Steam boiler pressure.
mmc239
mmc239 Member Posts: 94
I believe my steam boiler pressure is to high because my steam baseboard located right above my boiler spots a lot of water and has a lot of air. Is this the pressure gauge and if so is it too high?
    Steamhead Member Posts: 18,528
    The gray box is the pressure control. Crank it down!
    If the baseboard keeps spitting, let us know.
    Consulting
  • Ironman
    Ironman Member Posts: 7,904
    It shouldn’t be above 2 psi. If it’s a vapor system, 6-8 oz should be sufficient.
    Bob Boan
  • TonKa
    TonKa Member Posts: 111
    edited November 2022
    Does that gauge work?
    Set the pressuretrol to the lowest it can go: 0.5 psi.
    Pull the cover off the pressuretrol and verify the white wheel is set to 1.
    As far as the radiator goes, it is possible its problems may be related to the fact your pressure is too high. However, it may also be unrelated. You need to get the pressure straightened out first before anything else can be properly investigated, if needed.
  • mmc239
    Thank you. Do I I just push the dial down manually on the gray box?
    No. Turn the screw on the top counterclockwise. Watch the pointer go down.
    Consulting
    TonKa
  • mmc239
    Thank You.
    EBEBRATT-Ed Member Posts: 20,236
    @mmc239
    it's possible if you screw it down too low the boiler ma not start if that happens raise it a little. And if you really unscrew it too far the screw can become disconnected. use a little caution. you should also have the pigtail cleaned