Best single pipe steam unit for tiny space?

Options
We're gut renovating an 8'x5' bathroom in 1930s home...old layout had a small (approx. 10"Lx19"Hx4.5"W) single pipe steam cast iron radiator immediately next to the toilet. We had a cover on it since it was so close to our legs. We want to stick with steam but we're hoping to find a better solution for the layout. Should we consider a recessed unit, a wall mounted steam unit (Castrads has one?), a wall mounted Runtal steel steam unit, or is there something else we should consider? We could also partially recess the existing unit which would give us a few more inches of space. Thank you in advance for any suggestions!

Comments

  • Steamhead
    Steamhead Member Posts: 16,937
    Options
    Can you post a picture of the existing radiator?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • kateye
    kateye Member Posts: 6
    Options
    This is the radiator...



    And this is the bathroom before demo...we hope to eliminate the bump out in the corner by replacing the cast iron stack with PVC and push the toilet to be flush against the back wall (it was about 4" away from the wall before demo).

    We found that we have 3 AC ducts in the left wall so that may limit our options since we don't want to re-route them.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,192
    Options
    Steamview Radiators make a nice wall-mounted steam Radiator. Of course, you'll be installing new insulation .  You'll be able to put a much smaller Radiator in if you do.  Mad Dog 🐕 
  • kateye
    kateye Member Posts: 6
    Options
    That is a good point! Would Runtal/Steamview be able to tell me the BTU/radiator size needed for my room?
  • mattmia2
    mattmia2 Member Posts: 9,835
    Options
    You need to do a heat loss calculation but you also need to balance it with the rest of the system at least roughly. If all the other emitters are significantly oversized and you size this to just the loss of the room the boiler will shut off because of the other spaces heating before this space heats. You can balance some with vents but it is a lot easier if it is basically balanced to begin with.
  • kateye
    kateye Member Posts: 6
    Options
    So if we replace, would it be recommended to replace with a unit with roughly the same BTUs as the existing radiator in order to keep the system balanced (even if oversized for the space)? We have already removed two radiators from the original system (one from main bedroom where we had two radiators, since it was too hot) and one from a sun room that we renovated (and where we unfortunately installed hot water baseboard.). I am not sure if that makes a difference in the balance of the system!
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,732
    Options
    Gerry Gils solution with the vertical pipe radiator would be ideal for this. It's pictured somewhere on this site.
    mattmia2
  • kateye
    kateye Member Posts: 6
    Options

    Gerry Gils solution with the vertical pipe radiator would be ideal for this. It's pictured somewhere on this site.

    I think this is it...
    https://forum.heatinghelp.com/discussion/151994/new-steam-mini-tube-installation-in-ohio/p1
    It would definitely save us space but I'm not sure who could make this for me!
  • kateye
    kateye Member Posts: 6
    Options
    We are leaning towards buying a new but slimmer 2 column cast iron radiator that will give us a little more room next to the toilet. How do I determine the BTUs of existing radiator so I can choose an appropriately size replacement? Thank you again!
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,192
    Options
    As Mattmia..said above...do a Simple heatloss for the room and then size your radiator accordingly...otherwise you're just guessing...Mad Dog 🐕 
  • pecmsg
    pecmsg Member Posts: 4,909
    edited September 2023
    Options
    With 3 interior walls and 1 exterior, that room doesn’t need much at all. 
  • Steamhead
    Steamhead Member Posts: 16,937
    Options
    The vent on that radiator is in the wrong place, so it's not heating to its full capacity. If it was heating the room properly, you could use a slightly smaller rad and put the vent in the proper location, with no loss of performance.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2