Steam pipe return has Leak starting

RTW
RTW Member Posts: 125
I believe its called the dog leg pipe return to boiler. I just sanded some rust and found a hole the size of ones finger tip with soft black goo like substance inside that seeped some moisture. My guess is I can I cover it with epoxy, but what would the experts recommend? The connections are Cast Iron and I'm guessing the pipe itself is Malleable Steel that needs attention. Perhaps it was repaired way long ago. The rest of the pipe looks perfectly fine

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,840
    The goo is sludge from corrosion of the pipe. The real fix is replacing the pipe for a couple reasons, one of which is that sludge can clog the pipe so it really needs flushed out as that can prevent the water return to the boiler.

    Secondly, with that sludge oozing out the chances of any epoxy type repair working are slim to none. It's like trying to epoxy a water leak while the water is flowing, not going to work very well.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    Mad Dog_2
  • ethicalpaul
    ethicalpaul Member Posts: 6,667
    Sounds like the clogged pipe is holding back the water for you. Replace the pipe with steel or copper

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Mad Dog_2
  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    And "goo" can't be counted on to hold for long. There are some self-adhesive silicone tapes made expressly for this type of temporary repair, though, such as this stuff: https://www.amazon.com/Rolls-Self-Fusing-Silicone-Tape/dp/B0CF5568XB/ref=sr_1_4?crid=RPRV3ZR9VEUV&keywords=water+leak+sealing+tape&qid=1699978181&sprefix=leak+sealing,aps,917&sr=8-4&th=1

    It works, but replace the pipe as soon as you reasonably can -- I've never known a leak to get smaller with time...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • RTW
    RTW Member Posts: 125
    OK replacement puipe is the answer - after heating season that may require draining the boiler! I just painted on Rubber Paint over the finger tip size hole for now that's not yet leaking, but moist. In the past, I have used this same rubber paint on the new black pipe return under the water line that I replaced buried underneath the bilco door entrance and 4 feet in length ( another project that was pro-active with no leaks at the time). The brass spigot for the dog leg is just 12 inches away just before it enters the boiler. Ive run it before and nothing sludge like ever came out in recent memory so sludge must be there from long ago. Regards, Bob
  • ethicalpaul
    ethicalpaul Member Posts: 6,667
    I like Jamie's tape way better than a painted-on solution for a temp repair, but good luck regardless!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    @RTW
    A gear clamp or two (hose clamp like a car radiator) and some rubber gasket material will probably buy you some time.
    BobC
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    I call the Goo, "Splooge"Β  picked it up along the way....Splooge..Mad Dog πŸ•Β 
  • ethicalpaul
    ethicalpaul Member Posts: 6,667
    Just don't look it up on Urban Dictionary, MD!

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    Oh no.....Geez..Mad Dog πŸ•Β 
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Mad Dog_2 said:

    Oh no.....Geez..Mad Dog πŸ•Β 

    I've been wondering for a while now why you kept using that word...........

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    ethicalpaulMad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    Oh My Gosh...I had no idea!Β  Disgusting! Sorry 😞 guys..Eewww. Sister Hannah would whack me with the yardstick for this!Β  And, as usual, I deserved it!Β  Ha ha πŸ˜‚ 🀣 πŸ˜†. Mad Dog πŸ•Β 

    ethicalpaulmattmia2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    Here Ye..Hear Ye...I have created a New Word (to replace my unwitting use of THAT other word!)  for the Dark Chocolate 🍫 Thick, purulent Pudding that rests in the wet returns and Mud Legs 🦡 of the boiler....
    "SPLUNCK."Β  Mad Dog πŸ•Β 
  • dabrakeman
    dabrakeman Member Posts: 645
    I had a similar leak in Feb 2013. Used and epoxy wrap (RectorSeal Pipe Repair kit from HD ) and it held until spring when I had the whole 8' section of that horizontal drip leg pipe replaced.
    Mad Dog_2ethicalpaul
  • RTW
    RTW Member Posts: 125
    UPDATE: I wrapped the minor drip leak with silicone tape as advised on the dog leg lower return to boiler and it seems fine. I will monitor it and decide whether replacing it is necessary after the heating season. My guess is some external object in the past must have struck this heavy duty pipe at about floor level that made a hole the size of the tip of ones finger, then patched ( and recently began to drip). The rest of the pipe is fine, as are all other black pipes in system, and I have good well water. Regards, Bob
    Mad Dog_2
  • RTW
    RTW Member Posts: 125
    *mud leg I mean
  • pecmsg
    pecmsg Member Posts: 5,291
    I will monitor it and decide whether replacing it is necessary

    Its necessary.
    Mad Dog_2ethicalpaulbburd
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,518
    What if it let's go when you ain't home???
    Mad Dog πŸ•Β 
    pecmsg
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Mad Dog_2 said:
    What if it let's go when you ain't home???
    Mad Dog πŸ•Β 
    That's a bad day.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Mad Dog_2pecmsg
  • realliveplumber
    realliveplumber Member Posts: 354
    especially if the LWCO isnt working....
    Mad Dog_2pecmsg