knew and came back in the next day and admitted it.  He had been doing them that way since 1970..never an issue he said and I take him on his word!  He only lived another 3 years, but he never piped them that way again!  Good man..5 foot 5 145 lbs of Heating Dynamite! 

    Am I mistaken or aren't you one of the fellas that insists the Eqaulizer doesn't really serve a function? The Deadmen really didn't have a handle of The Steam??? Mad Dog 🐕 


  • ethicalpaul
    ethicalpaul Member Posts: 5,938
    edited November 2023
    I didn't say or mean that you should have ripped it out.

    I was confused because you seemed to say it was OK because you said you've "seen thousands just like it done by really good Old timer Steam Men". Just trying to understand when someone is a "hack" and when someone is a really good old timer steam man. It seems that sometimes bad installation practice is frowned upon and sometimes it's excused, depending on a variety of factors that is hard to pin down.

    What I said about the equalizer is that it does not keep water in the boiler or prevent water from rising in the A dimension during boiler operation, as has been seemingly common belief. I backed this up with observable, repeatable experimentation and welcomed anyone to show otherwise. I was berated by some people, believed by some people, and as far as I have seen, never disputed by fact or observation. But that is totally separate from this topic, and as far as I can tell, you bring it up here as a personal attack, to muddy the waters.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,989
    @ethicalpaul

    It's not that it is ok to pipe it wrong. But boiler that have been piped "wrong" have worked very well for years. WHY?

    In my opinion:

    1. A lot of boilers were way oversized (we all know this). A boiler can't really produce more steam than the system can condense, as soon as it does the system will shut down on pressure.
    2. Because the oversized boiler has "more sections" the steam separating area of the boiler is large compared to the system it is connected to. This reduces the velocity and turbulence in the boiler so there is probably less carryover of water.
    3. Older boilers were more forgiving, had larger sections and again frequently oversized.
    4. I have seen plenty of really old boiler with a supply out the top and a return in the back with no equalizer and they worked fine.
    5. We see this every so often on the Wall where someone posts a picture and can't tell a gravity hot water boiler from a steamer because the only thing different is the gauge glass. There is no Hartford or equalizer, so it all looks the same

    Most of the steam problems showed up in the 70s and 80s when the MFG started making small boilers. Steam separation now has to be done in the header instead of the boiler where it should be done like the old days the water in my opinion needs to stay in the boiler and has no business in the header where all it does is slosh around and kill steam.


    In the old days when the water stayed in the boiler it could be piped all wrong and would probably work. Not with today's boilers. And not all of todays boiler are designed alike. Some are more difficult to make work like the Uticas with side tappings

    Mad Dog_2ethicalpaulmattmia2offdutytech
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    Now now...no personal attacks here. Relax.  I couldn't disagree with you more about the Eqaulizer, but you have your opinion, we have ours  ✌ ☮ 🕊  Mad 🐕 Dog 
    ethicalpaul
  • ethicalpaul
    ethicalpaul Member Posts: 5,938
    Thanks Mad Dog. I'm sure it's running fine--as long as the water quality is fine and the velocity is OK, I agree there won't be an issue on this boiler. Water doesn't just shoot up the risers without a quality or velocity problem to cause it, as I showed in a couple of my videos.

    My point wasn't about this one boiler, it was more about the thousands that you mentioned and the general thinking. Thanks for caring about your customers and getting their stuff working better!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Mad Dog_2
  • mattmia2
    mattmia2 Member Posts: 10,211
    @EBEBRATT-Ed I suspect it is one step further, that this didn't become the standard practice until boilers got smaller and didn't have space to separate water from steam internally. I do disagree with one thing, I think the larger boiler producing more steam than the system can consume will only make the incorrect piping worse. Maybe if it were all upsized for the bigger boiler it might have more space to separate but people who oversize boilers usually don't follow the minimum pipe size specs.
    Mad Dog_2
  • Steamhead
    Steamhead Member Posts: 17,167
    mattmia2 said:

    @EBEBRATT-Ed I suspect it is one step further, that this didn't become the standard practice until boilers got smaller and didn't have space to separate water from steam internally. I do disagree with one thing, I think the larger boiler producing more steam than the system can consume will only make the incorrect piping worse. Maybe if it were all upsized for the bigger boiler it might have more space to separate but people who oversize boilers usually don't follow the minimum pipe size specs.

    This. Those older boilers had huge steam chests, which took care of separating steam from water. We don't have them now, which is why piping has to be just so to produce dry steam.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2mattmia2CLamb
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,354
    Thanks Paul E! Mad Dog 🐕 
    ethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,989
    Well, none of the old stuff matters now.

    We have to deal with what we have.

    Installation practices range from guys that cheat on the risers and the header and they may get away with it sometimes.

    to the ones that say "I won't do steam without a drop header.

    The truth is probably somewhere in between but you never know for sure. One job does not act like the next even with the same boiler. Too many variables.

    My personal preference is to install the # of risers the mfg wants and make the riser 1 size bigger then the mfg calls for increasing the size right out of the boiler. This helps the water stay in the boiler and out of the header Use the MFG size for the header not a drop header unless height is an issue. And make the boiler risers as long as possible depending on the room you have. Skim it with TSP following Dans method.

    The only time I deviate from that is if it is a public bid job. Then they get whats on the print or the MFG minimum whatever of those two is better. You give the engineer whats on the print he is happy and the other contractors bid accordingly (you hope). If the engineer draws a lesser job than the mfg requires you through that in his face.

    JMHO
    mattmia2Mad Dog_2