Replacing Badly Rusted Tankless Coil on Weil Mclain EG-45 - NSFW
Comments
-
If properly sized, I would recommend a new EG-45, with tankless coil for hwbb heat.
Unless you have a lot of free time, I would suggest cutting your losses and replace the boiler. Hate to see you spend more time, only to learn you cannot get the plate to stop leaking. Worse yet, one of the sections cracks.0 -
STEAM DOCTOR said:If the baseboard is all in the basement, and the piping is all below the water line, then there is no reason in the world to use a coil.ScottSecor said:If properly sized, I would recommend a new EG-45, with tankless coil for hwbb heat. Unless you have a lot of free time, I would suggest cutting your losses and replace the boiler. Hate to see you spend more time, only to learn you cannot get the plate to stop leaking. Worse yet, one of the sections cracks.
If I ditch the baseboard in the basement do you still recommend the EG-45? Im weary of the same failure happening with the tankless coil.
Thanks everyone!
0 -
If it is hot water you size it based on the heat loss of the house, not the amount of radiation (assuming the heat loss is <= the radiation)0
-
Or is this steam with a hot water loop?0
-
Hey there @hadeone
You are so deep into it now just go ahead and see it through. Clean the face where the gasket will be and be sure to drill and tap all of those pesky bolts. Use a center punch to start then a small drill bit then move up to the final size needed. Have some extra drill bits ready for when the first few brake. Just go for it.
Give us a look with some pictures of your successful repair when you are all done.1 -
I would stay away from the coil. They really are the weak point on an otherwise Grade A boiler. At only a few feet of elevation, very easy to keep water in the loop, without a coil. Using what we call the fishie method (Dan has a chapter on this in one of his books and I thing there are articles about this somewhere on this site).1
-
-
-
STEAM DOCTOR said:The Weil Mclains come with or without the coil option. And of course if you're going without the coil option, there are other options besides for the WM.0
-
https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/
Not a bad way to go with your situation, single small zone in basement.
Ironically we've had good luck with using tankless coils for heating on Weil McLain EG steam boilers. We've used them with indirect dhw tanks, radiant heat and hwbb loops with few problems. I always considered the "clean" water of the tankless coil a huge advantage. Pumps seem to last a long time, as do the other components as it is a closed system.1 -
ScottSecor said:https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/ Not a bad way to go with your situation, single small zone in basement. Ironically we've had good luck with using tankless coils for heating on Weil McLain EG steam boilers. We've used them with indirect dhw tanks, radiant heat and hwbb loops with few problems. I always considered the "clean" water of the tankless coil a huge advantage. Pumps seem to last a long time, as do the other components as it is a closed system.0
-
I have also used the coils for such applications. Many times. But my personal opinion is to avoid when possible.0
-
I am now boiler shopping and did a EDR calculation. I’m calculating 280 SF of radiation using the tables for Aero convector radiators and it turns out the EG45 installed was somewhat oversized (388 sf capacity). It seems like a new EG40 would work (321 sf). I understand it’s the same boiler as the EG45 but with 5 burners instead of 6.A local plumber is proposing a Crown replacement because they have tappings high on the sections which can be used for the baseboard zone. That would keep the zone water cleaner than lower tappings. Does this make sense? Using the boiler water directly seems like it will have the same effect on the zone pumps regardless of tapping. They are against WM because of the rubber seals.
Thanks for reading. Any more insight is appreciated.0 -
-
-
STEAM DOCTOR said:Peerless also offers tappings a bit higher up. Perfect for your application.Ideally I’ll avoid the coil but if the alternative will create other issues before a new coil does than is it worth it?
Just thinking out loud. Thanks for reading.0 -
-
I think that you are overthinking this. There are many thousands of people who feed their basement baseboard systems, with boiler tappings using regular boiler water. Worst case scenario, you will need to replace your circulator every once in awhile. Not a big deal. On the other hand, if you ever need to replace your coil, it can be a very big deal.1
-
STEAM DOCTOR said:I think that you are overthinking this. There are many thousands of people who feed their basement baseboard systems, with boiler tappings using regular boiler water. Worst case scenario, you will need to replace your circulator every once in awhile. Not a big deal. On the other hand, if you ever need to replace your coil, it can be a very big deal.0
-
-
@hadeone
The problem with the coil is not the coil itself but the gasket and the mounting bolts.
The original installer should have removed the bolts and put never seize on the threads and then retorqued the bolts. Then they should be checked every year or two retorqued the bolts.
The problem is no one ever does this and then you start to get leaks around the gasket.
If the leak is attended to promptly it's a non-issue remove the coil new gasket retorque and clean up and your fine.
When it gets neglected it turns into a mess.4 -
-
-
Should have used antiseize and stainless or brass bolts or studs and nuts.realliveplumber said:The original installer should have removed the bolts and put never seize on the threads and then retorqued the bolts.
The manufacturer should have put never seize on the threads3 -
The biggest issue with stainless steel bolts is No Stretching. All they do is snap.Grade 8 bolts with never seize.0
-
In my case, the Peerless ports work great for my hot water loop. I keep my ph at 11 to minimize corrosion and feed my boiler water through a screen filter, into a bypass loop, and into regular cheap grundfos iron circulator. The water is very clean and all is well after 3 years. SS circulators are quite expensive so I rolled the dice.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
Just as closure to this thread and some more data, I found a 2016 manufacturing date on the section of the old boiler. 7 years old…0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements