Our local supplier used to push them every time we purchased a Weil McLain or Union Steam all the time. Never actually installed one but have seen a few. In my opinion, pipe the boilers correctly and there is no need for a separator.6 -
I've cut a few out Sears and 'Monkey-Wards" made some thing similar. As Scott said..unnecessary. mad Dog
0 -
-
I'm sure, but wouldn't a good full port drop header do the same, Dr Holohan? (Professor Emeritus of The Steam and all Hydronics). If I cut it out, its at Suffolk County Community College Heating Museum where all my Larger relics have their final resting place. I know Prof. Eugene runs things out in California. Who in charge there now Dan? I have a few "new" older items I WILL NEVER junk... Mad Dog1
-
It does what a drop-header does, Matt, and at less expense. These devices are from the '80s and they helped when the steam boilers were really hot-water boilers, trimmed for steam usage. The steam velocity of those boilers was much too high and the separator slowed the steam significantly. They were more popular in New England than in NY.
I don't have any contacts at Suffolk Community College. I saw Eugene at AHR. He's looking good.Retired and loving it.1 -
I believe I saw these in Dan's book, TLAOSH0
-
YesRetired and loving it.0
-
Dano. I'm going to reach out to Suffolk CC and pay a visit to review what they have on display and reestablish a connection with them and see if they want more artifacts mad Dog0
-
Nice! Thanks.Retired and loving it.0
-
Thanks for the feed back guys. I knew I would get the answer on this site! I sent a photo to a few of my suppliers, but no one could tell me what it was. Thank you Mr. Dan Holohan for your class, books and articles which have helped our little outfit do steam better.0
-
I'm glad I was able to help. Thanks!Retired and loving it.0
-
Since the carry over happens in the boiler where it gets pulled into the narrow tapping, that would mean that water is entering the device.DanHolohan said:They do work. It contains a dip tube for the steam. The wide space in the road seriously slows the steam velocity as it leaves the boiler. There’s little carryover.
Where does this water drain back out from the device?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The globe is hollow, except for a dip tube that extends about halfway in from the top. The carryover water falls right back into the boiler as the steam enters the dip tube and heads up into the system. It's very simple. Devices such as this one have been around for more than 100 years. They reappeared during the '80s because the steam boilers of that time were really hot-water boilers, trimmed for steam.Retired and loving it.0
-
I wish someone had a patent drawing or something.DanHolohan said:The globe is hollow, except for a dip tube that extends about halfway in from the top. The carryover water falls right back into the boiler as the steam enters the dip tube and heads up into the system. It's very simple. Devices such as this one have been around for more than 100 years. They reappeared during the '80s because the steam boilers of that time were really hot-water boilers, trimmed for steam.
I'm having a hard time picturing it.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Similar to this: https://www.tfi-everhot.com/anti-surge-steam-separator.htmlRetired and loving it.0
-
-
Thanks, Scott.Retired and loving it.0
-
I didn't even notice it among all of the other posts, I'm sorry Scott.ScottSecor said:@ChrisJ did you click on the link I provided above?
That's exactly what I needed to see.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Steam drums and separators are a good idea. I believe some systems used flash tanks & separators in returns as well.DanHolohan said:It does what a drop-header does, Matt, and at less expense. These devices are from the '80s and they helped when the steam boilers were really hot-water boilers, trimmed for steam usage. The steam velocity of those boilers was much too high and the separator slowed the steam significantly. They were more popular in New England than in NY.
I don't have any contacts at Suffolk Community College. I saw Eugene at AHR. He's looking good.0 -
-
It's cheaper than a drop header, but it returns carryover to the boiler via the riser where it can interfere with the release of steam at the surface instead of sending it through the equalizer where it enters the boiler below the water line. Not sure if the reduction in efficiency would be significant, but there would be some.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
-
As my Dad used to say, "a trivial inequality." He was a mathematician. It's not hereditary.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements