Leaky boiler
spaceman789
Member Posts: 8
0
Comments
-
-
Bad expansion tank. Either it's completely failed -- most likely -- or wasn't properly charged. Of course, it could also be valved off... but my bet is it's just plain bad.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0
-
If that's the expansion tank, it's the older compression type -- and they simply never go bad. However, it's not at all uncommon for them to be misplumbed by modern plumbers, who have no clue as to what they do and how they do it. Can you take complete pictures to show the way it's connected to the rest of the system, and all the appliances, valves, sight tubes, gauges or whatever is related to it?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
That's a compression tank. Other than a possible baffle inside of it, it's just a hollow shell that has to maintain an air cushion in the top 1/3rd of it for water expansion. It's probably water-logged and needs to be properly drained.
The air vent that's on the line going to it needs to be removed. The tank maintains its air cushion by taking in air in the system from the top of the boiler. That vent is defeating that function and causing the tank to water log, leaving no room for water expansion.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
0
-
0
-
Potential to pull air into the system from that eliminator on the return side? No bypass.0
-
0
-
I’m not sure what this meansspaceman789 said:mikeapolis said:Potential to pull air into the system from that eliminator on the return side? No bypass.
I don’t see any extra valve on the compression tank that would let air in to drain, just the drainage pipe part.
Whats the brass fitting right above the hose drain?0 -
If you were to close the valve on the pipe from the boiler to the tank, and open that drain on the tank, it would empty. Glug, glug, glug, but it would empty. Then get rid of the air eliminator, as @Ironman said, close the drain on the tank and open the valve on the line to the tank. Will it work well? No, since someone eliminated the Airtrol tank and boiler fittings, from the look of it, but it will work. Without those you will have to figure out some clever way of keeping track of the water level in the tank -- it should be somewhere between half to two thirds full of water when the system is cold.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0
-
0
-
The reason it won't work well -- which is to say, the compression tank will tend to either waterlog or become completely empty and not regulate the pressure properly -- is that someone who didn't understand it took the automatic controls off. And added the air eliminator.
Which means only that you will have to keep your eye on it.
I have no idea what that other pipe is...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Whats the brass fitting right above the hose drain?spaceman789 said:
I’m not sure what this meanspecmsg said:mikeapolis said:Potential to pull air into the system from that eliminator on the return side? No bypass.
I don’t see any extra valve on the compression tank that would let air in to drain, just the drainage pipe part.
I can twist and remove it, no idea what it does though.
Guessing
Hook up a hose
Start draining
As the flow slows open the plug to allow air in
Not the proper valve for that tank0 -
You need one of these!
https://www.supplyhouse.com/Bell-Gossett-113041-DT-2-Drain-O-Tank-Air-Charger-8629000-p
It allows air in while draining the water.0 -
There may be a small riser tube that would let air into the top of the tank to drain it easier. Also not put the tank under a vacuum.0
-
@spaceman789
Do you see the automatic air vent above the boiler? The brass air vent with the small cap on it?
It needs to be removed and the pipe tapping capped. You can not use automatic air vents with the compression type expansion tank.
That vent is the reason your expansion tank is getting waterlogged. It's letting the air the expansion tank needs out of the system
I am surprised no one else mentioned it1 -
Uh, Ed, Jamie and I both mentioned it.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
0
-
Not that long, with the air eliminator still there. Weeks maybe? But in the meantime, and going forward, you know what to do!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If it were me I would just remove the standard tank and replace it with a bladder type tank. How big is the system? What kind of heat emitters are on it?0
-
Actually, that's probably the best thing to do, even though it won't last decades like a compression tank. There are even fewer people out there who properly understand compression tanks than there are who properly understand steam...mattmia2 said:If it were me I would just remove the standard tank and replace it with a bladder type tank. How big is the system? What kind of heat emitters are on it?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0
-
There is some argument to be made that the diaphragm tank does a better job of keeping oxygen out of the system.0
-
IIRC, those auto air vents you have can be disabled by tightening the cap on top.
You can tell by cranking them down tight and (maybe 24 hours) later crack them open to see if they did collect and trap air.
If so then tighten again and remove the vents later at your convivence.
I maintain a 1961 boiler with compression tank. After learning about the auto air vent problem and removing them.
My tank also has a sight glass. The top valve was leaking air also so after repairing that the tank still has held it's air for more than 5 years.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements