Need help improving heat to slabs

The slab zones in my system struggle to warm up. I have an OWB and a propane boiler. The propane boiler is dialed back during the winter months and only turns on if the OWB water temp drops below 120. OWB is set 165* on 185* off(all temps in post are F). Water from the OWB is a closed system thru a heat exchanger and not tied directly to the heating system. In the main boiler room I have 3 zones and an extension to the basement utility room. On that extension the water goes thru another heat exchanger and a mixing value to lower the temp for slab. There are 2 zones on that extension, 1 for the basement of the house and 1 for the garage. Pictures provided.
When the temps are cold the water returning is very cold, this pulls the temps down going into the slabs, especially the return from the garage. I set the thermostat for the garage at 50. I set the thermostat for the finished basement at 66. On cold days the basement cannot get up to temp when the garage heat is on, as the water to the basement zone never gets above 105 or so.
Not sure whether there are other issues as I am the second owner and was not around for the install, so the tubing might be too deep in the floor as I notice the floor in the basement doesn't get much above 70 except close to the utility room.
So my questions is what is best to do. The Taco 007 is kind of loud so maybe the flow is not good. Not sure of age of the pump. Temp coming into heat exchanger is 165 and leaving at 155. Zone water entering the heat exchanger is 80 and leaving at 105(right now it is cold outside, -19*F). Return temp on Garage zone is 75* and basement is 85*.
Not sure where to start. I can replace the pump to see if that helps the delta T. Mixing valve is turned to max so it is not doing much in this right now. Larger exchanger? Garage zone is always going to be colder return. Do i need to separate the zones? Both zones struggle to get to thermostat setting. Looking for advice on what to design and plan. Thanks in advance for any help.

When the temps are cold the water returning is very cold, this pulls the temps down going into the slabs, especially the return from the garage. I set the thermostat for the garage at 50. I set the thermostat for the finished basement at 66. On cold days the basement cannot get up to temp when the garage heat is on, as the water to the basement zone never gets above 105 or so.
Not sure whether there are other issues as I am the second owner and was not around for the install, so the tubing might be too deep in the floor as I notice the floor in the basement doesn't get much above 70 except close to the utility room.
So my questions is what is best to do. The Taco 007 is kind of loud so maybe the flow is not good. Not sure of age of the pump. Temp coming into heat exchanger is 165 and leaving at 155. Zone water entering the heat exchanger is 80 and leaving at 105(right now it is cold outside, -19*F). Return temp on Garage zone is 75* and basement is 85*.
Not sure where to start. I can replace the pump to see if that helps the delta T. Mixing valve is turned to max so it is not doing much in this right now. Larger exchanger? Garage zone is always going to be colder return. Do i need to separate the zones? Both zones struggle to get to thermostat setting. Looking for advice on what to design and plan. Thanks in advance for any help.

0
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 567 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.2K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
How many btus are you needing on the basement? On the house? If you don't know, give the number of tubing loops on each.
You can choose to do what you want, but you cannot choose the consequences.
The most common issue I see with OWB installs is undersized piping for the boiler to the house. In your picture, the HX looks pretty small and the mixing valve is likely a high resistance model.
Would you be able to sketch out your piping including pipe sizes and lengths? Also include the models of the pumps and HX.
If you are able to measure the temp difference between supply and return on your pipes, that is a great troubleshooting aid. Shooting the pipe with a little IR gun works pretty well, a piece of tape on the pipe eliminates reflectivity and gives you a more accurate read.
Albert Einstein
For tubing loops I assume that is one of my problems. The system is older and I would suspect should have been done with more loops. Both are 5 loops. My guess is that current install would be higher in the concrete and more loops. Both areas are about 1200 sqft rectangles.
My first thought is the 007s are too small for the required head of a typical radiant floor. Generally.......a 0015 is used (high head low flow) vs a 007 which is a medium head medium flow circulator.
There is not a lot of distance being fed by any individual 007. The main level has 2 zones of baseboard and 1 zone DHW and then the small 8-10' drop to the basement to the other HX. The second pump has 2 zones of 5 loops each in the slabs. And the third pump runs the heated water from the OWB to the house and back, 50 ft each way.
Yes, a 007 is generally not enough head for a typical 1/2" x 250-300' radiant loop slab.
The closed system for the slab, you can see 98% of it in the picture. Only thing not visible is the manifolds and valve for the garage slab at ceiling height. But it is identical to the one in the picture for the basement. The T left of the 007 goes down to lower manifold and up 5’ to the garage manifold. Return from the basement slab you can see the top of the manifold then the valve and up to the mixing valve. T’ed in before the mixing valve is the return from the garage manifold (valve same as basement manifold not visible). Top line coming into mixing valve comes from expansion tank from HX. That is everything.
So I hope that is easier than a drawing. I am on an iPad so drawing is not easy without installing a new app 😀.
trainer for Caleffi NA
Living the hydronic dream
Only thing I can figure is someone undersized the small heat exchanger ge to act like a mixing valve.....
Draw a picture in paper, then take a picture of your drawing. No app needed