mattmia2 said:It could be either. Try like a gallon of water. If it is trapped water it will pour through. If it is debris it will fill up the pipe. My strong suspicion is that there is a lateral in the supply below the floor that has the wrong pitch0
-
I think the basement is ok especially with the extra blocking on the girder, but give it a good look just the same,
if there's a horizontal above the first floor to the second floor, that would be my bet,
(and you may have made this worse when you blocked up the basement, where did that basement elevation change go, upstairs?)
did you try lifting those 2 rads?
gently get them as high as possible before breaking into a ceiling or floor,known to beat dead horses0 -
The main may have moved up when a boiler was changed or something pushing the connection to a lateral in the floor/ceiling up and pitching it the wrong way.
If you do have to go with the open procedure, smooth plaster is a lot easier to patch than a wood floor.0 -
neilc said:I think the basement is ok especially with the extra blocking on the girder, but give it a good look just the same, if there's a horizontal above the first floor to the second floor, that would be my bet, (and you may have made this worse when you blocked up the basement, where did that basement elevation change go, upstairs?) did you try lifting those 2 rads? gently get them as high as possible before breaking into a ceiling or floor,0
-
mattmia2 said:The main may have moved up when a boiler was changed or something pushing the connection to a lateral in the floor/ceiling up and pitching it the wrong way. If you do have to go with the open procedure, smooth plaster is a lot easier to patch than a wood floor.When I poured the water in the supply pipe with the valve off I listened carefully to how it sounded and it didn’t sound to me like it met a restriction close by. Sounded like it dropped 10 ‘ fast.0
-
ok, but if you pushed up the basement by a 2x4+,
well you don't have a 2x4 under the rad,
so there's still a difference there between the 1st and second floor,
disconnect the rad again, and just pull up on the pipes for all you got, gently,
or let off on the basement blocking by half (?)known to beat dead horses0 -
Ok so far I’ve had a chance to run a scope camera down the supply pipe at one of the second floor rads. I removed the shut off valve and could only go down the pipe about 30” or so to where there appears to be a 90 elbow routing the supply over through the floor joist area to inside the wall cavity. After a short horizontal There appears to be another 90 elbow to route the pipe vertical down inside the wall to the basement. I did not see any standing water or blockage but couldn’t see very far inside anyway .Being the both my second floor rear bedroom rads are both slow to heat and exhibit the same symptoms (steam inside supply pipe fighting to move) would it be possible the steam is condensing inside the vertical supply since it’s not insulated inside the wall cavity going from basement to second floor ? Or is my problem more likely in that floor joist section of pipe ?0
-
All my verticals are in basically uninsulated spaces and they heat quickly.
my one “slow/gurgling” radiator was due to a low spot in the basement where it goes into the wallNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
remember you said you blew in the open supply line,JoshP said:Being the both my second floor rear bedroom rads are both slow to heat and exhibit the same symptoms (steam inside supply pipe fighting to move) would it be possible the steam is condensing inside the vertical supply since it’s not insulated inside the wall cavity going from basement to second floor ? Or is my problem more likely in that floor joist section of pipe ?
and it blew back at you? do I have that correct?
you have to have a trapped pocket of water somewhere there on those 2 supplies,
consider opening the ceiling / wall where you saw that next 90 with the inspection camera,
known to beat dead horses1 -
-
Thanks I will be opening up some of the floor to get a better look and the pipes. I may try flushing more water down the supply too. I’ll post back results.0
-
I'd try flushing water through with a hose before cutting in to the floor. I'd cut in to the ceiling below because plaster is easier to patch than flooring0
-
mattmia2 said:I'd try flushing water through with a hose before cutting in to the floor. I'd cut in to the ceiling below because plaster is easier to patch than flooring0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements