mixing black fittings and galvanized

Hello,
I am a homeowner and we are having a new boiler getting installed today. After doing research, we specifically contracted to have the copper near boiler pipe replaced with black pipe. After the first day of work, we went down it it looks like they put in galvanized with cast iron fittings (on the steam / dry pipes). Is this okay? We raised this and they said galvanized is better because of the zinc coating to prevent corrosion and that they didn't ask to because it was an upgrade. Also, they said they couldn't get the black pipe and that's why they used something "better." I read that galvanized can flake in a steam system and clog things up - but the installer says that's not a problem in a steam system with relatively wide pipes. He said he'd be proud to have what he put in my house in his house and that the pipes will outlast the boiler. Also, it is of any relevance, the return is copper (keeping that from old system).
Any opinions about this? Should we insist that the galvanized pipe be removed and and replaced with black pipe?
I am a homeowner and we are having a new boiler getting installed today. After doing research, we specifically contracted to have the copper near boiler pipe replaced with black pipe. After the first day of work, we went down it it looks like they put in galvanized with cast iron fittings (on the steam / dry pipes). Is this okay? We raised this and they said galvanized is better because of the zinc coating to prevent corrosion and that they didn't ask to because it was an upgrade. Also, they said they couldn't get the black pipe and that's why they used something "better." I read that galvanized can flake in a steam system and clog things up - but the installer says that's not a problem in a steam system with relatively wide pipes. He said he'd be proud to have what he put in my house in his house and that the pipes will outlast the boiler. Also, it is of any relevance, the return is copper (keeping that from old system).
Any opinions about this? Should we insist that the galvanized pipe be removed and and replaced with black pipe?
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 562 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
If I, a lowly homeowner, can buy malleable iron or cast iron fittings (and I can), then any contractor should be able to figure it out.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
It seems that black pipe would be more readily available than galv pipe.
Perhaps they got a good deal on some import galv piping, which IMO will not last as long as galv pipe of the 50-60's.
You probably could not insist on USA black pipe at this point. Most likely would end up with China blk pipe.
How much length could be involved unless they are re-piping the entire house?
Home Cheepo, Blows?
Please post pictures!
here are pictures - the job is supposed to be finished tomorrow.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
At least its not copper!
Where is this boiler being installed?
I had only been in this trade for 5 months when I ordered $500 Wotan of fittings and nipples from my local pipe supply to install my boiler. It’s not that hard.
Hell they could order them from Supplyhouse.com.
It is time to find the install manual and check piping diagrams included based on the model number posted on the side of the boiler.
For a correct installation they shall follow the instruction manual.
It is around there somewhere......maybe 50 pages or so.
(maybe someone took it home to study it for tomorrow's work....doubtful).
Those black fittings (90's and Tees) are considered malleable iron, (considered to be OK for steam use) not cast iron.
Up on the old piping are original black iron fittings, you can see a different thicker design.
I too have about that many galv nipples in my shop I would like to get rid of somewhere.
Even an old grey hair like myself could remove that galv set up in an hour....by myself. Those look to be precut store brought nipples....no cutting threading needed.
The horizontal header has too much slope (some is needed) for correct alinement to install a union to feed the right hand riser that goes up to the existing old steam main.
The correct configuration is to have: 1st boiler riser----2nd boiler riser (if needed)--- steam main take off---steam main take off---drop to equalizer/Hartford Loop (reduced on vertical drop only).
ie. How is this boiler going to be skimmed?
Please keep us informed as to how this all works out.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
You have to find your exact model/size number and then refer to the piping required for that model.
These side pipers used to have 2 1/2" side outlets and you were to use that for the riser size...some lately have come with only 2" outlets. Perhaps they require a larger pipe size for the header.
So far all your pipe looks to be 2". Often the size is stamped on the edge of the fittings. Is that a reducing 90 on the right side of the boiler?, that is 2 1/2" x 2"?....I can't tell by the picture. A better shot would help.
If the book chart for your model/size of boiler states that 2 risers are optional then you may only get one out of this crew.
But most important is the SIZE stated for the risers and the horizontal header. (2 1/2" or 3" etc).
The size of the house does not matter for the boiler piping.
The main concern is the dryness of the steam which is dictated by the number of risers and pipe sizes of riser(s) and horizontal header. (this can cause grief for the life of the boiler).
manual about how to do the piping with one riser.
I don't think I would like that arrangement. No flexible couplings with rubber parts on steam. But that is my rule, I m not sure what the experts say, I only had about 15 Steam boiler accounts in my years of contracting. No Expert here, I have asked for advice here in the past.
Retired HVAC Contractor from So. Jersey Shore.
Cleaned & services first oil heating system at age 16
Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air
If you make an expensive repair and the same problem happens, What will you check next?
The sad thing is. Just read the manual. And it take no more work to screw it all up that to follow the MFG minimum piping requirements.
Again, a 2 x 1 1/4" reducing coupling may be needed to get the skimming water to float up above the top of all sections.
The push nipples across the top are usually much smaller than the side outlets.
Installer may not believe this, but a quick look inside the section push nipples will confirm the size reduction. IMO
Retired HVAC Contractor from So. Jersey Shore.
Cleaned & services first oil heating system at age 16
Specialized in Oil Heat and Hydronics where the competition did Gas Warm Air
If you make an expensive repair and the same problem happens, What will you check next?
By adding the reducer on the horizontal skim pipe you raise the water level higher inside the boiler. This insures that you are draining water that is coming up through all sections of the boiler and not just the one closest to the side opening.
The connecting nipples inside the boiler are smaller than the 2" side port, so as you drain off water only the closest section will drain off.
The other sections will just hold the water as the level will not come up over the reduced internal nipple openings. The bottom of the small internal nipples are higher than the bottom of side drain.
I noticed this on an older boiler of this design when getting the 2 1/2" plug out of the tee, looking inside at the push nipples between sections, even 1 1/2" pipe would not fit inside the openings.
Maybe the design has changed since then, but I doubt it.
This is a reason that these side connected boilers work better with both side outlets connected to the header.
With just one riser, then all the steam has to pass across the reduced size nipples and struggle to get out of the boiler. IMO
as far as what to do now and how many hours it would take, you'd need to get someone else on here to advise you, cause i'm just an engineer not a plumber. if the pipes can be adequately isolated from each other electrically then that breaks the electric circuit and GC can't happen, but you'd need an experienced plumber to tell you if teflon tape and pipe paste is enough to do that. they sell dielectric (i.e. electrically insulating) unions and fittings (https://supplyhouse.com/Dielectric-Unions-and-Nipples-1640000), so the fact that product even exists makes me suspect that teflon tape alone might not do the trick, but again i have zero hands-on experience of it, so someone else would need to comment on that. sorry i can't be of more help, but better for me to know my place than give you bad/unnecessary advice.