Minisplit wiring coming up short- is that a problem?
bipbap
Member Posts: 233
Just had a new minisplit system installed and there are two outdoor condensers on roof.The refrigerant lines made it to one condenser with no problem, but they will not reach the location for the other one.
It seems like a mistake since much longer runs made it there and the ones that didn’t make it aren’t especially far from the condenser. See photo.
Is that poor install? Should he run new lines?
Can they join two lines or will that cause issues down the road with leaks?
Thanks in advance!
Are you talking wiring or copper tubing?0
Copper.
the other condenser is supposed to be hung to the right of the one in photo and the sets of copper lines will not reach that far.
How is the contractor going to extend the line set? There relatively cheap so just get the right size!0
I have put in quite a few minisplits.
I have always extended lines by 15% silver brazing while flowing dry nitrogen while torching.
Then pressure testing the lineset before evacuation with vacuum pump.
The only flare connections I have is at the unit.0 -
Ok so did he screw up or is this not really an issue?
Im not saying the lines cant be extended but if he cant get the length correct can he extend them properly.
Contact Mitsubishi and let them answer your question. There very good.0 -
I would not consider it a screw up.
I never get linesets for mini's. I build them up as needed and then insulate them in the field.
Usually you want continuous runs, but sometimes not possible.
I will use up short pieces rather than scrap them. Especially in 3/4" regular AC lines.
Although I do not bury a splice in wall or ceiling and will mark the location somehow as it is under insulation.0 -
I'm not saying you and I couldn't extend that set, I'm asking if the contractor can?
I avoid brazing mini line sets as much as possible but sometimes we have to do what we have to do!
Now with that said
Zoom Lock
Refrigeration Shark Bite
No Way
Let the factory tell the homeowner what "They" want.
It's hard to tell in this particular instance, but as a general rule the copper lines can be extended with zero impact on performance or aesthetics (assuming, of course, that normal best practices are followed), up to a certain maximum determined by the mfgr. It's sometimes less work to do it in one run & sometimes less work to piece it in. Depends on the job.
& sometimes you just miss measure.
Yes contractor will have to extend them
there just didn’t seem to be any good reason they came up short considering the runs weren’t long.0 -
I would be more concerned about what looks to be metallic flexible conduit and if it is considered approved for wet locations?
It may or may not be, IDK.0
- 87.5K THE MAIN WALL
- 122 Chimneys & Flues
- 116 Geothermal
- 169 Indoor-Air Quality
- 15.9K Strictly Steam
- 57 Water Quality
