Combi-Boiler Correct Sizing for Home
JohnJr
Member Posts: 14
Hello, first post and new user here. I came across this website and noticed a lot of valuable information and would like to present my own situation. I am looking to install a combi boiler in my home for both baseboard heating and hot water and need to get a best estimate on my home's heat loss to correctly size my combi boiler. I will be using liquid propane for the combi boiler, and the only other gas appliance will be the kitchen stove. My house is a doublewide, 1 story, 1400sq ft, 3 bed/ 2 bath. It has 2 entrance doors, 7 windows, and 3 skylights. The location is in Northern Minnesota with very cold winters. The house has a crawlspace and rests on a concrete slab foundation. This house was recently renovated as well with the following;
(Roof)- Metal roof, synthetic wrap, 5/8'' OSB, R38 insulation w/ blow in insulation in between, well-sealed, no access to attic space. 3 newly installed skylights very well sealed.
(Siding & Windows)- Vinyl siding and 7 windows (double pane and vacuumed that are well-sealed and insulated), house wrapped 3/4'' OSB sheathing, R19 batt insulation in exterior walls, 1/2" gypsum sheetrock for interior walls.
(Doors) - 2 doors w/ storm doors, composite frame, steel door exterior, insulated and well-sealed.
(Crawlspace) - Metal roof skirting exterior, house wrapped, insulated exterior walls and rim joists with R20 Owens Corning XPS foam board encapsulated and non-vented, sealed with caulking and canned spray foam. Rests on a concrete slab in very good condition. Less than 3ft in height and only for utility use. All water pipes insulated. Portable dehumidifier hooked up with automatic drain out.
(Flooring)- All vinyl plank flooring, no carpet.
If I'm missing anything or any of you need more information please let me know as I'd be more than glad to fill you in.
If any one could provide advice from their own experience or knowledge on my home's estimated heat loss and recommendations on specific brands or models of combi-boilers it would be greatly appreciated.
(Roof)- Metal roof, synthetic wrap, 5/8'' OSB, R38 insulation w/ blow in insulation in between, well-sealed, no access to attic space. 3 newly installed skylights very well sealed.
(Siding & Windows)- Vinyl siding and 7 windows (double pane and vacuumed that are well-sealed and insulated), house wrapped 3/4'' OSB sheathing, R19 batt insulation in exterior walls, 1/2" gypsum sheetrock for interior walls.
(Doors) - 2 doors w/ storm doors, composite frame, steel door exterior, insulated and well-sealed.
(Crawlspace) - Metal roof skirting exterior, house wrapped, insulated exterior walls and rim joists with R20 Owens Corning XPS foam board encapsulated and non-vented, sealed with caulking and canned spray foam. Rests on a concrete slab in very good condition. Less than 3ft in height and only for utility use. All water pipes insulated. Portable dehumidifier hooked up with automatic drain out.
(Flooring)- All vinyl plank flooring, no carpet.
If I'm missing anything or any of you need more information please let me know as I'd be more than glad to fill you in.
If any one could provide advice from their own experience or knowledge on my home's estimated heat loss and recommendations on specific brands or models of combi-boilers it would be greatly appreciated.
0
Comments
-
The first thing to do is to use this heat loss calculator: https://www.slantfin.com/slantfin-heat-loss-calculator/ to figure out how many BTUh you need to heat the house. Down at the bottom of the page there is a rather obscure "click here" which lets you run the calculations on a PC or Mac, or you can use it as an app on your smartphone.
It will also give you the heat loss for each room and -- if you want -- even tell you you much of Slant/Fin's baseboard you need (you can use other folks baseboard, though -- they won't mind!)
Then with your BTUh number from that you can select -- or your installer can select -- the correctly sized boiler for you heating load.
Now... you mention a combi. They can be a little problematic to size, as if your hot water load is large (not likely in a double wide but it might happen) it's hare to find one which is big enough for that and yet small enough to handle the heating load. Try not to oversize.
The most important thing on brands -- particularly for the newer modulating/condensing boiler and combis -- is whether the installer really understands and likes the system and can install it and adjust it correctly and keep it maintained. Also, make sure that when parts are needed that the supplier is close by.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Space heating load is nearly irrelevant when talking combi units as the DHW load is almost always 2-3x the space heating load, but for discussion's sake, I also live in a 1400 sq ft double wide, in central MN, with similar specifications and mine is about 35,000 BTU at design (-20F). Where are you located, exactly? I send quite a few systems up around the Bemidji area and have others scattered all the way across the border from Lake of the Woods to Grand Marais, was just up in Cook last weekend and Ely the week before installing boiler systems. Anyway, if you're set on a combi, we'll want to figure out the DHW load before anything else. Worst case scenario, how much hot water would you ever be using at one time? Just 1 shower? 2 showers and laundry?3
-
Wow such a small world we live in. I'm located in Britt. Worst case scenario for water would probably be to have one or two showers running with laundry and/or dishwasher running too. However, I think that's a little overkill but safe for worst case scenario.0
-
If you can get @GroundUp to help you, @JohnJr , you'll be in good hands.
That's beautiful country up that way -- years ago I spent a good bit of time paddling around in that region...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Wow, when I said Cook I was actually in Angora but didn't say it because nobody knows where it is haha. Was probably 10 minutes away from you at some point! Anyway, if we're shooting for worst case scenario and you've updated the showerheads to higher flow units, toward the end of the winter with the sub-50 degree water temps and say 2 GPM for each shower and 1 GPM for laundry, we're looking at 199,000 BTU unit which is huge for such a small home's space heating system. Personally, I don't like combi boilers or tankless WH in general for average household applications (heat-only boiler and indirect WH tank are a much better option IMO), but if you know that you want a combi I'd be happy to discuss this further with you. Would you be willing to sacrifice a little DHW production in order to make the boiler live a happier life? Say stepping down to a 150k or maybe even a 110k unit like a Lochinvar Noble (which is what I install, I feel they're the best combi currently available) for a more appropriate space heating size? The 199 would do a great job with the DHW but it may very well suffer with short cycling on warmer days without a buffer tank, which kind of defeats the purpose of a combi. What do you think?JohnJr said:Wow such a small world we live in. I'm located in Britt. Worst case scenario for water would probably be to have one or two showers running with laundry and/or dishwasher running too. However, I think that's a little overkill but safe for worst case scenario.
1 -
I would be willing to sacrifice a little DHW if it meant a longer life from the boiler. You also are the second person today to recommend a Lochinvar, but I have also been leaning towards the Navien NCB 210E. What are your thoughts on this model for my home and situation? Could you please explain in a little more detail how the combi would potentially short cycle on warmer days without a buffer tank? Is there any way to mitigate this without a buffer tank?0
-
0
-
On the short cycling, @JohnJr , what happens is that the lowest the boiler can go produces a certain minimum amount of heat -- but on a warm day your house can't absorb all that heat. So the boiler has to turn off. But then the house cools off a little and the boiler comes back on... and so on. Adding a buffer tank doesn't change the total run time much if any, but does allow the boiler to run longer -- and stay off longer -- which is better for it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
My thoughts on combi boilers in general are not very positive, so please take this with a grain of salt, but I would sooner heat my home by rubbing sticks together and take cold showers for eternity than own a Navien combi. Again, merely a personal opinion, but I have junked easily 20x more Navien units than anything else combined since starting this business only 5 years ago. There are a handful of good ones too obviously, but the failure rate I see is ludicrous and I can't believe they're still in business. Jamie did a good job explaining the short cycling issue, but the answer to your question regarding the buffer tank is no. Unless you add a dump zone and shoot unwanted heat outside to prolong burn cycles.0
-
My nearly worthless opinion as another non professional homeowner is to listen to Groundup when he suggests a heat only boiler with indirect tank. Much more efficient, probably cheaper, and also more reliable. Less things to break.
Simple and reliable is the name of the game when its -20f outside.
Also I've been through MN a few times. Dated a girl that lived in Minneapolis 14 or so years ago. Beautiful state. A little cold for my blood tho. Last time I was there in winter I think the high during the day was like 2f.0 -
How is it that a boiler will run 2 to 3 times longer to heat the domestic water than to heat the space? It has to heat a lot more water to heat the space, no? All the water in the closed loop pipes and radiators?I'm not a plumber or hvac man and my thoughts in comments are purely for conversation.0
-
All the water in the closed loops and pipes isn't really all that much water. Of course that varies, but it's kind of surprising how little water is in a pipe -- to a first approximation, only a gallon or so in 100 feet of half inch pipe. So if there are let's say 10 gallons in the boiler, and 400 feet total of pipe and emitter (thinking baseboards here) you ay be looking at perhaps 15 gallons of water. An indirect water heater may have 80 gallons of water...
So there's a lot less water to heat the space than is accounted for by domestic hot water.
If it's a combi, you also have to consider that not only is there less water involved in heating the space, it's not flowing anywhere near as fast in most houses.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Its also about the 'temperature rise" of the incoming water for the combi to achieve. What is temp of incoming well water in MN winter? 35-38F? Coming through at up to 5gpm! As opposed to water in a close heating loop starting near room temp-- like 68F.0
-
That's why combis and stand alone instant hot water heaters have such huge power requirements! Your example here, assuming 110 water is a usable definition of "hot" -- is going to take close to 200,000 BTUh output from the burner... enough to heat an average sort of 8,000 square foot house!psb75 said:Its also about the 'temperature rise" of the incoming water for the combi to achieve. What is temp of incoming well water in MN winter? 35-38F? Coming through at up to 5gpm! As opposed to water in a close heating loop starting near room temp-- like 68F.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Wow I feel better now, I thought I was the only dude that was anti-combi1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements