Radiant in floor system over pressure
ebm
Member Posts: 5
My infloor system was installed about 13 years ago by an infloor engineer. The company subsequently closed. After a couple of years the system started to blow off. I purchase “pumping away” and discovered that the pump was pumping to the expansion tank. I had my plumbing and heating guys change the pump and tank location but the system continued to blow off. I also purchased Primary/Secondary pumping and had the system set up accordingly but the blow off continued. We increased the size of the expansion tank and that didn’t work so my plumbing guys and I are at a loss to solve the problem. Any ideas?
thanks
Dave
thanks
Dave
0
Comments
-
Under what conditions does the pressure rise? Does the gauge show the temp rising to the relief valve's rated pressure?
Could be:- Bad relief valve
- Bad fill valve (or improperly located)
- Improper expansion tank pressure (needs to be charged to system pressure when isolated from system)
- Pinhole in indirect heat exchanger
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein3 - Bad relief valve
-
I agree with @Zman. My first question was how are you heating your domestic hot water?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
The heater is a Slantfin Molitron electric boiler. The temp gauge shows both the temp (120 - 130) and the pressure 27 to 30 psi where it starts to drip fluid. The pressure valve and the fill valve have both been replaced twice. The reduction valve coming into the house has been replaced. The domestic hot water is on a separate system with its own 60 gal electric hot water tank. The floor system has its own 60 storage tank because we are on a time of day power set up0
-
What size is expansion tank? You may need a larger one with that 60 gallon storage tank.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The expansion tank is a Watts ETX 600
-
Also, was the air charge adjusted to match the pressure setting of the fill valve before it was connected to the system?
The tanks normally come precharged to 12 psi, but if the fill valve is set higher, the the air charge needs to be increased to match that or else the tank’s capacity is decreased.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
What is your design pressure? The pressure the fill valve and tank are set to. Does the pressure rise consistently as the system heats up?
Can you post a picture that shows the orientation of the circulator, expansion tank, and fill valve?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I think -- but I'm not positive -- that your problem is that the expansion tank is much too small. It would be about right for the radiation -- there's a fair amount of slack in there in the sizing -- but you have that 60 gallon storage tank. Look at it this way. That tank is, as I say, sized more or less right for a typical hot water heating system. Such a typical system will have around 20 gallons of water in it. You have that expansion tank, so your system has a water volume four times that. That's just not going to work...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks to all for the responses. First to Ironman,I believe the tank was pressurized to 15 psi to be the same as the fill valve.
second to Zman the system is set up for 15 psi and yes the pressure does slowly rise as to heats up.
thirdly to Mr Hall, My plumbing guy was thinking the same thing. I don’t have room in my mechanical room for a floor tank so he is going to tee in another ext 60. Hopefully that solves the issue. Thanks0 -
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements