Which way to tilt radiator w/ valve & vent on same side?
farrisjc
Member Posts: 5
(Alternate title: is this installed incorrectly?)
Renovated a 100yr old house - trying to get the one-pipe steam optimized (boiler seems fine and so far we had it drained/cleaned, plus new valves and vents on each radiator), but this one in the bathroom has the loudest water hammering.
First step I wanna try is shimming it, but I’m unsure which way it should tilt since the valve and air vent seem to defy the standard and are both on the same side… generally it does provide enough heat and the vent only rarely bubbles - but is this design problematic? Or if it should still be fine - which side should be elevated?
Thanks!
First step I wanna try is shimming it, but I’m unsure which way it should tilt since the valve and air vent seem to defy the standard and are both on the same side… generally it does provide enough heat and the vent only rarely bubbles - but is this design problematic? Or if it should still be fine - which side should be elevated?
Thanks!
0
Comments
-
Toward the valve. The condensate has to drain out the valve. Unless the internal construction of that is unusual it won't heat very well because the vent will close before the steam reaches the other side(the air also will tend to be trapped in the side opposite the valve and vent and it won't get much steam in that side even if the vent didn't close). The real fix is to move the vent to where there is a plug or boss for the vent on the other side.
Although with it being so small it might be ok.0 -
Thanks Matt - noted on the inefficiency w/ this setup, but it’s a very small bathroom so it seems fine for now.
I just want to make sure I’m 100%, by “toward the valve” you mean elevate the left side of the radiator?
I ask only because the valve opening to the pipe is facing the right side - so I could kind of see elevating the right side making sense if you specifically needed it pitched “toward the valve opening”… but I think you mean generally that any water in the radiator needs to drain toward the valve - and thus I should elevate the left side. Let me know, thanks!0 -
The left side of the radiator should be slightly higher than the right because the water in the radiator itself has to run toward where the valve is connected.0
-
Roger that - appreciate the help!0
-
But the problem as I think you noted is that if you pitch the left side higher (which I agree with) the nature of this radiator is such that the short horizontal pipe will collect some water. So I wouldn't pitch it very much.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
And I assume @pecmsg means "raise the left side 1/8" from level" not "from whatever it currently is"
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
One inch in 10 feet is the rule. You don’t need much.Retired and loving it.0
-
Got it shimmed on the left about 1/8” - will let you know how it goes. Appreciate the responses everyone!0
-
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements