no hot water

Options
ncreek
ncreek Member Posts: 9
Lost hot water, i hear a fan running but have no ignition, cut off uniti at switch and turned back and unit goes though the motions , turn hot water on and nothing , fan stays running when cut water off

Comments

  • kcopp
    kcopp Member Posts: 4,432
    Options
    Can we get some more info? What type of water heater? Brand& model?
  • ncreek
    ncreek Member Posts: 9
    Options
    Navien NR-240A LP
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Have you contacted the installer?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ncreek
    ncreek Member Posts: 9
    Options
    I installed it, im thinking the igniters are bad or flow sensor? Whats your take
  • kcopp
    kcopp Member Posts: 4,432
    Options
    With any gas appliance....
    Do you have gas? What is the incoming pressure? Are other appliances working?
  • HomerJSmith
    HomerJSmith Member Posts: 2,441
    Options
    Is the condensate draining? Could be the thermo fuse?
  • mattmia2
    mattmia2 Member Posts: 9,670
    edited February 2022
    Options
    what did the combustion analysis show?

    did it work then stop or did it never work?
  • ncreek
    ncreek Member Posts: 9
    Options
    It never worked and shows no fault code
  • ncreek
    ncreek Member Posts: 9
    Options
    Draining fine, 
  • PC7060
    PC7060 Member Posts: 1,160
    Options
    Gas on?  That would usually throw a code tho
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    Check static and dynamic supply and manifold pressure.

    Any packing material in the vent like the clear packing tape over the little piece of cpvc to transition to PVC that htp shipped with my boiler?
  • Zman
    Zman Member Posts: 7,569
    Options
    ncreek said:

    Draining fine, 

    If you read other posts on this site, you will find that folks looking for help offer a lot more details. Pictures and responses using a few more words help us help you.

    Normally I would wonder if the gas line is purged of air with adequate pressure or if the flow switch is closing the circuit.

    The fan running all the time regardless of call for heat is a red flag. That sounds like a manufacturing issue. Have you gone through the troubleshooting part of the manual or called tech support?
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Ironman
  • ncreek
    ncreek Member Posts: 9
    Options
    I havnt trouble shooted yet, havnt the time, was just looking to see if someone might of had the same issue, in gonna start with system pressure and the ignition Pin, with the fan running, if it is getting fuel then maybe the ignighter Pin is bad/ dirty
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    how would the electrode be dirty if it has never run? i'd start with seeing if it even gets to the point of turning on the gas valve, might be a pilot then main stage, might just be a main stage. look at the sequence of operations in the manual and see how far it gets.

    did you look in the menus for stored errors?
    wmgeorgeIronman
  • mattmia2
    mattmia2 Member Posts: 9,670
    Options
    the fan running all the time makes me think it is failing to prove draft
    Zmanwmgeorge
  • ncreek
    ncreek Member Posts: 9
    Options
    The unit is 13 tra old and ive never had 1 problemi with it, never code or shows one now, thats whats got me stumped.
  • ncreek
    ncreek Member Posts: 9
    Options
    Draft is fine, no obstructions, unit looks brand new inside
  • pecmsg
    pecmsg Member Posts: 4,861
    Options
    the fan running is telling you
    it tried to light and failed
    it light but there’s other issues. 

    Time to get it serviced. 
  • Zman
    Zman Member Posts: 7,569
    Options
    ncreek said:

    It never worked and shows no fault code

    Now I'm confused...
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Ironman
  • Zman
    Zman Member Posts: 7,569
    Options
    ncreek said:

    The unit is 13 tra old and ive never had 1 problemi with it, never code or shows one now, thats whats got me stumped.

    Or this...
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Ironman
  • ncreek
    ncreek Member Posts: 9
    Options
    No this the first time ive had any problem with it, and it shows no fault code, i have serviced it regular. Idk
  • wmgeorge
    wmgeorge Member Posts: 222
    edited February 2022
    Options
    What does this mean?? The unit is 13 tra old and ive never had

    Or this? I havnt trouble shooted yet, havnt the time

    Old retired Commercial HVAC/R guy in Iowa. Master electrician.
    Zman
  • psb75
    psb75 Member Posts: 835
    Options
    You need to use your words and language carefully. That is how we communicate on this forum. It's largely up to you to present information fully, and carefully. Otherwise WE CAN'T HELP YOU.
    Ironman