How low can UG propane tank reach before pressure dropping out?

sunlight33
Member Posts: 378
I have a 500-gal underground propane tank (on a lease) supplying fuel for my boiler. When it was at 21% I called my propane company and they told me I will be getting delivery soon because I am on their automatic delivery system with the remote motoring. Now it's 13% and the company reassured me again that I will not be running out of propane, but they wouldn't tell me the delivery date. I use about 1% (5 lb) of propane daily. I have been using this company for eight years and they had always been reliable, but they never wait the tank to be this empty before refueling. Perhaps the drivers are calling sick due to Covid but at what point should I start to worry? 5%?
0
Comments
-
Propane delivery is much much more a matter of temperature than fill. What drives the propane out of the tank is the vapourization of the liquid -- and the pressure that exerts is entirely dependent on its temperature.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
A good reason to bury propane tank? Also will ground reduce venting in summer?Jamie Hall said:Propane delivery is much much more a matter of temperature than fill. What drives the propane out of the tank is the vapourization of the liquid -- and the pressure that exerts is entirely dependent on its temperature.
0 -
YupBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I would be more concerned about the accuracy of the gauge. With an underground tank, the temp will be stable and you should be able to go to 1% (unless the gauge is sticking).
Both of my local propane companies have closed their local offices in the last few years. Dealing with their websites and call services has been a major PITA."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
I would say 5% is the real minimum I'd ever go. If you are using 1% daily, then I surmise you don't need to worry much about wetted surface for vaporization. That usage is low for a 500, which is helpful in that you can get away with going lower.
This is all assuming your gauge is accurate, which most generally are.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Finally got the refill today. Even the driver himself was surprised at how low the tank has gotten to, well he said the reason for this lag was due to shortage of truck drivers.0
-
Dave Yates just wrote a great article on this in PM Mag.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements