Steam two pipe Radiators not heating properly , some weird sounds
JoshP
Member Posts: 73
I have a two pipe steam system . Pipes and radiators original to house installed late 1920s, current American standard boiler probably early 60s. I’ve got the system working pretty darn well almost silent when operating . The Issue I’m having is two second floor radiators in two different bedrooms (adjacent to each other) at opposite end of boiler (boiler in the basement) have always sounded like off and on gushing water maybe some might call it panting (heavy breathing )in the vertical supply steam pipes running up through the walls to those two radiators. I’ve replaced the traps at those radiators and also made sure they were pitched to drain condensate properly. I’ve read it could be debris or water “stuck” in the supply pipe causing a reduced flow or small blockage. Those two rooms are generally considerably cooler than the rest of the house. The t stat will generally shut off at set point before those two radiators get full of steam. No banging or knocking from the vertical pipes. Any thoughts or remedies ? Thanks
0
Comments
-
Look for a horizontal, or near horizontal, section of piping either in the supply or in the return common to those two radiators which isn't pitched adequately to drain.
Is there a main vent or crossover trap on the main feeding these two?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:Look for a horizontal, or near horizontal, section of piping either in the supply or in the return common to those two radiators which isn't pitched adequately to drain. Is there a main vent or crossover trap on the main feeding these two?0
-
can you post a picture of one of the trouble makers,
actually, 2, one of each end showing as much supply or return pipe as possibleknown to beat dead horses0 -
The supply and return are on the same side on both rads. Don’t think that makes a difference but thought I would note it if you see the pics and are wondering.0
-
ok,
i meant to see the radiator, and as much pipe as possible,
and now I'm really interested,
are the rads vented at the far end ?known to beat dead horses0 -
neilc said:ok, i meant to see the radiator, and as much pipe as possible, and now I'm really interested, are the rads vented at the far end ?No vents at the rads. Both pitched at least 1/4 bubble to return . Both have covers. I have replaced the trap elements with new ones. Also note someone before me replaced the valves with non steam type but the ones in my bedroom also have non stream type valves and doesn’t stop them from heating up the room.0
-
the working rads, are they piped the same way? both pipes at the same end like these?
Are the returns under the noneworking traps hot? steam hot?
known to beat dead horses0 -
Two pipe with traps, @neilc .neilc said:ok,
i meant to see the radiator, and as much pipe as possible,
and now I'm really interested,
are the rads vented at the far end ?
Can you get enough of the insulation off to check the pitch of the horizontal parts of the runouts? They may be flat enough to hold some water -- though not enough to hammer.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
yeah, but, uh,@Jamie Hall said:
ok, steam in the top, pushes air out the bottom,
I'm just having problems seeing the far end clearing its air,
maybe the supply valves need to be throttled down ?known to beat dead horses0 -
Jamie Hall said:
ok, i meant to see the radiator, and as much pipe as possible, and now I'm really interested, are the rads vented at the far end ?
Two pipe with traps, @neilc . Can you get enough of the insulation off to check the pitch of the horizontal parts of the runouts? They may be flat enough to hold some water -- though not enough to hammer.0 -
neilc said:the working rads, are they piped the same way? both pipes at the same end like these? Are the returns under the none working traps hot? steam hot?0
-
I will also mention when we first bought the house my FIL not realizing it was a steam boiler opened up the fill valve because the boiler was drained and off and began to fill the system with water. I had water leaking out of the rad connections on the second floor. Not sure how much water was added but I subsequently drained the system to correct water level . This was 10 years ago.I’ve replaced the trap element and adjusted the pitch since then.0
-
I would try loosening the union at the trap on a radiator and observing it during a heat cycle to see if you get steam to the radiator quicker. Be ready, obviously, to catch any condensate and escaping hot steam and end the cycle. But this will tell you at least if the issue lies downstream in the return or if you're not getting sufficient steam to the radiator.0
-
Did those radiators ever heat properly after the system was flooded?
The supply and return on one end should be fine because the steam will rise to the top of the radiator and move across then down pushing the air down so it should fill just fine.
Remember if a trap is failed open it doesn't keep the radiator it is on from heating, it potentially keeps other radiators from heating because the steam in the return blocks air from venting through the return and potentially gets to the outlet of other traps and closes them.0 -
mattmia2 said:Did those radiators ever heat properly after the system was flooded? The supply and return on one end should be fine because the steam will rise to the top of the radiator and move across then down pushing the air down so it should fill just fine. Remember if a trap is failed open it doesn't keep the radiator it is on from heating, it potentially keeps other radiators from heating because the steam in the return blocks air from venting through the return and potentially gets to the outlet of other traps and closes them.0
-
veteransteamhvac said:I would try loosening the union at the trap on a radiator and observing it during a heat cycle to see if you get steam to the radiator quicker. Be ready, obviously, to catch any condensate and escaping hot steam and end the cycle. But this will tell you at least if the issue lies downstream in the return or if you're not getting sufficient steam to the radiator.0
-
Is the return pipe cold?
You're not thinking like steam. If air can't get out, steam can't get in. If steam heats a steam trap it will close, it doesn't care if it comes from the supply or the return. If steam encounters more than a small amount of water, that water will absorb the heat of the steam and the steam will collapse back in to liquid water. Most "blockages" in steam systems are not solid objects but air, steam, or water.1 -
I would take the cage trap cover off of the trap and remove the cage unit. Just have some one at the boiler to shut it off when ready. This way if you do have a failed trap causing the problem you will most likely see it coming thru the trap. If radiator heats and no steam at return trap shut radiator valve off and wait. It might come a little later. This will help with determining a supply or return issue0
-
mattmia2 said:Is the return pipe cold? You're not thinking like steam. If air can't get out, steam can't get in. If steam heats a steam trap it will close, it doesn't care if it comes from the supply or the return. If steam encounters more than a small amount of water, that water will absorb the heat of the steam and the steam will collapse back in to liquid water. Most "blockages" in steam systems are not solid objects but air, steam, or water.0
-
Water sitting somewhere -- and it doesn't have to be a full pipe, could just be an extended puddle -- is all about pitch. Consistent pitch. There are recommended slopes for pipes -- but even if it isn't quite right, it probably will work -- provided there are no, and I do mean no, low spots or sags.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Just checked returns on both after a longer heat cycle. The traps are pretty warm but returns in basement are maybe room temp. Warmer than ambient temp in basement but not hot.I’ll work on opening up the trap and seeing what happens.0
-
Are these off of the main in about the same location? Is this the end of the main or are there more radiators past this? What happens at the end of the main to get rid of air and condensate?0
-
mattmia2 said:Are these off of the main in about the same location? Is this the end of the main or are there more radiators past this? What happens at the end of the main to get rid of air and condensate?0
-
pedmec said:I would take the cage trap cover off of the trap and remove the cage unit. Just have some one at the boiler to shut it off when ready. This way if you do have a failed trap causing the problem you will most likely see it coming thru the trap. If radiator heats and no steam at return trap shut radiator valve off and wait. It might come a little later. This will help with determining a supply or return issue0
-
Any suggestions here ? I disconnected both supply and return lines from one of the problem rdas. Was able to get both about 3/4” higher by pushing up on the lines from the basement . This increased the positive pitch of the horizontal lines before the run up inside the wall to the rad. It didn’t seem to help. Also why are both sides of the system , the two mirror image rads in question, acting the essentially the same way as described above?0
-
maybe the water belly is closer to the boiler ?
have you posted any pictures of questionable piping?known to beat dead horses0 -
neilc said:maybe the water belly is closer to the boiler ? have you posted any pictures of questionable piping?
0 -
ok, so, after the riser and return leave the basement, and shoot up the first floor to the second,
what's happening up there?
are there horizontal laterals before supplying the 2 rads?
and on the blue and black diagram, or as I read,
we're talking about 2 different rads,
on 2 different risers and returns,
and the 2 riser sets are fed from 2 different mains in the basement?
known to beat dead horses0 -
neilc said:ok, so, after the riser and return leave the basement, and shoot up the first floor to the second, what's happening up there? are there horizontal laterals before supplying the 2 rads? and on the blue and black diagram, or as I read, we're talking about 2 different rads, on 2 different risers and returns, and the 2 riser sets are fed from 2 different mains in the basement?0
-
I'm stumped,
is the boiler firing its fullest?
out of tune, under fired?
does it make pressure on the gage?
for giggles, try closing valves on the working rads, and see if steam reaches these 2 naughty rads,
same vein, open the union on the supply valve(s), run boiler,
got steam ?
that near boiler piping, is not correct, = wet steam ?
dirty water? = wetter steam?
and those 2 basement laterals are just wetting and collapsing the steam delivery,
maybe they need to pitch down to the risers, and add @Jamie's crossover traps, to the dry returnsknown to beat dead horses0 -
If you try neilc's suggestions above of turning off the other radiators' supply valves and then find you get heat to the cold radiators then I would wonder if perhaps you have too much main venting or valve issues at the suspect radiators or some of the steam quality issues mentioned above.0
-
If you turn off another emitter and other emitters that weren't heating start heating, on 2 pipe steam, it is steam passing through those emitters that are now closed and in to the returns and keeping those emitters that weren't heating from venting. It is possible that it could be underfiring/sizing of the boiler, inlet restrictions for a trapless system on some bot not all of the emitters, or condensate from the working emitters blocking the return that doesn't drain right.0
-
mattmia2 said:If you turn off another emitter and other emitters that weren't heating start heating, on 2 pipe steam, it is steam passing through those emitters that are now closed and in to the returns and keeping those emitters that weren't heating from venting. It is possible that it could be underfiring/sizing of the boiler, inlet restrictions for a trapless system on some bot not all of the emitters, or condensate from the working emitters blocking the return that doesn't drain right.0
-
Lets see. If you get no air or steam out of the open valve not connected to the radiator then it is the supply. Try taking the bonnet off the valve make sure both haven't fallen apart inside the valve. Since it was flooded there could be debris in each runout trapping water although it is a lot more likely in the return or a one pipe with the valve at the bottom. You could try pouring like a bucket of water down the supply.0
-
to be clear,JoshP said:
I’ll try closing down the two second floor rad valves and see what happens. I did open the union at the trap and took the cap off the trap and cycled the boiler.
I was suggesting shutting off radiators that are working, to force steam to the 2 that are not working,
or maybe as others are saying, (and I agree with), maybe a "working" rad is passing steam thru it's trap, and fouling the returns of the non working rads,
and second, to eliminate or prove the fouled returns theories,
I would open the union at the supply valve to the non working rad(s),
run the boiler, and see that steam does, or does not pass thru the supply valve, this becomes another good time to confirm the valve is open, and not failed closed internally.known to beat dead horses0 -
mattmia2 said:Lets see. If you get no air or steam out of the open valve not connected to the radiator then it is the supply. Try taking the bonnet off the valve make sure both haven't fallen apart inside the valve. Since it was flooded there could be debris in each runout trapping water although it is a lot more likely in the return or a one pipe with the valve at the bottom. You could try pouring like a bucket of water down the supply.
To be clear the rads are heating up to some degree but minimally and usually only about 1/2 of the top of the rad is hot before the system cycles off. And as noted there is lots of noise from the steam trying to get through to the rads.
Today to took off the shut off valve at one of the problem rads. Inspected the valve and there are no issues with it. Opens fully no restrictions. I poured a small amount of water down the open supply. Then I used my small portable air compressor to shoot some compressed air in the pipe. My luck I popped the fuse in the air compressor before I could really get much air in the pipe. So I restored to blowing in the pipe myself. I’m getting puff back of air as is there is a restriction in the pipe. Considering I’m blowing in the pipe and it’s a second floor riser and still get air blown back at me does that mean I’ve got a pool of water or something more in the pipe restricting the pipe flow ? Shouldn’t the supply be open back to the boiler and just fill with the air i blow in?0 -
It could be either. Try like a gallon of water. If it is trapped water it will pour through. If it is debris it will fill up the pipe.
My strong suspicion is that there is a lateral in the supply below the floor that has the wrong pitch0 -
mattmia2 said:It could be either. Try like a gallon of water. If it is trapped water it will pour through. If it is debris it will fill up the pipe. My strong suspicion is that there is a lateral in the supply below the floor that has the wrong pitch0
-
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements