New Thermostat - Circulator Issue
RDKing_66
Member Posts: 2
I just replaced the thermostat (line voltage) for a gas fired, hot water baseboard, zone in my house. The zone is operating at the correct temp, but the circulatator pump for that zone keeps cycling on and off every 10secs for a 5 sec run. This is 2 wire connection. Any ideas why pump keeps cycling?
0
Comments
-
The thermostat directly controls the circulator pump? Direct connection, no relays, no boards, no... ? If that's true, then there's something amiss with the thermostat. Could be the wrong thermostat for the application, or could have some setting wrong if it's a fancy one with settings, or... ?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Line voltage t-stats are a bit unusual in a baseboard system. Can you provide more details or pictures of the controls?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thanks Jamie. There are no relay boards or connections that I know of. I believe it is direct. I metered the connection at the box and it was 120v so I purchased a line voltage thermostat. It is a fairly basic unit. Digital read out, temp up/down, but not programmable.0
-
A lot of old gas and oil systems used line voltage thermostats, but they were usually wired through the low side of a dual aquastat, or a B control.
The cheapo builders special was to run a 14/3 romex to the first floor thermostat, and a 14/2 to the second floor from the first floor gem box. White was Common, Red first floor, Black second floor.
The bimetal Honeywell T451 thermostat only had about a 4 degree swing.
What are the operating controls on the boiler?
What type of circulator, Older 3 piece, motor cutting out on thermal overload?
0 -
Maybe the thermostat is designed for a resistive electric heat load only and is unhappy about the starting current of the circulator motor.0
-
-
Wrong Tstat or its set up wrong.RDKing_66 said:I just replaced the thermostat (line voltage) for a gas fired, hot water baseboard, zone in my house. The zone is operating at the correct temp, but the circulatator pump for that zone keeps cycling on and off every 10secs for a 5 sec run. This is 2 wire connection. Any ideas why pump keeps cycling?
Old retired Commercial HVAC/R guy in Iowa. Master electrician.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements