stick w/ oil or switch to propane?
year built: 2003
size: 3400 sqft
location: Atlantic Canada
current system: 2003-era NTI C-series heating oil boiler w/ indirect tank for DHW
distribution: hot water radiators (about 60%) and in-floor (40%, some in-slab and some in-joist)
oil tank: inside basement, fiberglass, brand new (supplied by seller), 796L capacity
i believe the boiler is original. we had it cleaned and serviced when we moved in (i think it had been some years since anyone did that), but i reckon it's time to replace.
the company that did the servicing recommended we move to propane to save money. that would have the additional benefit of allowing me to add 1) a standby generator, and 2) a propane stove for the kitchen to replace the electric range.
but when i start pricing out oil vs propane and look at relative efficiencies, i don't see savings. my goal is to see what i'm missing.
since moving in, i had an energy assessment done. here is some info from that:
per that report, we are planning on adding some additional attic insulation. upgrading windows is probably a ways off. i suspect there are some areas that are lacking sufficient insulation, so we'll be addressing those in time.
in December, i had a Daikin minisplit installed (FVXS15NVJU/RXL15QMVJU). that unit, set at 69F, keeps the kitchen and dining rooms @ 22C, and also keeps the upstairs hall @18-20C depending on outside temps. that hall leads to the bedrooms. i typically leave that thermostat set @ 19C, and that calls for heat only occasionally. the master bedroom is a little cooler than i'd like, but i reckon i can turn the upstairs to 20C if we can get our overall costs down.
post mini-split install, i believe most of the oil usage is going to the living room (a mix of in-joist and in-slab radiant heating) and my office above it (hot water rads). i'm currently getting quotes for a 2-head minisplit to help take the load off the boiler.
but i still have to replace the boiler. here are some of the fuel prices i've captured in the short months since living here:
- electricity $0.1492 CAD / kwh
- heating oil, ranges from $0.774 - $0.896 CAD / liter ($2.31 - $2.67 USD / gallon)
- propane, ranges from $0.764 - $0.868 CAD / liter ($2.28 - $2.59 USD / gallon)
i captured those prices between Dec 2020 and now; i don't know what summer pricing looks like.
when i multiply out the costs and expected efficiencies of new oil vs propane boilers, and the BTU of the fuels, it still looks like i get more BTU per liter of heating oil. and those prices per liter are comparable.
BUT, am i missing anything? should i be thinking about cycle times, or condensing/modulating, or pump efficiencies, or anything else? i also don't yet have a handle on who would own the propane tank here, and if that does indeed limit me to that supplier. what if i get such a large propane tank that i can buy only during the summer? does that change the equation? what else am i not thinking about?
note that i do have enough property for an above-ground propane tank.
i can always add propane separately, of course, to get the genie and stove.
in the spring, i plan on having at least 3 companies out here to quote new systems, but the more i learn now, the better.
i'll finish w/ some photos of my current setup.
Comments
-
As you have found, LP usually is not less expensive than oil. In fact, in the states, on a per BTU basis (which is the only valid comparison) it's usually more -- sometimes a lot more.
Also relevant -- the potential savings from increased efficiency are relatively small, even if you get the best possible match between your installed radiation, the heat loss, and the boiler. In your situation -- with the mini-splits already there -- it would likely be even less.
So... if it were mine, I'd stay with the oil and replace the boiler -- when it actually dies -- with the best matching small boiler available in your area.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England5 -
I agree with Jamie. That is an ugly looking installation. If it makes you feel better about it, heating oil is being replaced by renewable alternatives, not really possible for propaneTo learn more about this professional, click here to visit their ad in Find A Contractor.1
-
i'll admit i hadn't given much thought to waiting for it to fail. it's probably 18 years old at this point; is there a rule of thumb for the life expectancy of a boiler like this?Jamie Hall said:I'd stay with the oil and replace the boiler -- when it actually dies -- with the best matching small boiler available in your area.
and fair point about getting near the limits of efficiency w/ the minisplits in the mix.0 -
-
Stick with the oil, as the others mentioned. There's been more than once where propane supplies were a huge problem. At least with heating oil, when supplies get tight, you can get it trucked in.
If you get a boiler like an EK, you'll find it to be super efficient, quiet, etc.
The added benefit is most of them can be converted to nat gas, or in your case, propane if the market flip flops.
Keep the generator a separate issue. It would need it's own, massive tank to do whole house. But if you went with diesel, now your adding a good 30% to a whole house gen.There was an error rendering this rich post.
1 -
-
Is that a Direct/ Balanced flue oil boiler? They can be a bit of a pain to get to run right... Prone to sooting up.0
-
It's a steel single pass firetube boiler DV, although it is wetleg.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
-
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
that's an interior door to the finished part of the basement.kcopp said:I would focus of getting your homes envelope squared away. Air seal and insulation. IF I am seeing the pix right I see daylight coming from under your basement door...in the oil tank picture.
from the blower test, the house is sealed moderately well. i've identified a couple windows, plus both sliding glass doors, that are leaky in high winds. the plan is to delete one of those sliding glass doors and swap out the other for something more efficient.
this summer, i'll be adding more blown-in cellulose into the attic, bringing it to R35. as we do reno's, we'll be assessing the current insulation and addressing any deficiencies we find. we already have a handful of spots that were shown deficient in the FLIR, though they were all somewhat minor.0 -
btw i forgot to mention this house has nine (!!!) thermostats. i reckon some of the spaghetti is due to that.0
-
Not sure if that's a wet leg boiler. It looks like the return comes in above the chamber.
It is block steel and will lose efficiency over time. With all the expansion and contraction, the steel can absorb the heat better over time, but can't hold it.
It's definitely fugly but a decent setup with the diverter valve.
There are plenty of 3 pass oil boilers or an EK Frontier that will be more efficient than what's there now. And most of them can be converted to an LP power burner if desired.
IMO, you have time to do research and planning. It doesn't need replacing, yet.0 -
Think you will find that the oil/propane debate has no "one" answer .... have bought many old houses and switching to propane was typically done when I had a forced air furnace. Propane allowed for not only more efficient equipment -- it gave you better control comfort (modulation) and eliminated most of the service. The fuel was/is a flip flop .... but, over time they don't offer huge savings one way or another. Propane can change quickly over shorter periods.
With a boiler it's more of a math problem ... you could switch to a condensing boiler using propane and gain some efficiencies ....but, my guess is you will not see the payback and gain no additional comfort doing the switch. I never did the switch w/ boiler unless NG was available.
Minisplits work -- again it's math to determine when to use. There is also a comfort factor -- typically you can't match the comfort of hot water piped through a home in cold weather.
You may look into seeing if there are any HP water heater rebates -- often they are nice with oil boilers. The area around the boiler provides some free heat for the water heater and they keep the boiler off in the summer -- plus you get some dehumidification in the summer. I know people who only use them in the summer ....it's all about the rebate0 -
Admit the boiler install is not pretty. But if it were me I'd address all the insulation and sealing possibilities. Basement foundation is a big one, attics in WI we are at R50+,keeping the heat inside will be your key to heating efficiency. It's not always the boilers fault, and one can do a combustion analysis to find out the current boiler efficiency.
D0 -
Explore ground-source water-to-water heat pump possibilities in your area. Look for any engineers who can help with sizing/specifying and/or any drill contractors who can do the loop well. The upfront cost is higher (but there may be incentives available), but the operating cost is at or below NG in my experience.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
my understanding is that geothermal doesn't work well w/ my hot water baseboards because of temperature constraints. i.e. my current system was designed for heating oil temps. if that's incorrect, please let me know.ethicalpaul said:Explore ground-source water-to-water heat pump possibilities in your area.
0 -
-
That's correct. You will need to evaluate the capability of your baseboards to meet the heating load required at various water temperatures.zimv20ca said:
my understanding is that geothermal doesn't work well w/ my hot water baseboards because of temperature constraints. i.e. my current system was designed for heating oil temps. if that's incorrect, please let me know.ethicalpaul said:Explore ground-source water-to-water heat pump possibilities in your area.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
How long do you plan on staying in the house? Most home buyers only care as to how old the furnace is.0
-
A great opportunity to size your radiation to the house as it exists today, and to explore options such as radiant flooring. I mean, unless those are like designer baseboards that are beautiful and architecturally significant like most of them are...zimv20ca said:
my understanding is that geothermal doesn't work well w/ my hot water baseboards because of temperature constraints. i.e. my current system was designed for heating oil temps. if that's incorrect, please let me know.ethicalpaul said:Explore ground-source water-to-water heat pump possibilities in your area.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
After the energy upgrades rerun the load clc.
Then do a heat emitter assessment.
See if what you have can meet the heating load at lower SWT.
Lower SWT opens you up to more heat generator options, now and down the road.
The modulating features on a mod con boiler can bring a lot of efficiency and reduced cycling, properly installed and dialed in.
https://www.caleffi.com/sites/default/files/file/idronics_25_na.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This is a good calculator to enter all the parameters, like boiler efficiency, energy costs, etc..
Even has wood should you need to start burning your IKEA, like some Texans did recently
https://coalpail.com/fuel-comparison-calculator-home-heatingBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
AKA supply water temperature
LP is a fickle fuel, prices can vary quite a bit. In areas where it is the predominate fuel it stays fairly affordable. In the lower mid west for example I filled last fall at .99/ gallon, you could lock in for 1.25 for the season.
I didn't as we were selling the home. I had to top off before we left and it was 2.45 a few weeks ago.
If you do go LP, purchase your own tank, pre-buy in August or Sept, or lock in to one of the fixed price deals. The dealers around me understand folks may be on fixed incomes and they always have programs available to avoid pricing people out of heat.
Another tip is to shop LP in early summer, if small dealers pre-bought too much they tend to drop prices instead of paying storage fees at the bulk plants.
When "big oil" gets greedy as they did in 2014, not much the small local dealers can do about that.
There seems to be a lot of consolidation in LP dealers now also, the small mom and pop shops are being swallowed up and the local friendly service and pricing deals often goes away also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
update: i've decided to stick w/ oil and replace the boiler, probably this spring.
i got a quote for a "DK2-4 CALISTO 4 SECTION CAST BOILER", which is apparently a cast iron, direct-vent (which i have now), cold start boiler. it's rated at 87% AFUE, which is enough (barely) to qualify for a $500 CAD rebate from the provincial gov't here.
i found this information sheet online:
https://kerrcontrols.ca/wp-content/uploads/2019/04/Calisto-2019.pdf
they spec'ed out this burner:
"RIELLO BURNER 22/27"
tbh, i don't know these systems and don't feel i know enough to know if this is good. i asked about sizing it smaller, and was told he "had to" size it for the coldest day, when it's too cold for the (soon to be) 3 minisplit heat pumps. i inquired about sizing it smaller such that it can keep the house steady at a lower temp; i'm still waiting on the answer there.0 -
-
Cut and paste job?To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Would have been nice to clean up a bunch of that plumbing, and to at least remove that rubber hose from the water heater relief valve. Also, that new Tekmar control that has the OPN on it, means one of the sensors is not hooked up, or has something wrong with it, and needs to be checked out.
Rick0 -
my understanding is that 3 of the 4 zones on the Taco are being used. i have 11 thermostats collapsing to 3 pumps, and those are in zones 1-3.rick in Alaska said:Would have been nice to clean up a bunch of that plumbing, and to at least remove that rubber hose from the water heater relief valve. Also, that new Tekmar control that has the OPN on it, means one of the sensors is not hooked up, or has something wrong with it, and needs to be checked out.
Rick
not sure if that's what you're talking about, this is all still new to me.0 -
also, while the prior boiler was set to 160F, this one is set at 180F. i've no idea if that's a proper setting.0
-
-
got it, thanks. one of the owners of the installing company is coming by to check it out.rick in Alaska said:Not what I meant. On the little Taco box to the left, it has a display reading "opn", which is a sensor error, and needs to be checked out. Hope this helps.
Rick0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements