One pipe steam radiator,.. loud pop after shutdown

Comments
-
You might try putting a little pad of slippery plastic -- like a square cut from a milk bottle -- under each of the feet of the radiator. The description sounds like an expansion and contraction noise.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
is your noise inside the room with you, or in the wall or floor?
try slipping a little piece of milk jug plastic under the 4 feet of the radiator,
try this same plastic trick where the supply pipe comes thru the floor or wall,known to beat dead horses0 -
Thank you!,..I'll try that.
I was wondering if it might be one of the upper or lower joints, Thought of putting a drop teflon based oil on them thinking that since someone painted the radiator many years ago, that it somehow caused it,..and when the oil evaporated off, there would still be a bit of teflon left to slightly lube the area. (?)
but I will try the plastic first,..0 -
I have a 2 pipe steam system that seems to me to short cycle. That is, it does keep up the heat of the house but it runs for a while and the water from the sight glass shortly goes down to where the auto shut off goes off and then the water returns also in a few munutes,(seems some comes from top down of the glass when its running )..is that normal?0
-
1 pipe, 2 pipe, 3 pipe, 4.
so the radiators have 1 pipe to them ?
and you're seeing 2 pipes at the boiler ?
can you post pictures of the boiler, floor to ceiling to show connected piping?
and then a closer shot of the controls, and that sightglass,
No, not normal or correct operation,
that's priming or surge, or unskimmed boiler water coming over the top of your sightglass, and it's geting splashed out into the system as WET steam,
water should not be leaving the sightglass, tripping your LWCO, low water cut out,
post pictures,
what pressure are you set to and whatpressure do you see on your gage when the water leaves the boiler,
Picturesknown to beat dead horses0 -
so the radiators have 1 pipe to them ?
and you're seeing 2 pipes at the boiler
Thank you,... but,
No,no,...they are two different boilers,..I'm a landlord,...I'll try to do pictures but I have never done that,..might have to get help from a younger guy,..0 -
No, thi is not normal. Most likely slow wet returns which need to be flushed out.Rick_41 said:I have a 2 pipe steam system that seems to me to short cycle. That is, it does keep up the heat of the house but it runs for a while and the water from the sight glass shortly goes down to where the auto shut off goes off and then the water returns also in a few munutes,(seems some comes from top down of the glass when its running )..is that normal?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I wonder if I caused this? Its an old house with old radiators but a new heating system with new near piping,..so I fell for the ads about stopping corrosion and all the other things that an additive might prevent. So I added 8 way boiler water conditioner...it says its for steam and hot water systems,Builds alkalinity, controls PH, inhibits corrosion, and "sure cure" color indicator.
I followed the directions and left a quart in the system. I think it was not over done, ( water was a bit undercolored.)
Anyway I basicall understand the need for skimmining, and I have heard from some steam guys (although we don't seem to have many very knowlegable of those around here) Who say don't add anything,
Do you think I should I take the time to skim this boiler?0 -
I'll also try to flush the wet returns (but the water is very clear when I open the valves for a moment,..(except for a bit of color of the additive) I'll try more aggressive flushing if you think it would be wise,..0
-
some of the guys here that use 8way, or other additives, use at a reduced rate, not at manufacturers' recommended rate,
and when used full strength, seem to find too much violence in their boil,
many here advise running straight water, unless deficiencies are identified to require additives,
using minimal additive amounts, to adjust water pH, is common,
It can't hurt to skim, and would be a good step when you seeing the carryover in the sightglass,
you'll be diluting the 8way, = good,
and or after skimming, empty the boiler and refill with fresh water only,
known to beat dead horses0 -
Thank you, I really appreciate you guys, sorry I'm such a babe in the woods,..but I;m learnin,...0
-
One more consideration,..would this have an effect on the 2 pipe system with a cause? Its a big house with 17 radiators, but since we don't use much of the area and to save fuel, have closed off some rooms,..4 rooms and 6 radiators by closing off the floor valves,..Would this cause this problem?0
-
Probably not. What shutting off the radiators will do or has done is cause the boiler to cycle on pressure more often. This does hurt efficiency, but not much.Rick_41 said:One more consideration,..would this have an effect on the 2 pipe system with a cause? Its a big house with 17 radiators, but since we don't use much of the area and to save fuel, have closed off some rooms,..4 rooms and 6 radiators by closing off the floor valves,..Would this cause this problem?
A word of caution, however. Do be sure that the rooms which are closed off are staying warm enough so you are not getting condensation in them, particularly on the windows or outside walls or the ceilings, but also on furniture and books. That could easily cost you more in the long run than any fuel might save.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you again!..yes,.. I check them often enough as I have things in them that I need to access...0
-
but it runs for a while and the water from the sight glass shortly goes down to where the auto shut off goes off
How long is "a while"?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I would say about 2 minutes,..0
-
That's not a clogged return, that's surging as mentioned by some earlier in the thread.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
So,..the best try for correction would be skimming?0
-
Maybe, or the near-boiler piping might be incorrect which can cause it. Send some pics of the boiler from different directions showing floor to ceiling
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements