Need cleanable check valve: $56 union connect or $20 Sharkbite?
Comments
-
-
I wouldn't use a SB for a maintenance/serviceable part. While they are re-connectable more than once, they become less reliable every time they're re-used, unless they make a two piece union that is meant to come apart (haven't seen one). I'd just sweat in a union an be done with it.Jells said:My check valves on hydronic heat get all gunked up with mineral deposits to where I have to rap them with a hammer to get them open! So I want an easy way to pull them and give them a vinegar bath. Is there a downside to cheaping out with the Sharkbites? I have the flex in the system to remove them. The union ones are pretty pricey.
0 -
Don't know, by all reports we don't have very hard water, but it is what it is. Clogs up the checks and mixing valves. I recently put a Clearwave on the main service, figuring if it helped it was worth the relatively small price.hot_rod said:whats causing all the mineral deposits?
0 -
Thanks. I usually give em some extra grease, but I recognize they are not immortal. However they're about 1/3 the price of the union check! I'm assuming that union check is robust enough to be serviced many times, if not I'd be better off just replacing the SB one every time.MaxMercy said:
I wouldn't use a SB for a maintenance/serviceable part. While they are re-connectable more than once, they become less reliable every time they're re-used, unless they make a two piece union that is meant to come apart (haven't seen one). I'd just sweat in a union an be done with it.Jells said:My check valves on hydronic heat get all gunked up with mineral deposits to where I have to rap them with a hammer to get them open! So I want an easy way to pull them and give them a vinegar bath. Is there a downside to cheaping out with the Sharkbites? I have the flex in the system to remove them. The union ones are pretty pricey.
0 -
You could use 2 pairs of circulator flanges, less expensive than a union if cost is your concern.0
-
Go cheap and pay later!Jells said:
Thanks. I usually give em some extra grease, but I recognize they are not immortal. However they're about 1/3 the price of the union check! I'm assuming that union check is robust enough to be serviced many times, if not I'd be better off just replacing the SB one every time.MaxMercy said:
I wouldn't use a SB for a maintenance/serviceable part. While they are re-connectable more than once, they become less reliable every time they're re-used, unless they make a two piece union that is meant to come apart (haven't seen one). I'd just sweat in a union an be done with it.Jells said:My check valves on hydronic heat get all gunked up with mineral deposits to where I have to rap them with a hammer to get them open! So I want an easy way to pull them and give them a vinegar bath. Is there a downside to cheaping out with the Sharkbites? I have the flex in the system to remove them. The union ones are pretty pricey.
2 -
Expensive, but they sure make things easy. They also have a high Cv.https://www.supplyhouse.com/Caleffi-NA51256-3-4-Press-Serviceable-Inline-Check-Valve-Low-Lead
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
The sweat version is the one in my Supplyhouse cart. Alas, I do not yet have a press tool!Expensive, but they sure make things easy. They also have a high Cv.https://www.supplyhouse.com/Caleffi-NA51256-3-4-Press-Serviceable-Inline-Check-Valve-Low-Lead0 -
I'd like to see a study of sharkbite failures vs sweated fitting failures. I bet Sharkbite has them.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Jells said:
Don't know, by all reports we don't have very hard water, but it is what it is. Clogs up the checks and mixing valves. I recently put a Clearwave on the main service, figuring if it helped it was worth the relatively small price.hot_rod said:whats causing all the mineral deposits?
Looks like a complete waste of $100-300 to me.
I'd go unions for sure.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
I consider a Y strainer a pointy of muse device. Use them to protect balance valves, checks,anything prone to getting debris. Easy to clean without disassembling.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
hot_rod said:I consider a Y strainer a pointy of muse device. Use them to protect balance valves, checks,anything prone to getting debris. Easy to clean without disassembling.0
-
Does your system leak and require refilling? If it is not too big a system, why not clean it up and fill it with better water. If it is plugging your check valves, it is probably scaling the boiler and any other HX in the system. You might experiment by closing the fill valve and seeing if you lose pressure."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
nothing like scale to drive down boiler an HX efficiency.
If fill water is over 7 GPG, this build up starts the first day you fill your system.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:nothing like scale to drive down boiler an HX efficiency. If fill water is over 7 GPG, this build up starts the first day you fill your system.
Of course, we have to understand that chart was made by someone trying to sell products that solve such issues.
I'm not saying it's not true, I'm just saying it very well may be exaggerated.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
But the sweat joint failure is all pilot error, not the technology. If I had to replace the SB check after 3 services, I'd be at par with the Union. But I was a sport and ordered the sweat union ones. They're here and I'll install them this week.ethicalpaul said:I'd like to see a study of sharkbite failures vs sweated fitting failures. I bet Sharkbite has them.
Here we go, where I get piled on for disclosing it's a potable water system running off a 40k BTU tank. I have a programmable 24V timer that runs the pump for 5 min each week 52 weeks a year to clear the sitting water during off season. It's a much simpler solution to the sanitary problem than a plate exchanger.Zman said:Does your system leak and require refilling? If it is not too big a system, why not clean it up and fill it with better water. If it is plugging your check valves, it is probably scaling the boiler and any other HX in the system. You might experiment by closing the fill valve and seeing if you lose pressure.
Amazon ASIN B01MRYMT3H
0 -
-
You could put it between 2 of these and be able to flush acid through it occasionally:
https://www.supplyhouse.com/Webstone-50613W-3-4-Sweat-PRO-PAL-Full-Port-Ball-Valve-w-Drain-Lead-Free
or use one of the threaded version and one of the union version and be able to remove the check valve.0 -
-
Expensive, but they sure make things easy. They also have a high Cv.https://www.supplyhouse.com/Caleffi-NA51256-3-4-Press-Serviceable-Inline-Check-Valve-Low-Lead0
-
Putting one of those in every unit would get pricey and labor intensive to maintain. $30 cart every 4-6 months! I looked into a 'softener' for the whole building, but it seemed a PITA too. No easy solutions, which is why I took a chance on the Clearwave.PatN said:0 -
What @Alan (California Radiant) Forbes said. Add a pair of press isolation valves and you’ll be set!PC7060 said:Expensive, but they sure make things easy. They also have a high Cv.https://www.supplyhouse.com/Caleffi-NA51256-3-4-Press-Serviceable-Inline-Check-Valve-Low-Lead
The checks are on the loop so there's already isolation valves.0 -
Interesting idea, but not as simple as pulling out the check and dropping it in vinegar for a while.mattmia2 said:You could put it between 2 of these and be able to flush acid through it occasionally:
https://www.supplyhouse.com/Webstone-50613W-3-4-Sweat-PRO-PAL-Full-Port-Ball-Valve-w-Drain-Lead-Free
or use one of the threaded version and one of the union version and be able to remove the check valve.0 -
Jells said:
Putting one of those in every unit would get pricey and labor intensive to maintain. $30 cart every 4-6 months! I looked into a 'softener' for the whole building, but it seemed a PITA too. No easy solutions, which is why I took a chance on the Clearwave.PatN said:
You came here and asked a question. Most are against your idea, but you argue your point.
Go ahead, use Shark bites. Professionals use them only temporally and replace with a permanent solution!2 -
So.
Aside from you doing your own work in multiple unit buildings that you rent.........
You have 30 gallon tank heaters in each unit that are being shared to do space heating and domestic hot water?
Wonderful.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I've hired licensed professionals for permitted jobs that used Sharkbites in special cases, like at the bottom of a riser where getting it drained enough to sweat is a PITA. So your statement is not universally true, but to be fair it was like 2007 before Pro-press was so ubiquitous. Plus you didn't read the whole thread to see I ordered the union checks anyway.pecmsg said:Jells said:
Putting one of those in every unit would get pricey and labor intensive to maintain. $30 cart every 4-6 months! I looked into a 'softener' for the whole building, but it seemed a PITA too. No easy solutions, which is why I took a chance on the Clearwave.PatN said:
You came here and asked a question. Most are against your idea, but you argue your point.
Go ahead, use Shark bites. Professionals use them only temporally and replace with a permanent solution!0 -
They're 40 gal, and I told you the dog pile would commence! These are 450 sq ft attached rowhouse units where the direct venting possibilities for a dual use mod-con heater are non-existent. These systems are not uncommon in my area.ChrisJ said:So.
Aside from you doing your own work in multiple unit buildings that you rent.........
You have 30 gallon tank heaters in each unit that are being shared to do space heating and domestic hot water?
Wonderful.
My 1st conversion from gas-on-gas I listened to the heating contractor, and let them put in a Minitherm boiler and an indirect tank. It was expensive, noisy, had a big footprint and was unreliable due to some venturi effect in the flue constantly turning it off.0 -
I said wonderful, that's not necessarily an insult.
Since these heaters are typically 50-60% efficient I'm going to assume fuel cost isn't included with the rent.
Wow that just hit me.
450sqft?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Yes. Exactly. 120 year old city rowhouse 1br. That's why such a modest form of heating works. Plus they're mostly attached. And they pay for their own gas. I even have been installing Nests for them, as the utility is giving them away.ChrisJ said:I said wonderful, that's not necessarily an insult.
Since these heaters are typically 50-60% efficient I'm going to assume fuel cost isn't included with the rent.
Wow that just hit me.
450sqft?
The unit I'm working on I've dispensed with baseboard and am doing it with totally with Twin flo kickspace heaters. In such a small space baseboard reduces the room, besides always getting rusty, dirty and falling apart, with tenants blocking their airflow. I am surprised it's taking 3 heaters, I thought two K120s would do it, but we finally had a cold snap and it was running 100% at 26 degrees out with a temp drop of 20 deg on the loop. I'm adding a 3rd Twin flo.0 -
Jells said:
I've hired licensed professionals for permitted jobs that used Sharkbites in special cases, like at the bottom of a riser where getting it drained enough to sweat is a PITA. So your statement is not universally true, but to be fair it was like 2007 before Pro-press was so ubiquitous. Plus you didn't read the whole thread to see I ordered the union checks anyway.
You came here and asked a question. Most are against your idea, but you argue your point. Go ahead, use Shark bites. Professionals use them only temporally and replace with a permanent solution!You may want to try this. https://www.supplyhouse.com/3M-Aqua-Pure-AP43011-Aqua-Pure-AP430SS-Hot-Water-Heater-Scale-Inhibitor-System-AP431-Cartridge-Included?utm_source=google_ad&utm_medium=Shopping_tm&utm_campaign=Shopping_TM_LPLTV&gclid=EAIaIQobChMI9JC4gIL--wIVRuTICh13BgFKEAQYBSABEgLAQvD_BwE
Putting one of those in every unit would get pricey and labor intensive to maintain. $30 cart every 4-6 months! I looked into a 'softener' for the whole building, but it seemed a PITA too. No easy solutions, which is why I took a chance on the Clearwave.Qualified: Someone that KNOWS how to do a job.Pro Press is over 20 years in use in the USA. Longer in Europe.1 -
Professional: Someone that gets paid to do a job.Qualified: Someone that KNOWS how to do a job.
And there's the rub about hiring a contractor of any flavor, I have to become an expert in their field to tell whether they know what they're talking about! By that point, if it doesn't involve a lot of heavy lifting, I just do it myself.
I can't tell you the **** I'm going through trying to get a steam boiler system with bad combustion diagnosed and serviced. Last guy, who was originally called to service the flue as part of eliminating the possible causes of bad combustion, stands there talking about his decades of installing boilers as a Master Plumber and licensed chimney sweep, and tells me, without measuring combustion or even examining the system closely, that I need to rip out the 10 year old boiler and install a new one! A previous one, again without combustion analysis, tells me to rip out all the returns! When I said I wasn't going to do that before running a combustion analysis on the sooted up boiler, he ghosted me. If I didn't know something about this stuff, I'd have spent over $10k and the problem would still not be fixed!3 -
These are common in the rest of the world where tankless and combi are the common DHW source. You refill the phosphate crystals every so often.
of course we need a supersized version for the US market in flow capacity and canister size.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
What I'd really want is a whole multifamily house sized version of that. Suggestions on product? I got the Clearwave because looking at all the options for the consumable types made my head explode.hot_rod said:These are common in the rest of the world where tankless and combi are the common DHW source. You refill the phosphate crystals every so often.
of course we need a supersized version for the US market in flow capacity and canister size.0 -
Jells said:Qualified: Someone that KNOWS how to do a job.And there's the rub about hiring a contractor of any flavor, I have to become an expert in their field to tell whether they know what they're talking about! By that point, if it doesn't involve a lot of heavy lifting, I just do it myself. I can't tell you the **** I'm going through trying to get a steam boiler system with bad combustion diagnosed and serviced. Last guy, who was originally called to service the flue as part of eliminating the possible causes of bad combustion, stands there talking about his decades of installing boilers as a Master Plumber and licensed chimney sweep, and tells me, without measuring combustion or even examining the system closely, that I need to rip out the 10 year old boiler and install a new one! A previous one, again without combustion analysis, tells me to rip out all the returns! When I said I wasn't going to do that before running a combustion analysis on the sooted up boiler, he ghosted me. If I didn't know something about this stuff, I'd have spent over $10k and the problem would still not be fixed!Glad you think all were good for is heavy lifting!
I guess my almost 50 years in the field were a waste of time, you already know it all!
most here have forgotten more then you’ll ever know!Good luck
try not to hurt anyone!0 -
pecmsg said:I guess my almost 50 years in the field were a waste of time, you already know it all!
most here have forgotten more then you’ll ever know!0 -
You have a few options to remove or mitigate hard water problems. Ion exchange water softener, requires salt backwash. Phosphate treatment, requires replenishing the crystals, magnets, or TAC type treatment. I've tried all but TACJells said:
What I'd really want is a whole multifamily house sized version of that. Suggestions on product? I got the Clearwave because looking at all the options for the consumable types made my head explode.hot_rod said:These are common in the rest of the world where tankless and combi are the common DHW source. You refill the phosphate crystals every so often.
of course we need a supersized version for the US market in flow capacity and canister size.
As with any technology they all have pros and cons. Love and hate fan base
Or live with the problems and maintenance of the minerals.
https://www.watts.com/our-story/brands/oneflow/template-assisted-crystallization-technologyBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements