Hi all, I'm in the process of planning a renovation on my 1950's house and I'm having problems figuring out my heat loss so I can size a new heating system. The exterior walls will have R18 and the wood frame R13 which gives me effective R31. Tools like slant fin don't seem to be handle that much. Could anyone direct me to something that could do that?

Comments

  • pecmsg
    pecmsg Member Posts: 4,861
    Options
    I don’t understand R-18 and R-13 in the same wall?
  • callumshill
    callumshill Member Posts: 5
    Options
    Sorry early morning post before the coffee kicked in. I'll be adding 4" of foam with an r value of 4.7" outside the sheeting. That's where the R18 comes from.
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,304
    Options
    Hi, If the app doesn’t go high enough in R value, you could put in fewer square feet of wall area to compensate. For example if your R value is twice what the app gives you, then cut the square footage in half.

    Yours, Larry
  • Jamie Hall
    Jamie Hall Member Posts: 23,323
    edited January 2021
    Options
    A true Manual J calculation will handle it, but I'm not familiar with a plug and chug application which will go that high. You can finagle it, though with some hand calculation and the Slant/Fin results, as I recall. If you use say R10 for the walls, and get the partial heat loss for the walls and windows and infiltration and all separately, then cut the partial loss for the walls (just the walls, not the windows!) by 3 (that would be R30) and then add them all back together, you'll be well within the margin of error.

    A word of caution when working with very high R value insulating systems, however: Either take thermal bridging into account in your calculations, or arrange your construction to avoid it (which is much easier said than done). Thermal bridges, such as studs or other framing, or even through bolts, become important in the performance of a wall even at R20
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options

    A true Manual J calculation will handle it, but I'm not familiar with a plug and chug application which will go that high. You can finagle it, though with some hand calculation and the Slant/Fin results, as I recall. If you use say R10 for the walls, and get the partial heat loss for the walls and windows and infiltration and all separately, then cut the partial loss for the walls (just the walls, not the windows!) by 3 (that would be R30) and then add them all back together, you'll be well within the margin of error.

    A word of caution when working with very high R value insulating systems, however: Either take thermal bridging into account in your calculations, or arrange your construction to avoid it (which is much easier said than done). Thermal bridges, such as studs or other framing, or even through bolts, become important in the performance of a wall even at R20

    Exterior foam insulation virtually eliminates thermal bridging . How will your air sealing be handled ? ACH ( air changes per hour) does much more tyo affect your load than any R Value increase above R 15 .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Zman
  • Jamie Hall
    Jamie Hall Member Posts: 23,323
    Options
    @Rich_49 mentions air changes. Which is a very good question. How do you propose to get adequate air changes per hour? You need at least two to maintain anything like livable indoor air quality. Sensible heat heat recovery unit?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Robert_25
    Robert_25 Member Posts: 527
    Options

    Hi all, I'm in the process of planning a renovation on my 1950's house and I'm having problems figuring out my heat loss so I can size a new heating system. The exterior walls will have R18 and the wood frame R13 which gives me effective R31. Tools like slant fin don't seem to be handle that much. Could anyone direct me to something that could do that?

    If all of your walls will have the same insulation value, you can pick the closest match in your heat loss software. The result will be that our radiation will be a little oversized, which will allow you to use lower water temperatures.
  • callumshill
    callumshill Member Posts: 5
    Options
    Those are great comments. As well as adding the extra insulation I'll be working on improving the air sealing in the house (right now it's 11.93ACH!). I'm planning on installing a HRV from VanEE as I'm in Canada. For the heating I'm leaning to a gas Combi Boiler and want to make sure it's sized right to avoid short cycling.
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    I hope you mean 11.93 ACH50 .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • callumshill
    callumshill Member Posts: 5
    Options
    Hi Rich, yes the house is just bit leaky right now.
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    Did someone perform a blower door test depressurizing the building to -50 pascale to determine that number ? Do you or someone counciling you have a target blower door number that you will reach ultimately ? Of not sizing a system properly is 100% impossible and a waste of your time and effort .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • callumshill
    callumshill Member Posts: 5
    Options
    Yes I had the initial blower door test done to get that first reading. I'm aiming for around 3.0 or better after I'm done the renos.