Dual contactor
Why there are two contactor for condensing unit?
    Jamie Hall Member Posts: 27,618
    As marked -- a high and low staging. Have to see the wiring and mechanics to know exactly what it was doing.
    EBEBRATT-Ed Member Posts: 20,634
    2 speed compressor. Bristol (I think) was the only one that made them that I know of. Trane and Lennox used them don't know about anyone else.
    But if it is the one I am thinking of they had 3 contactors hi speed, lo speed and a tie contactor that switched the windings around electrically. But those contactors were mechanically interlocked as well. Usually one speed would fail as there wasn't a good way to protect the windings from overload
    I am assuming you only have 1 compressor in there.
    If you had a name and model # you might get mor information
    EdTheHeaterMan Member Posts: 12,581
    edited June 2022
    Two stage. two contactors
    Your thermostat should have Y1 and Y2 contacts to make that system operate at its best.
    Looks like an American Standard
  • ratio
    ratio Member Posts: 4,278
    Yeah, Bristol two capacity compressor. I say two capacity because it doesn't stage up or down for the different rates—it actually turns in opposite direction! Very neat, the crankshaft has an eccentric bushing on it that, turning in one direction, allows one piston to reciprocate, but turning on the other direction it locks in a position that is coaxial with the crank & therefore the piston doesn't move.
    They're very sensitive to damage from liquid slugging so be very careful with the charge.
    HVACNUTPC7060
    Good grief. I thought Rube Goldberg and Heath Robinson had patents on that sort of contraption...
    mattmia2 Member Posts: 17,666
    I'd imagine whoever designed it envisioned a modern pcb being constructed for the controls that hooked directly to the motor instead of 3 1950's era contactors point to point wired together to control it. Reversing a motor to shift functions without additional controls isn't an uncommon control strategy for all sorts of mechanical systems.
    edited June 2022
    The Bristol that @ratio is talking about is one I never heard of. The one I know had a high and low speed.
    The Bristol I know of was out of VA. Now there are in Dubai. So who knows.
    We are all guessing anyhow. If the OP expects any help some picture model, serial # etc would be needed. Otherwise why do we bother?
  • johnjohn89
    johnjohn89 Member Posts: 115
    2 speed compressor. Bristol (I think) was the only one that made them that I know of. Trane and Lennox used them don't know about anyone else. But if it is the one I am thinking of they had 3 contactors hi speed, lo speed and a tie contactor that switched the windings around electrically. But those contactors were mechanically interlocked as well. Usually one speed would fail as there wasn't a good way to protect the windings from overload I am assuming you only have 1 compressor in there. If you had a name and model # you might get mor information
    Thank u
  • johnjohn89
    Thanks a lot all of you
  • ChrisJ
    ChrisJ Member Posts: 17,549
    The one I have is a Copeland and just uses a solenoid to open and close bypass holes. It's a low voltage solenoid in that case.
  • ratio
    Some (all) if the internal bypass solenoids are 24 VDC. There's a bridge rectifier moulded into the li'l rubber cap that plugs on to the terminals (although I suppose that means it's not actually 24 volts...) Guess what happens if AC is applied to it. Hint: you'll be replacing the compressor. Honestly, I can't imagine why anyone anywhere ever thought it would be a good idea to mount a DC component inside a hermetic compressor & not protect it against AC voltage.
    PC7060
    The same people that thought putting an overload inside a hermetic compressor was a good idea.
    A bridge rectifier on 24vac nominal will give 24vdc nominal minus the junction voltage. That can be very small with barrier diodes.(although those have a limited lifespan but are more efficient but wouldn't be a good choice for this application)
  • pedmec
    pedmec Member Posts: 1,473
    why would you lose the compressor if the solenoid fails? its just an internal three way valve that normal positioning is bypassing 33% of the load. so in a failure of the solenoid you still have 67% capacity. compressor speed is not changed unlike the bristol which is a 50% capacity but in a failure is totally gone.
    just asking in case i'm missing something. never stop learning
    pecmsg
  • ratio
    I do new installs, which means I do 1st year warranty work. If the compressor isn't 100% healthy, they're getting a new one.
    I suppose if I was doing service work, I'd offer the customer the option of running unloaded like that. Given the preponderance of oversized equipment, they might not even notice!