240 Plug Variations Dryer outlet/ MIG welder Question

electronictofu
electronictofu Member Posts: 18
edited July 2023 in THE MAIN WALL
Hi all,

I am looking at a MIG welder from Harbor Freight, they cut off the demo unit cable, but its 240 for sure, and looks like 3 wire, meaning 3 prong? I have a dryer outlet Id like to use but it's 4 prong (4-wire red,black,white,ground). Can I cut the cord on this welder and wire on the plug that will fit this outlet or is that bad news bears?

Heres the welder:
https://www.harborfreight.com/170-amp-dc-240v-migflux-cored-welder-57865.html

Image of welder cable demo unit cut



And image of my dryer outlet (Id rather buy a 110 Lincoln that wire another outlet right now) but these Harbor Freights are pretty nice for the price!

Thanks in advance pros and DIY'ers.
-Phil

Comments

  • mattmia2
    mattmia2 Member Posts: 10,655
    Probably should be protected at 20a instead of 30a but putting a plug on a 240 v appliance to connect it to a 120/240v receptacle isn't a problem, just don't connect the neutral at the plug.
    Larry Weingarten
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,434
    Oh man...We may very well have some electrical experts here, but I'd say you really want a very experienced Licensed Master electrician or Electrical Engineer to give you the Skinny.  I once installed (8)  WM 88 Series oil HW boilers in a Large Housing project. I wire my own boilers, but these were subbed out to an Electrical contractor.  I forget exactly what they did wrong, but something just didn't look Kosher to me.  I think it was wired 220 but only needed 110.  I gently questioned the Electrician who told me to stick to the piping & assembly of the boilers.  Ok......

    Time to fire them up...It ran for about 30 seconds until it smoked the motor and transformer.  Cooked!  The same guy wired all of them.   He INSISTED he knew what he was doing.  After the 3rd one smoked,  he admitted defeat..Ha ha 😂 🤣 😆 😄. 

    Moral of the story....Wiring is no hobby or DIY project, especially 220....Be careful.  Mad Dog 🐕 
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,062
    It appears that you have an existing outlet for a 240 V 30 Amp appliance

    The welder looks like it should be on a 20 amp circuit.

    All this means is that you have enough electric to power the welder, and the welder should be protected with a 20 amp circuit protection.

    I would remove the outlet and select another outlet with a 20 Amp rating, change the circuit breaker that supplies that outlet from 30 Amp to 20 Amp

    Add the matching plug to the welder and you should be good to go.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Member Posts: 1,414

    Looks like this receptacle has some issues !!!


    Mad Dog_2 said:

    He INSISTED he knew what he was doing.

    @Mad Dog_2 He did, he just did not know what he 'should' have been doing.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    EdTheHeaterManMad Dog_2CLamb
  • hot_rod
    hot_rod Member Posts: 22,997
    Many of those small homeowners welders can be used with 120 or 240
    My 210 EASAB came with a short adapter cord to plug into 120V. But welding is limited to 1/2 amperage

    It makes it very portable. The machine will show the circuit requirements on the label

    Why the cut cord?


    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,222
    The welder is a 3 wire (2 hot wires and a ground). Your dryer is a 4 wire (2 hot wires , 1 ground wire , and 1 neutral wire.

    You could put a 4 wire plug on the welder to match your outlet (just don't connect the neutral)

    BUT not code compliant

    Do this at your own risk. As others have mentioned your welder looks like it should be protected at 20 amp.

    Why not just put in the correct circuit?
  • WMno57
    WMno57 Member Posts: 1,408
    Circuit breakers in panels are ONLY to protect the wiring in the home/structure. If anything downstream from the outlet needs protection, it is on the appliance manufacturer to provide a fuse in the appliance.
    mattmia2HomerJSmithethicalpaul
  • pecmsg
    pecmsg Member Posts: 5,215
    WMno57 said:
    Circuit breakers in panels are ONLY to protect the wiring in the home/structure. If anything downstream from the outlet needs protection, it is on the appliance manufacturer to provide a fuse in the appliance.
    Not true. 
    The manufactures decide what amperage is needed to safely operate the equipment 15, 20, 30, 40. The electrician then runs the appropriate wire size. 
    ChrisJ
  • hot_rod
    hot_rod Member Posts: 22,997
    If it is a 200A  machine it may need  a 50A 240V circuit and plug/ receptacle

    Here is what a dual voltage setup looks like
    I found the 3 prong 50A  receptacle at the depot 
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • realliveplumber
    realliveplumber Member Posts: 354
    So if you have an electric drill (remember those) or a fan, or whatever, and it is stamped 2 amps on the unit, you can still plug those into a 15 or 20 amp receptacle.
    WMno57
  • 109A_5
    109A_5 Member Posts: 1,414
    hot_rod said:

    Why the cut cord?

    Corporate policy ? Maybe the unit was a defective return, and then became a display model. Years ago folks would cut the cord on defective equipment, so the dummies that ignored the defective tag could not get hurt. However it made more work for the repair guy. Safety First.

    Security, the thieves may not want to replace the cord.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • HomerJSmith
    HomerJSmith Member Posts: 2,583
    edited July 2023
    The name plate rating determines the size of the wire powering the appliance. As I recall, vaguely, the current carrying capacity of the wire is rated 25% less than the wire is capable of carrying. The purpose of the breaker is to cut power to the wire in the case of a ground fault condition which could raise the current above what the wire is capable of carrying which would cause the wire to heat up and possibly melt and start a fire. You can always use a larger wire, but never a smaller wire than the rating of the breaker for that reason. The grounding conductor is there to trip the breaker in a ground fault condition in a situation where the metal frame might become energized.

    You can never use a 70 amp breaker on a 20 amp wire, because the wire isn't protected. Yes, WMno57, the breaker is there to protect the wire against an over current condition.
  • HomerJSmith
    HomerJSmith Member Posts: 2,583
    Even tho the name plate current rating says 20 amps, the manual should tell you the circuit size for that appliance.
  • jumper
    jumper Member Posts: 2,384
    Also make certain that device is for 240; not 215 or something.
    mattmia2
  • hot_rod
    hot_rod Member Posts: 22,997
    Looks like the spec sheet shows 240V 20A power.

    So a basic plug like this, plus receptacle.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • electronictofu
    electronictofu Member Posts: 18
    Dang! This board is on fire, you all rock. Well, the Harbor Freight welder is brand new and only $229, and a used Lincoln which is what Ive owned 3 of at 110v runs a little more pricey. But If I had to ad an outlet and do more mods than just a cable cut I guess Im betting off waiting to find a good MIG that'll fit a standard wall plug. Just hesitant buying used welders and they are pricy for more commonly known brands like Lincoln. I think it's smart to avoid any risks and wait after reading all the comments, although it'd probably be ok, but as said not ideal nor to code.
  • hot_rod
    hot_rod Member Posts: 22,997
    There are limits in what you can do with a 120v MiG. Welding power and  duty cycle will take a hit, If either are important for the welding you do

    I recently bought a spool gun to weld some 1/8 aluminum, it would not weld with the 120V input

    Lucky the ESAB Rebel has a switch to allow 240V input by switching to a 240V circuit also. This allows you to weld on the highest settings

    120v makes it very portable, with flux core wire you can go anywhere. I took it to a neighbors to weld a broken motorized hospital bed that her husband uses. Welded it right in the bedroom from a standard outlet

    The transformers in side of basic MIGs have shrunk and weight is a fraction of the 120 Hobart Handler  I  bought 30 years ago, that recently died


    The ESAB Rebel EM 210 can be found online for under a $1000, but much more $$ than the Harbor Freight and other bargain brands

    Bob "hot rod" Rohr