I was looking for some input from the group how they handle expansion on long runs of heat-pex tubing. This is for a snowmelt job that has a run approximately just under 100ft of 1 1/4" from the point of exit of the house to a 4 loop manifold. I ran the 1 1/4" heat-pex tubing in a 3' PVC conduit for the total run. Every time the snowmelt goes on the piping in the basement expands approximately 5"-6". I used expansion fittings for my connections. Just concerned over time they may leak because of the movement of back and forth. Spoke with Uponor and they told me not to be concerned, but we all have heard that before.
1
Comments
-
No way to stop that expansion movement. As long as it is not stressing any fittings on either end, let it move. Sometimes an expansion loop is used, but they look funky.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
I remember Uponor used to make a fitting to handle this, but no more. I am just concerned with Uponor expansion fittings putting stress on them.1
-
-
-
Dumb question: when you "lock it solid like in concrete" what happens to the expansion then?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
You wind up with a lot of compressive stress in the pipe -- which shouldn't be a problem -- which shows up as a very slight increase in wall thickness -- which also shouldn't be a problem.ethicalpaul said:Dumb question: when you "lock it solid like in concrete" what happens to the expansion then?
Now if there is a short section somewhere which isn't restrained... if the pipe decides to slide, which could happen, it will buckle and ruin your whole day.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
At the PPI website they show how to calculate an expansion arm. This may be cleaner than a U shape expansion loop?
Enter the tube size, length and temperature change and it shows how to build the armBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
Ironman said:This is one reason that we use PEX-AL-PEX when provision for expansion is not available. It only grows about 1” per 100’ @ 100* temperature rise. Very similar to copper. With PEX, it’s about 12 times that.
and fittings?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Next time I will use fusion plastic pipe. That’s what we used inside. Nupi is the manufacturer.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements