Mitsubishi phantom loads

Polycarp
Member Posts: 135
I have a Mitsubishi hyperheat multi split heat pump. I have power metering on the HP’s branch circuit and the unit is always pulling around 220W. It used to go down to near zero, but doesn’t anymore.
I thought it might be the crank case heater, but Mitsubishi says that should only pull 50W, and also should be turning off when the outdoor temp is higher. This is a constant load.
I've checked the indoor units (which are powered from the outdoor unit) and they are only pulling about 15W each. I’d expect some off-operational load, but this just seems too high. It accounts for 35-45% of our total energy use.
we’ve had the installer out, but they didn’t even bring the right communication cable, so I doubt their ability.
I've checked the indoor units (which are powered from the outdoor unit) and they are only pulling about 15W each. I’d expect some off-operational load, but this just seems too high. It accounts for 35-45% of our total energy use.
we’ve had the installer out, but they didn’t even bring the right communication cable, so I doubt their ability.
0
Comments
-
-
Yeah, chasing things like that you'll need to check the zero & calibration of your instruments, particularly if it's some comsumer-grade thing like a kill-a-watt.
What are you using?
0 -
Hi, @Polycarp , Do you, or a friend have a thermal camera, like a Flir One? It's a very useful gadget! Use it to have a look at the equipment and see if you can find any hot-spots. That would tell you what's using the power, which will help a lot in troubleshooting.
Yours, Larry0 -
Do you have an outlet near the outdoor unit?
Is anything plugged into it?
Code requires an outlet within 25' of AC unit, I have done the outlet with the AC circuit and using 12-3 cable to get the neutral there.
The load of an outlet connected in this manner goes thru the AC CB.
What type of measuring device are you using and where is it connected?
Note: do you get the same reading if the system is in cool or heat mode?
Perhaps there is a holding coil on the reversing valve drawing power when in the opposite mode of operation.0 -
ratio,
The metering system is Emporia. I double-checked with a fluke current meter and got the same answer +/- 1%.
JUGHNE,
There is nothing else on this circuit but the heat pump. The outlet for the HP does not have a receptacle, so there is no way to plug something else in.
I also get the same results whether the thermostats are in auto, heat, cool or off modes.
Larry,
I don't have a Flir or easy access to one, but maybe this is the excuse I've been waiting for.0 -
You have all the indoor units off when you are getting 220w? What is Mitsubishi saying you should be reading?0
-
220 watts is a lot of heat, you could not hold a 200 watt bulb in your hand very long.
You might have a power supply board/transformer etc that is cooking itself.
I got a handy FLIR camera for 350 and that might be 400 now, but it is a great toy.
I can see my heating loops thru the concrete and where the dog was laying 5 minutes after he gets up.
For instance on a 12' ceiling with diffusers from 2 systems you can tell which is heating, without a ladder.
Also for finding failed open steam traps on rads.
0 -
Kind of what I'm getting at... 220 watts is a lot of heat, indeed, and it has to be going somewhere. One of those nasties about energy is that it has a way of winding up as heat, pretty much every time.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- 117.6K All Categories
- 82.8K THE MAIN WALL
- 2.7K A-C, Heat Pumps & Refrigeration
- 43 Biomass
- 403 Carbon Monoxide Awareness
- 8 Chimneys & Flues
- 1.6K Domestic Hot Water
- 4.3K Gas Heating
- 107 Geothermal
- 148 Indoor-Air Quality
- 2.7K Oil Heating
- 45 Pipe Deterioration
- 681 Plumbing
- 4.8K Radiant Heating
- 353 Solar
- 13.3K Strictly Steam
- 2.9K Thermostats and Controls
- 48 Water Quality
- 31 Industry Classes
- 65 Job Opportunities
- 12 Recall Announcements