Wiring for Nest
Two btu per sq ft for degree difference for a slab
Comments
-
-
There’s just one transformer on the pump controls.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I hope you wired them in parallel, @Alan (California Radiant) Forbes ! But if they really are in parallel they will act as a single power source.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Ganging class 2 transformers, the transformers secondaries need to be wired in polarity (phase). The easy way to determine if the transformers secondaries are correctly wired together is to take one secondary of each transformer and tie them together. Take the other secondary of each transformer and strike them together quickly and they will spark. Reverse one secondary lead and connect them together again and strike the other untied leads which will spark. The connection that produces the smallest spark is the connection that is in the correct polarity.0
-
I'd use the @EdTheHeaterMan fuse trick when wiring transformers togetherBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Here's what I was taught...
There is no hot or ground on the secondary side of a transformer. It is floating until one side is grounded.
Ground one side of the secondary, measure L1 to R, should read about 96v.
If it reads 144v, then you have the wrong side of the secondary grounded.
There was an error rendering this rich post.
3 -
Phasing single phase transformers is easy. Connect the common of both transformers together & measure the voltage between the two Rs. If it's zeroish (2-4 volts is common) they're in phase, if it's 50ish volts (2x nominal 24 VAC) they're out of phase. You shouldn't need to involve the primaries unless it's three phase. (Phasing transformers on 3 phase involves getting onto the right primary too. It does make a difference.)1
-
I'd use the @EdTheHeaterMan fuse trick when wiring transformers together
Yeah, I liked ETHM’s trick as well. I went the easy route with a circuit breaker on the transformer.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
There is a minimum service charge for that idea. $2.50 for the fuse or $4.99 for the circuit breaker.hot_rod said:I'd use the @EdTheHeaterMan fuse trick when wiring transformers together
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
EdTheHeaterMan said:
I'd use the @EdTheHeaterMan fuse trick when wiring transformers together
There is a minimum service charge for that idea. $2.50 for the fuse or $4.99 for the circuit breakerOperators are standing by.place your order in the next 10 minutes and we’ll ship 2 for the price of one. Just pay the extra shipping and handling.1 -
There will come a time when the Caleffi switching relays will come with a snap in 40Va, a second 40 can be snapped in. Both circuit breaker protected. Gone will be the small 15 Va transformer populated on the board.
Plenty of power for stats and light arc welding projectsBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
So, when I buy a transformer with the primary wiring hot and neutral (black and white) and the secondary wiring marked "R" and "C", can't I assume that it's properly phased?
And when I wire it in parallel to the transformer on the SR control, can't I assume that it is properly phased as well since the terminals are marked "R" and "C"?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
IF the transformers are the same mfgr, it's probably a safe assumption that they're the same polarity so that wiring the primaries & secondaries in parallel will be uneventful. It's not a given that any old transformer will be in phase with any other. Transformers are inherently uncaring about things like polarity and even power input—a 120:24 transformer will happily (mostly, there is some risk of the insulation breaking down at the higher voltage) give you 600 volts out if you feed the 24 volt side with 120 volts.1
-
No. Not only is electricity colour blind, it's illiterate. As someone once said -- "trust, but verify".So, when I buy a transformer with the primary wiring hot and neutral (black and white) and the secondary wiring marked "R" and "C", can't I assume that it's properly phased?
And when I wire it in parallel to the transformer on the SR control, can't I assume that it is properly phased as well since the terminals are marked "R" and "C"?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Also, be aware that Honeywell has 120/24 transformers out there now where the neutral is black and the hot is white.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
We are all trying to get along in this new politically correct world. Nice to know that Honeywell is allowing the roll reversal of the black and the white wires.The Steam Whisperer said:Also, be aware that Honeywell has 120/24 transformers out there now where the neutral is black and the hot is white.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements