Hybrid water heater
Cate
Member Posts: 3
We just built a semi custom home and a hybrid water heater was put in. We are a family of five and I am having issues with there being enough warm/hot water throughout the busy times of usage. We are only able to have one shower at a time before the warm/hot water is gone. Any tips/advice on what I can do? I tired switching it over to “electric” mode but it switches itself back after a little while. I’ve looked through the manual and there wasn’t any information that I found useful for this situation.
0
Comments
-
What make, model is the water heater? How was the sizing of it determined?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
state premier hybrid electric
model #: HPX-50-DHPTNE 130
Since it wasn’t a full custom build we didn’t get to determine how they chose this item. I can only imagine since it passed an inspection that it is supposed to be the correct size for the size of this home... but I have no knowledge in this area so that is a guess.0 -
Set the tank temp to 140 and then mix down for use.0
-
Inspectors don't determine the sizing of equipment since that requires proper calculations. They just determine that it's installed per code. It's probably under-sized for your needs.Cate said:state premier hybrid electric
model #: HPX-50-DHPTNE 130
Since it wasn’t a full custom build we didn’t get to determine how they chose this item. I can only imagine since it passed an inspection that it is supposed to be the correct size for the size of this home... but I have no knowledge in this area so that is a guess.
As, mentioned, you can crank the water temp setting up to 140* and add a tempering valve set at 125* to prevent scalding, but that's only gonna give you about 15% more stored heat capacity.
You could add a second 50 gal electric tank that the present one would load into.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
That's a 50 gallon capacity heater. And it is simply not big enough for 5 people. Further, it is electric resistance for anything like rapid recovery -- and that doesn't help.
You need a bigger, probably straight electric, water heater -- although there are bigger hybrid ones, if you don't mind the budget...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
A 50 gallon electric is like 1 bath with 2 maybe 3 people. If your winter incoming water temp is lower, like 32-45 degrees or so, it probably won't make enough hot water for back to back showers even in that situation. it really is the starting size for electric water heaters.0
-
Thank you everyone! I will take these options and talk to our plumber.0
-
You'll have to allow time between showers for it to recover. The 65 gal. version of the heat-pump would have been better. 80 gal. model would probably be perfect. Remember these are "slow and efficient." With the 50 gal. you'll have to adjust your usage to match its ability to heat water. Low flow shower heads would be good.1
-
Do you have other fuel options? Gas fired tankless or Gas fired tank?
What do you have for a heating system?
0 -
Hi @Cate , To add to what others have said, your tank is way too small. Consider adding a second tank in series. Make it a 50 gallon electric, downstream of your present tank. You might want to look into Marathon heaters as they have very good insulation. Then try setting your heat pump unit to heat pump only and see how that works for you. I'll add that a quick, partial fix is to use 1.5 gpm showerheads or lower to extend the hot water you do have. If you have access to the drain from an upstairs shower, than adding a shower heat exchanger will essentially double the shower time you get per gallon of hot water as it's recycling those BTUs.
Yours, Larry
ps, Do you have a recirculation line for hot water? Does it have a good check valve in it? This could create a cross connection which would mess with hot water delivery.0 -
@Cate
It is usually considered that 80% of the water heater capacity is hot water. That is because as you start to draw hot water cold water enters cooling some water in the tank. so a 50 gallon x .8=40 gallons of hot water.
That being said you shouldn't run out of water with 1 shower0 -
As a small piece of anecdotal data, I chose the 65 gallon version of the Rheem for my house. Just my wife and I in a 3-4 bedroom 1200sqft home with 1.5 bathrooms. It's done real well for us but if we had 3 teenagers I'd be in a world of hurt.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements